Unico system with Carrier Heat Pump
1 1/2 Unico system with a matching Carrier 13 seer heat pump 410A . Heat load is about 10kbtu's , air flow around 325 cfm's . Line sets insulated both (attic job) . We can only get a coil temperature of 42° F .Unico calls for around 35° f coil temperature . The subcooling is 12° . Any suggestions.0 -
Not in order
Overcharge unit,high humidity,too much airflow.
I'm seeing some of the newer equipment only running a 5 degree subcool temps.
0 -
Unico
Everything is set up to factory specs0 -
Try this
measure your suction line temps if its 18 to 20 degree below
return temps then she fine.Head to the next one.0 -
specs ?
Which factory ?? carrier or unico. I have been wondering how well the 13+ seer stuff was going to play with unico's. Might want to try wrapping up part of the condensor coil without pulling any of the charge out and see what happpens.0
This discussion has been closed.
Categories
- All Categories
- 86.2K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 99 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 915 Plumbing
- 6K Radiant Heating
- 381 Solar
- 14.8K Strictly Steam
- 3.3K Thermostats and Controls
- 53 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements