Steam Trap on Radiator
Jamie Hall
Member Posts: 24,859
a bad trap. The mechanism that allows air to get out (but not steam) is different from the one that allows water to get out -- thus it is quite possible (in fact, very likely!) that when the trap goes, it will go in just this way.
Fortunately, unless you have something really really strange, it's really easy to open the trap and replace the innards.
Fortunately, unless you have something really really strange, it's really easy to open the trap and replace the innards.
Br. Jamie, osb
Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England
Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England
0
Comments
-
Steam Trap on Radiator
Is it possible for a thermostatic trap on a two-pipe steam radiator to allow water but not air to pass through?
I'm trying to determine whether my steam trap is the reason that air won't vent out of the radiator, or whether it's that the return line itself isn't vented well enough through the main vents.
If the boiler is on for a long time, the radiator will eventually fully heat, and condensate will drain out of the steam trap to the return line, which makes me think that the trap is not stuck in the closed position.0 -
trap
> Is it possible for a thermostatic trap on a
> two-pipe steam radiator to allow water but not
> air to pass through?
>
> I'm trying to determine
> whether my steam trap is the reason that air
> won't vent out of the radiator, or whether it's
> that the return line itself isn't vented well
> enough through the main vents.
>
> If the boiler
> is on for a long time, the radiator will
> eventually fully heat, and condensate will drain
> out of the steam trap to the return line, which
> makes me think that the trap is not stuck in the
> closed position.
Open the trap when cool and see in water drains down. If it does then replace the guts of the trap....There was an error rendering this rich post.
0 -
What would it mean if water does not drain down when the trap is cool?0 -
Trap
Where and what is your main vent? Should be by the boiler.0 -
Trap not working or blockage.There was an error rendering this rich post.
0 -
I'm not understanding
Big Ed - Did you mean that if the trap allowed water to drain down there was a problem, or if the trap did not allow water to drain down there was a problem?
Fred - I live in a large old condo building with a shared boiler, and although I've been down to see the boiler I've never been able to find the main vent(s).0 -
Almost certainly
a bad trap. The mechanism that allows air to get out (but not steam) is different from the one that allows water to get out -- thus it is quite possible (in fact, very likely!) that when the trap goes, it will go in just this way.
Fortunately, unless you have something really really strange, it's really easy to open the trap and replace the innards.Br. Jamie, osb
Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England0 -
Replacing Hoffman 17C innards
Jamie - When you say it would be easy to replace the innards, do you mean easy like replacing a light bulb? The trap is a Hoffman 17C, which seems like a very common model for which I can buy the replacement thermostatic disc.
I'm not a plumber, so if it requires any special expertise I'd want to call someone for help, but my experience so far is that the heating contractors in the Portland, Oregon area know very little about this type of thing.
Thanks,
Rob0 -
not quite
at the lightbulb level, but not too far from it -- there are stores on-line (State Supply? I forget at the moment) which, given the model of the trap -- which you have -- offer replacement innards (float, seats, themostatic mechanism, the works). You unscrew the top (that's where it can get interesting), pop out the old, pop in the new...Br. Jamie, osb
Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England0 -
Consolidated supply in Portland can order you replacement
thermostatic element for that. The rep happens to be in Vancouver also. Columbia hydronics is the Rep. for Hoffman. Good luck, Tim0
This discussion has been closed.
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 917 Plumbing
- 6.1K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements