csst grounding
[Deleted User]
Posts: 0
I presume you are talking about the incoming service from the outside, which would have been PE, because it is illegal to use PE inside of the building. And to answer your question, YES, it is required to ground the CSST at all terminations to avoid the swiss cheese syndrome should the building get hit by lightning.
To the best of my knowledge, it has to be an approved earth ground, and I don't believe that the building super structure qualifies as an approved earth grounding source.
But I've been wrong before, and I'll be wrong again...:-)
ME
To the best of my knowledge, it has to be an approved earth ground, and I don't believe that the building super structure qualifies as an approved earth grounding source.
But I've been wrong before, and I'll be wrong again...:-)
ME
0
Comments
-
csst grounding
What is the grounding requirement for this pipe? I ask because I saw a non english speaking contractor running a ground from a steel I beam to a natural gas service.I asked around the site and this was grounding the csst pipe in the building.The gas service was plastic.
Thanks for any info Mike0 -
NEC
I believe you'll find NEC requires gas piping (and water piping, CATV & phone wiring, outside antennas &/or towers, etc.) to be bonded to the electrical service entrance grounding rod (single point ground)
This ensures *everything's* at the *same* ground potential particularly important if there's a lightning strike nearby.
Your fellow electricians should know for sure.
The utility feed may be (likely is) plastic to near where it rises out of the ground at the meter set, but this doesn't matter to the internal metallic piping/CSST.0 -
This content has been removed.
-
What about
Jumping a ground from CSST to the CW copper pipe , which acts as a ground for the electric??
To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"0 -
I understand the reason to ground the CSST, but what about flex connectors? I haven't heard or seen anything about them. They aren't that much stronger than CSST when lightning is concerned. As Singh mentioned, it's important to give a bit of distance between the CSST and any other conductor.
To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"0 -
Maybe
If you can catch the metal water service pipe where it comes into the building. That way you catch the water pipe bond to the electrical service,which takes you to the neutral/ground from the power company.
I would prefer the building steel which combined with the concrete is an excellent ground. My last choice would be a single driven rod as the resistance to ground could be quite high. Realistic if lighting was to hit a building it would do so because of the building steel which hopefully would guide the bolt harmlessly into the ground.0 -
I'll try to get a definitive answer
Going to an NEC 2005 seminar tomorrow evening.0 -
0
-
0
-
Read the mfg instructions!
SECTION 4.10 ELECTRICAL
BONDING/GROUNDING
1. Definitions:
Grounding: The process of making an
electrical connection to the general mass
of the earth. This is most often accomplished
with ground rods, ground mats or
some other grounding system. Low resistance
grounding is critical to the operation
of lightning protection techniques.
Bonding: The process of making an electrical
connection between the grounding
electrode and any equipment, appliance,
or metal conductor: pipes, plumbing,
flues, etc. Equipment bonding serves to
protect people and equipment in the
event of an electrical fault.
Equipotential Bonding: The process of
making an electrical connection between
the grounding electrode and any metal
conductor: pipes, plumbing, flues, etc.,
which may be exposed to a lightning
strike and can be a conductive path for
lightning energy towards or away from the
grounding electrode.
2. The TracPipe® gas piping system shall be
bonded in accordance with the National Fuel
Gas Code, NFPA 54/ANSI Z223. The piping
system is not to be used as a grounding conductor
or electrode for an electrical system.0
This discussion has been closed.
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 917 Plumbing
- 6.1K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements