connecting coall stoker in conjunction with oil burner, details
Bruce Harlor
Member Posts: 1
Where can detailed instructions be found to connected a coal burning unit with a seperate oil butning unit?
0
Comments
-
More info needed
Bruce,
That is an open question.
Is it steam, hot water, warm air?
One thing I can tell you up front is if it is not one unit LISTED for multi-fuel, then you will need 2 separate chimneys.
You can not use a fuel oil unit and a coal unit both in the same chimney.
Ed Carey
0 -
interesting question -
and combination of fuels. Depending on your jurisdiction this may or may not be feasible. That said - coal stokers and oil burners (number 2 or used oil) can be interlocked with the correct sequence of relays & temp controls to prevent both firing simultaneously. Its a popular combination for grain dryers. I would recommend you find a PLC guru and pose the question at his/her desk. Unless you are completely comfortable with commercial burner controls (and correctly trained); the complexity can be over whelming. Detailed information? That depends entirely on your selection of controls. This also brings up the issue of combustion air and chimney requirements - again some jurisdictions may allow this combination, others may not. In the combo burners I have seen - it was always the fire insurance carrier that had final word.0 -
Multi-fuel Boiler
There is a multi-fuel boiler that is made to burn coal and oil. Are you using anthracite or bituminous coal? I am very fond of coal boilers. Today many of them are automated so that you do not have to shovel coal into them. Here is a link to a multi-fuel boiler:
http://www.alternateheatingsystems.com/Multi-Fuel_boilers.htm0
This discussion has been closed.
Categories
- All Categories
- 86.2K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 52 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 99 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 915 Plumbing
- 6K Radiant Heating
- 381 Solar
- 14.8K Strictly Steam
- 3.3K Thermostats and Controls
- 53 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements