Chimney question. for new wood stove

Wayco Wayne_2
Wayco Wayne_2 Member Posts: 2,479
at my car dealership has a rental property where they want to install a wood stove in the basement to supplement heat. The installer said he was going to pipe the flu into the chimney for the oil furnace. He called me and asked me if this was all right. I said I didnt think so but I'd check here at heating help. Does anyone have knowledge in this area? WW

<A HREF="http://www.heatinghelp.com/getListed.cfm?id=255&Step=30">To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"</A>

Comments

  • Bob Harper_2
    Bob Harper_2 Member Posts: 54
    wood stove venting

    No, wood cannot share with any other fuels or appliances. You will need an insulated listed liner installed dedicated to just that stove.

    Get a chimney contractor or hearth pro in there before someone burns the house down. If they don't have a clue about the venting, they certainly don't have a clue about clearances to combustibles either.

    Hire a pro!
    Bob
  • hot_rod
    hot_rod Member Posts: 24,511
    wood heat in a rental property?

    that makes me nervous. It's not the best appliance for in-experienced users.

    CO, combustion air, over temp protection, plenty of issues to be concerned with.

    hot rod
    Bob "hot rod" Rohr
    trainer for Caleffi NA
    Living the hydronic dream
  • J.C.A._3
    J.C.A._3 Member Posts: 2,980
    WW

    Bob has the goods....Believe him! JCA
  • Wayco Wayne_2
    Wayco Wayne_2 Member Posts: 2,479
    Thanks for the help

    I knew but wasn't sure. Good to hear from folks who are. WW

    To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"
  • nick_7
    nick_7 Member Posts: 15


    In somwehat the same vein, I have an oil-fired boiler in basement venting to a masonry chimney that it turns out is shared with an open fireplace on the floor immediately above. anyone have an idea if there would there be adverse issues there in either proper venting of the boiler or in using the fireplace occasionally ? thanks
  • Bob Harper_2
    Bob Harper_2 Member Posts: 54


    If the oil boiler is truly sharing its flue with an open fireplace, both need to be shut down immediately!

    You can NOT share wood with any other fuel-period! You can NOT share an open fireplace with anything else-period!
    The oil appliance needs a dedicated flue suitable for the class of service. What you could do is reline the oil flue and block off the fireplace opening. Put flowers in the fireplace.
    Left as is, this is a suicide machine.

    Are you sure it shares its flue with the fireplace or are there two flues in one chimney: one oil flue and one fireplace flue? There is a huge difference.
    Bob
  • nick_7
    nick_7 Member Posts: 15


    I am pretty sure it is the same flue, the same opening, for boiler and fireplace. It has been that way for a couple of years. Is the problem possible CO? I have a CO detector right next to the fireplace that has never registered a problem. thanks
  • Jamie Hall
    Jamie Hall Member Posts: 25,632
    Wood flues

    get a lining of creosote. Fuel fired chimneys, particularly oil, get a lining of combustibles... either one can light off the other on the right conditions. If you're lucky, you have spectacular fire works out the top of the chimney. If you're not, you don't have a house any more.

    As the guys say: do not mix wood with anything else. No more than one wood stove or fireplace on a flue. Ever.
    Br. Jamie, osb
    Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England
  • Weezbo
    Weezbo Member Posts: 6,231
    Yes . Especially non existent MUA + :wood stove ,fire places....

    some very not good things can happen .*~/:)
  • Tom_4
    Tom_4 Member Posts: 16


    I was reading this post and I agree that you should not combine both oil and wood in the same flue. So why is it ok for companies to manufacture wood/oil combination boilers that use the same flue. I personally know many people with seperate wood fired and oil fired appliances in the same flue that have been that way for 20 to 30 years with no problems. As I said I do not agree with it as it could be a potential problem. Tom
  • Tom_4
    Tom_4 Member Posts: 16


    I was reading this post and I agree that you should not combine both oil and wood in the same flue. So why is it ok for companies to manufacture wood/oil combination boilers that use the same flue. I personally know many people with seperate wood fired and oil fired appliances in the same flue that have been that way for 20 to 30 years with no problems. As I said I do not agree with it as it could be a potential problem. Tom
  • Tom_4
    Tom_4 Member Posts: 16


    Sorry for all the posts. I keep getting error messages when trying to post a reply. Tom
  • Tom_4
    Tom_4 Member Posts: 16


  • check the top of the chimney

    you could have 2 flues in the same chimney. Bob Gagnon

    To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"
    To learn more about this professional, click here to visit their ad in Find A Contractor.
  • Tom_4
    Tom_4 Member Posts: 16


  • Tom_4
    Tom_4 Member Posts: 16


  • Tom_4
    Tom_4 Member Posts: 16


  • same flue

    It is a violation of code, a wood fire can create excessive draft over the oil appliance from what I understand. Some of the German dual-fuel boilers (Kunzel, and not approved in the States!) have a stack thermostat on the solid-fuel flue that is interlocked with the oil burner; when the solid fuel flue gases are over 140 F the oil burner is locked out.

    Pete
  • Bob Harper_2
    Bob Harper_2 Member Posts: 54
    inspection

    The point here is, you need a proper inspection. The very fact these issues have been raised is grounds for a Level II inspection, which includes visualization of the flue with a video or digital camera. If there are separate flues, you still need to know their condition. Most homes have one chimney like a double barreled shotgun: one barrel for the heater and one for the fireplace.

    The hazards include CO, fire, odors, and damage to the chimney. If this is indeed the situation, it must be repaired immediately. Also, the home cannot be sold like this as it constitutes a "hidden defect". Should anyone get hurt, you could become liable.

    Get a chimney inspector in there ASAP! Go to www.f-i-r-e-service.com to locate a qualified inspector near you.

    HTH,
    Bob
This discussion has been closed.