Change a two pipe steam system to forced hot water can it be don
Would like to convert a two pipe steam system to forced hot water.What are the pitfalls, higher pressure as opposed to lower pressure, but house is three stories. THANKS
  • HitzKup_2
    HitzKup_2 Member Posts: 45
    Don't try
    You will be married to it for ever.
  • Only if you enjoy
    living dangerously. There are way too many things that can go wrong. Fix the steam.
    "Steamhead"
  • kamney
    kamney Member Posts: 15
    The radiation of the load is sized for stream - its undersized for hot water - drawback - you will be cold
    can you add - infloor or baseboard to make up the difference?
    Jamie Hall Member Posts: 26,846
    Specific drawbacks
    1. It will be WAY more expensive to convert to forced hot water than to fix the steam to work properly.
    2. You will have considerable replumbing here and there to get the circulation even vaguely even.
    3. You will have -- almost guaranteed -- serious leaks in both the radiators and the pipes because of the tremendous pressure increase (three stories? Looking at 20 pounds per square inch, min, vs. 12 ounces per square inch -- say 40 times the pressure).
    4. Why even think of it? Steam heats at least as well, if not better...