two pipe steam with traps and air vents

Austin_2
Austin_2 Member Posts: 3
hi
i have been in the heating busines for 20 years. i have dan's book of steam. i went to a church and the radiator had traps and air vents. i thought if there were traps then there should be no air vents. what kind of system am i working on?
also, what is the math to adjust pressure controls. can you give an example equation please w/#'s involved.

Comments

  • Brad White_200
    Brad White_200 Member Posts: 148
    I have seen one system

    like that, but while the vents were not on each and every radiator, they were on most.

    All I can suspect was that using the vents were a way to speed things up. They were of a newer type than the traps so I suspect an after-thought. (Working around other issues? That would not surprise me.)

    On the whole, absent one radiator that had neither trap nor vent, the system worked better than I would have thought. I suspect by this that the vents did no harm.

    I would be interested to hear if this is, in fact, a particular type of system though.
  • nugs
    nugs Member Posts: 77


    Cut in + differential = cut out

    It's not common to find vents on trapped radiators. I suspect that they were installed because someone couldn't or wouldn't repair the traps.
  • Austin_2
    Austin_2 Member Posts: 3


    but if you have two pipe and the traps stay open then steam would go into returns and trouble some of the vents
    are very old and i have to put my ear cloes to the vent
    to hear them work and the same with main vent and then
    steam came out
  • RonWHC
    RonWHC Member Posts: 232
    Careful.

    Some Honeywells have a subtractive differential. Main minus Differential = cut in. Main setting is cut out.
  • Jamie Hall
    Jamie Hall Member Posts: 24,647
    for example

    Vapourstats. However, it will say on it... somewhere... whether it is subtractive or not.
    Br. Jamie, osb
    Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England
  • gerry gill
    gerry gill Member Posts: 3,078
    are there any original traps

    and inlet valves? i'm looking for a name to identify the system..trane,dunham,etc...bet those air vents weren't supposed to be there..