EDR Equivalent for steel pipe with fins

I have approximately 60' of 4" steel pipe with a spiral fin attached to it. Does anyone know what the EDR would be for this? I have attached a few pictures.
Thanks
Thanks
0
This discussion has been closed.
Categories
- 80.9K THE MAIN WALL
- 2.5K A-C, Heat Pumps & Refrigeration
- 36 Biomass
- 394 Carbon Monoxide Awareness
- 2.6K Controls
- 1.4K Domestic Hot Water
- 3.7K Gas Heating
- 101 Geothermal
- 130 Indoor-Air Quality
- 2.3K Oil Heating
- 30 Pipe Deterioration
- 565 Plumbing
- 4.2K Radiant Heating
- 333 Solar
- 12.2K Strictly Steam
- 36 Water Quality
- 7 Industry Classes
- 51 Job Opportunities
- 7 Recall Announcements
Comments
where did that come from?
Lower math: measure the diameter of the fins, figure the area of one fin (3.14 times the square of the diameter, divided by 4). Subtract the cross section area of the pipe (4" pipe is about 12 square inches). Count the number of fins per foot, multiply by the area you got by the subtraction and multiply by 2. That's the number of square inches of radiation per foot of pipe. Multiply by the feet of pipe and divide by 144; that will give you a sort of approximation to the effective radiating area and thus the EDR.
Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England.
Hoffman Equipped System (all original except boiler), Weil-Mclain 580, 2.75 gph Carlin, Vapourstat 0.5 -- 6.0 ounces per square inch