p-h calculator
scott snyder
Member Posts: 2
I was in you're class on saturday may 20. I would like you to calculate my findings so I can check to see if I did them correctly. I am working on a 5 ton rooftop AC. The head pressure is 250 the suctin pressure is 55 The liquid line temperture is 85 and the suction line temperture is 53. Can you send me the results on what you get so I can compare what I came up with Thank You.
0
Comments
-
check my claculations p-h calculator
I was in you're class on saturday may 20. I would like you to calculate my findings so I can check to see if I did them correctly. I am working on a 5 ton rooftop AC. The head pressure is 250 the suction pressure is 55 The liquid line temperture is 85 and the suction line temperture is 53. Can you send me the results on what you get so I can compare what I came up with Thank You.0 -
p-h
Scott, what are your indoor and outdoor temps?0 -
Thoughts
Like techman stated, more info would be nice. It almost sounds like you are under charged and dirty condenser coil. Besides temps in & out, what metering device do you have? If you have the older style Bryant RTU, they usually have the double pass coil which MUST be separated to clean! Cleaning just the outer coil will not work, thus my diagnosis. I really cannot tell w/o ambiant temps.
Mike T.0 -
What am i missing.
I'm seeing high subcool temps and high superheat readings.
Could it be a mild day or clogged cap tubes?0 -
Don
I can see your point, but without more info it's all just a guess. Especiall with say 65-70* outside, I think the head is hi.
Mike T.0 -
Suction line Temp
Are we dealing with a package unit, Scott, as with the others we discussed?
Is it safe to assume that the evaporator outlet temperature and the compressor inlet temperatur are prety close to being the same?
R-22 right? (I hope)
If so, it still looks like we have a liquid line restriction, which could include an underfeeding metering device.0
This discussion has been closed.
Categories
- All Categories
- 86.2K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 99 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 915 Plumbing
- 6K Radiant Heating
- 381 Solar
- 14.8K Strictly Steam
- 3.3K Thermostats and Controls
- 53 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements