Stupid homeowner questions.......
Constantin
Member Posts: 3,796
Some locations in the US have negligible heating loads due to the climate (think FL), super-insulation, passive heating, etc.
In my mind it also depends on the kind of usage. Constant loads require bigger boilers attached to storage than intermittent ones...For example, some homeowners want to fill a giant jacuzzi and take 3 bodywash showers at the same time...
Waste water heat exchangers can help scavenge some of the BTUs being flushed down the drain, but they only go so far. The real problem is delivering 10+GPM of flow at a 80°F ΔT.
So, I would sit down with the homeowner and determine what the usage patterns are. Instantaneous water heaters (dedicated or boiler-fired) have their fans, so do storage units. In my mind, both have their place.
I sized my boiler plant to the heat loss and probably could ahve gone down another size due because Manul J is very conservative. Conversely, the 80 gallon water heater being kept at 120°F has endured multiple showers running at the same time, w/o any issues.
Well, here I am again with a few clueless homeowner questions...If a wallie would open up shop in Louisville, KY, maybe I could get the information locally...:
I am considering a Trinity Combi unit to replace my giant 6 yr old Dunkirk boiler and standard hot water heater. If we make the switch, how should we supply hot water in the summer? Is it sensible to run the boiler all summer for hot water?
On the subject of boilers, do you have opinions about the Trinity units? How about the Utica UB95M-200 that is advertised here?
Thanks for any information you can share!0 -
Generally, Deirdre,
Low-Mass high efficiency boilers are an excellent way to produce abundant hot water in summer. Older style high-mass cast iron boilers by comparison take a while to ramp up to temperature so you can see the inherent inefficiency in that. My own boiler (Monitor MZ) has low water content and low mass so it can heat my tank from a cold start in about twenty minutes (tank at 50, water to 130). Once the tank is warm the "touch up" takes five minutes if that.
I will let others opine about the specific boilers you are considering. Each has their following and their detractors (cars, neighborhoods, airlines - everything has an opinion attached to it!). The others who may comment tend to be on the installation and service side, so see the full array from installation to warranty issues, service and support.
Hope this helps-
Brad0 -
further cluelessnes
Brad, I am guessing that the trinity is a low mass high effeciency unit??? Do you mean that in the summer we would wait for the boiler to come up to temp to heat the water when we needed it, or should we plan on a storage tank?0 -
Trinity
The Trinity is a low mass boiler with a plate type heat exchanger built in for the domestic hot water. You are correct in saying that the boiler will need to heat up in order to generate hot water, but that boiler only holds about a gallon of water (give or take), so the heat-up is meaningless.0 -
First, you need to make sure the combi uniit has the domestic hot water output you need. I think it's output isn't bad there, but on demand hot water often has limitations.
Secondly, there are better boilers in this class for heating; it's minimum modulation rate isn't so good and I imagine your heating load may not be particularly high?
However, I do believe it is pretty economically priced and will do a pretty good job. Depending on your total overall loads (including domestic loads), it may or may not make sense to use something a bit better with a storage tank for DHW that has a coil in the tank. The higher your loads, the more it makes sense to upgrade.
Personally, and maybe some of the other pros around here know better as I am not a plumber, I hate on demand hot water systems. Fluctuation in water temperatures at the fixture seems awful hard to avoid. But again I may not know best there. In fact, if anyone else knows how to make sure that does not happen, I'd love to know, because the coil in my boiler at home (ooooo I can't wait to tear that thing out) STINKS!!0 -
It takes a LOT of energy to "instantly" produce domestic hot water.
It takes an ENORMOUS amount to "instantly" produce domestic hot water in quantities greater than say one tub, one clothes washer or one dishwasher combined with anything more than a simple lavatory.
The flat-plate heat exchangers attached to some boilers definitely work--just make absolutely certain that you're aware of the flow limitations and NEVER oversize such a boiler just to meet the DHW load! In other words the boiler is FIRST sized PROPERLY to meet the space heating load and such sizing will define how much "instant" hot water can be produced.
Most modern high-efficiency boilers (and by "high efficiency boiler" I'm NOT referring to a conventional design with a flue damper and pilotless ignition) use what is called "Domestic Hot Water Priority". This means that the FULL output of the boiler is devoted to producing DHW when such is needed. The logic behind this is that DHW demands are usually short in duration and the house won't have a chance to drop too much in temperature while DHW is being produced. DHW priority can however be a serious problem if you've set your thermostat(s) down at night, turn them up when you wake, and expect to "get ready using DHW" at the same time the house is RECOVERING from setback!!!!
The solution to the problem of DHW demand higher than can be produced by a boiler SIZED TO THE HEAT LOSS OF THE HOME is storage. This is called "indirect" domestic hot water. Remember though that your high efficiency boiler wants to give priority to DHW. This means that the heat exchanger in the indirect tank must be capable of transferring heat from the boiler just as fast as it can be produced at maximum boiler ouput. This ability does not come without significant expense--think $$$$ because heat exchanger surface does not come cheaply! For that reason, I recommend only the finest quality indirects that will likely outlast you AND your children. The heat exchanger in my big horizontal Viessmann tank looks like the bottom and sides of a coffin made from 1 1/2"? stainless steel tube--if my body would fit through the 4" or so inspection hole, I'd say bury me there...
The typical alternative is a stand-alone DHW heater. They're cheaply made, short lasting, poorly insulated and terribly inefficient with natural gas, but they're cheap and easily replaceable by even a basic handyhomeowner.
Really?
So, if in July I want to wash a load of whites in hot water, when I turn the washer on, how long before the water flowing in is hot? Or, for a shower that flows at 3 gallons a minute, how long before the water is hot
The heat load on the house is pretty high-- it is a big, old house (the boiler will be heating 4,000 of the 6000 sq. ft. total). I think the heat loss is aproximately 100,000 btus (don't tell me to get a manual J, NO ONE in Louisville will do one).0 -
If the load is that high, investing in a better heat source might be worthwhile. If it's THAT high, I'd be thinking viessmann or other very high quality boilers.
For a house that big, your comment about time to heat raises an interesting point. You probably have some really long hot water runs to some fixtures, right? So you probably want a hot water recirculation system or you'll be standing there all day waiting for the hot water to make its way through those long lines.
Recirc and on-demand hot water do not mix. Storage tank it is, in that case.0 -
By better heat source, do you mean higher AFUE? They all seem so high-- Does the 94% rating of the Veismann really make a huge difference over the 92% of the Trinity? The Trinity unit is about 2800, but I can't even find a quote on the Viessman-- They seem to have a no direct price quoting policy and forbid internet price quoting as well. My GUESS, based on the sales pitches I am finding around is that there price is much, much, higher, mayber 5,000 for the same load size..... Will that 2% improvement in fuel effeciency ever get back that difference? Or, do I not understand what the true effeciency of the two units are?0 -
Dear D
I admire your determination to understand what you are buying. Keep it up! You'll get it, especially if you hang around here and keep asking "stupid homeowner questions"
I would be a little concerned with the DHW output of the Trinity for a house the size of yours. You probably have at least a couple bathrooms and if by chance both showers were being used at the same time you would likely run out of hot water. If you can control your hot water usage to a point where you never use more than 3-4 gallon per minute it may work OK for you. I have seen however, far more people disappointed with this type of hot water production than not.
I feel that a good quality indirect water heater fired with a high efficiency condensing boiler is about as good as you can get. This would be considering recovery time, initial dump load, (filling a tub while running the washing machine etc.) and system efficiency.
IIRC you were working on a two temp system using radiant floors and a higher temp for rads or hydro air? If so, copy and paste this address and go to page 29. It will show you a piping schematic of how an indirect ties into a boiler and give you an idea of how it works. This particular drawing is from the Vitodens installation manual but the concept would be the same for other boilers also. You can also see the various components that are required to achieve the multiple temps needed for your system. It's not as complicated as it looks. Just follow the water flow through the system as it leaves the boiler on the left. Please feel free to e-mail me directly. I'm a little far away to do an install for you but if I can help you with some advice I'd be happy to give it. I'm picking up a pretty strong vibe that you are trying hard to sort out the wheat from the chaff. Keep asking questions.
http://www.viessmann.ca/web/canada/ca_publish.nsf/AttachmentsByTitle/docVitodens200big-ii.pdf/$file/Vitodens200-44-60-ii.pdf
Being that this is the whole manual, the file is fairly large (2+Mb) so it may take a while to download if you don't have hi speed.0 -
so mike, even in a case where HW load exceeds
heating load, your rule still holds, yes?--size to heat load and then add adequate storage? I've heard contractors say in that case they increase boiler size.
David0 -
The Trinity boilers are fine, not the best, but fine. I have installed many of them with no more problems than I have with any other boiler. A Buderus is a good step up. I would use a storage tank to store your hot water. I do not think much of the combo unit. Use it only if you do not have room for a tank.
Dave in DenverThere was an error rendering this rich post.
Heat Loss Calcs
can now be done on a PC. I'd bet that every pro in this thread has a heat-loss program- from the simple (and free) Slant/Fin program to more complex ones like Wrightsoft. If you wish, click on "Heat Loss Calcs" in the bar above and you'll be linked to Slant/Fin's site, where you can download the program (if you have a broadband connection) or order it on CD-ROM.
If you don't calc, you're guessing!
Residentially when driven by a high-efficiency boiler, yes.
I got to my "guess" by using an online room by room calculator.
Yes, it is a long way to the third floor bathrooms! So, we do wait about 45 seconds for hot water up there. Fortunately, the plumbing was designed to run straight up through all three floors, a pretty straight vertical line from the water heater to the kitchen, laundry and baths. A recirculator is on our list of "nice to have in the future", but not on the priority list for right now.
Our current set up is a 200,000 btu Dunkirk and two gas fired hot water heaters. The priority is getting more effecient by dropping to hopefully, one right sized unit to handle heat and hot water. Which brings me to: Do you up the size of the boiler to accomodate hot water production? I get the impression that we are supposed to size the boiler to solely the heat load-- but if that is the case, how is the hot water being supported?0 -
Deirdre- Storage of DHW
I am glad the others responded as they know the equipment far more intimitely...
I did not know that the Trinity as described had an integral plate exchanger for so-called "instantaneous" HW production. Personally I do not prefer that method.
Rather, I was thinking (forgive me, assuming) an indirect; a large coil within a storage tank.
If I had a boiler with an integral plate exchanger, I most certainly would install a Super-Stor or other storage device. The flow rate of the plate exchangers is rather fixed and geared to one major appliance (laundry OR shower) at any one time, but not both.
What I love about The Wall: Like several coats of paint, everyone chips in until things are covered.
Brad0 -
Well part of the equation is, how often will you get your AFUE?
Trinity's minimum modulation rate (a good rough threshold of when you can expect to really start getting your efficiency) is approximately 50% higher than several other modcon boilers out there such as the Ultra, Munchkin and Vitodens.
It's not a bad boiler.. certainly better than the dunkirk you have now.. but there are better and other than the vitodens, the price differential may not be that much.
Of course if the other units are not easily servicable in your area (i.e. no one is using them) then by all means get the trinity and be happy with it!
I may just be a bit of purist here.. maybe you should just ignore me
The last word
Vitodens.
Nearly everyone here who has used a high-efficiency modulating/condensing boiler will tell you that, when properly installed, they ALL produce efficiency MUCH higher than implied by AFUE. The standards for AFUE simply do not consider how the boiler actually operates when heating a structure.
As a breed, condensing/modulating boilers are very efficient--but they ALL must be properly installed and controlled.
For the highest possible efficiency, these boilers need to run for the maximum possible length of time using the minimum possible supply temperature.
The minimum possible supply temperature part of that statement is the most important and it is GREATLY influenced by the emitters used in the system. The best emitters are not only capable of operating at low temperatures, they are also capable of extracting a maximum amount of heat from the water.
Not all systems will be able to take full advantage of these boilers. As the systems to which they are connected become less suitable, they become less and less efficient--eventually hitting a point where they are not much better than simple traditional boilers.
Emitters in general order of suitability:
1) Radiant floors/walls/ceilings with either tube in concrete, heavy aluminum conduction plates or Warmboard.
2) Free-standing iron radiators--particularly in systems that were originally gravity hot water.
3) Modern panel radiators, recessed iron convectors, cast iron baseboard.
4) Fin-tube baseboard.
5) Radiant floors/walls/ceilings using either bare tube or "flashing-like" plates.
6) Hydro-air.
In a system with mixed emitters it is EXTREMELY important to understand that system efficiency can be no better than allowed by the least suitable emitter!!!!
Hydro-air in particular can be especially difficult to use efficiently with these boilers. I know that some will disagree, but I have been told by multiple people on the technical side of things that such systems are usually a waste of a fine boiler. It's not impossible to use hydro-air with a condensing/modulating boiler and still have tolerable efficiency, but it does require high engineering skills. In your case I suspect you'd either have to fly in a highly experienced heating design engineer or study, study, study, design yourself and specify to a local firm.0 -
I believe your house is large and old, correct?
If so, ANY properly sized boiler with have quite a lot of output--just not enough to instantly meet a domestic hot water demand of much more than a single hot shower.
Indirect domestic water heaters just look like tanks. But instead of having a burner and a flue (like in yours), they have an internal heat exchanger the connects to the boiler.
As mentioned, most high-efficiency boilers produce domestic hot water on priority--DHW gets the FULL attention of the boiler when called for. Just like your current water heaters, the boiler cannot meet a large demand INSTANTLY, but water hot water is stored in the tank, drawn from the top with replacement water going to the bottom. Because hot water rises--just like hot air--you get significantly more hot water than can be instantly produced. The capacity of the indirect domestic water heater should be based on a realistic estimate of peak demand. And again, since the indirect is usually supplied via priority you want an indirect that can instantly absorb the FULL output of the boiler.
Be forewarned that if this system uses hydro-air and if you set back the thermostat at night and expect the house to warm while everyone is doing their morning business, you will probably be very disappointed.0 -
Mike
I'd agree that hydro air doesn't take full advantage of the efficiency these boilers are capable of. However, I've done a couple systems that are "blended", using rads or floors at low temp and the H/A at whatever it needs. If you arrange your piping correctly, you can use the low temp return to drop the return temp from the H/A before it gets back to the boiler. Obviously there are other issues that come into play, such as both circuits running at the same time and GPM flow in each, but with a little planning you can kinda morph them together into a nice low return temp.0 -
Steve
Your "blending" sounds like a good application by a great and practical engineer. I was thinking of entire zones heated solely via hydro-air where most or all circuits are frequently running at the same time.0 -
matching indirect to boiler.
Mike, from your post the other day, "Remember though that your high efficiency boiler wants to give priority to DHW. This means that the heat exchanger in the indirect tank must be capable of transferring heat from the boiler just as fast as it can be produced at maximum boiler ouput."
(Such a great thread by the way.)
So how is the capability of said indirect tank heat exchanger to transfer heat from the boiler AT MAXIMUM BOILER OUTPUT calculated? So e.g. if one gets a mod con boiler that modulates from 20k to 80K firing rate and you know your peak need will be saturday morning with two laundry loads and two 15 minute showers in the first hour what kind of specs are you looking for in the indirect?
Thanks,
David
I wonder how many installers out there actually measure this out.0 -
Size the tank not the boiler
If you know going in that you have a big dump load of hot water such as a two person tub or that the scenario you brought up occurs regularly, you account for that with the tank volume. Sizing the boiler to provide 5, 6, 7 GPM will nearlly always result in severe oversizing. Best to allow for that with the tank and let the boiler do its thing at a normal pace.
The Vitodens has a sweet feature that will keep it in condensing mode nearly 100% of the time while making domestic HW. It can be programmed to maintain a temperature a certain level above the domestic tank while in DHW mode. I think 36* is the default. So if your tank is at say 90*, the Vito will fire to 126*. After hitting that 36* differential target, it will modulate down and keep that same delta T as the tank temp comes up. So, if you have a tank setpoint of 120*, the Vito will finish off at 156*. With a normal 20* drop, that's still right at condensing temp range. After hitting the tank setpoint the Vito will purge the excess heat from the boiler into the DHW tank and reurn to heating mode. Nice.0 -
An excellent disscusion in this topic. Thanks0 -
First thing to figure out is how many BTUs you're going to consume in that hour.
Let's say the top of the indirect where you draw the water will average 130°F for that hour.
Then let's say that the cold water is 55°F.
I consider 115°F a hot shower--some like it hotter--but I'll still use 115°F.
Assuming you're using a single, standard showerhead and haven't removed the flow restrictor, you get about 2½ gpm for a shower.
(130° * 2 gpm) + (55° * 0.5 gpm) = 287.5
287.5 / 2.5 gpm = 115°
So, you need 2 gpm of hot water @ 130° for your 115° shower.
2 * 15 minute showers = 30 minutes.
30 minutes * 2 gpm = 60 gallons.
60 * 8.33 pounds per gallon = 500# of water.
Each pound had to be raised from 55°F to 130°, a difference of 75°.
75° * 500# = 37,500 btus in 30 minutes for the showers. To meet this load instantly the boiler would have to transfer heat at a rate of 75,000 btus per hour.
Now, let's add in the washing machine. I'll assume two full loads--one with "hot" wash, one with "warm", both with "cold" rinse.
Wash cycle will take about 15 gallons of water. I'll assume the solenoid mixing valve will flow 3 gpm straight "hot" and 5 gpm (2.5 each) "warm".
Your hot load will fill in 5 minutes. 15 gallons * 8.33# per gallon = 125#. 130° - 55° = 75 btus/#. 125# * 75 btu = 9,375 btus in 5 minutes. "Instant" satisfaction would require 112,500 btus/hour.
Your warm load will fill in 3 minutes. 7½ gallons of this are hot. 7.5 * 8.33# = 62.5#. 130° - 55° = 75 btus/#. 62.5# * 75 btu = 4,688 btus in 3 minutes. "Instant" satisfaction would require 93,760 btus/hour.
So, the peak flow will be 2 gpm for the shower + 3 gpm for the clothes washer (hot load) = 5 gpm. Using the btu/hour rates required for each this would mean that for "instant" satisfaction, the boiler would have to transfer energy at the rate of 112,500 + 75,000 = 187,500 btu/hour. Unless this is an extremely large and/or extremely "leaky" home, a properly sized condensing/modulating boiler will likely have less than half of this output ability.
The solution to the problem is storage. How much?
Let's say the boiler is capable of transferring heat at the rate of 75,000 btu/hr to the indirect while operating at nearly full output.
In this "peak load" hour, we consumed 37,500 + 9,375 + 4,688 = 51,563 btus. WELL within the capacity of the boiler to fully "recharge" the indirect. At 75,000 btu/hr it would take the boiler about 41 minutes to replenish.
You might be thinking, "I don't need storage." WRONG! During one 15 minute period (shower & hot load of clothes) you consumed 18,750 (shower) + 9,375 (clothes) = 28,125 btus but the boiler could only transfer 1,250 btu/minute * 15 minutes = 18,750 btus. There is a deficit of 28,125 - 18,750 = 9,375 btus.
Where do those 9,375 btus have to come from? Storage!
Each pound of heated storage water has 130 - 55 = 75 btus available for use. 9,375 / 75 = 125# of water. 125# / 8.33 = 15 gallons.
Does that mean you only need a 15-gallon indirect tank? NO! Why? Because as you use the hot water in the tank, it's being replaced with cold and that water can't be heated to temperature as fast as it's being added! Fortunately, hot water naturally rises in a tank. The fact that you draw from the top and replace at the bottom enhances the effect as the water doesn't get too much opportunity to "mix" in the tank--it stratifies.
Let's say that the top 1/2 of the tank stays well within temperature. That means you need 15 * 2 = 30 gallons of storage. (Would those with more experience please comment on that "top half" estimate?)
Let's say now that those two 15-minute showers occurred simultaneously and see how things change.
37,500 btu required for the showers. 18,750 btus available from the boiler for a difference of 18,750 btus from storage. 18,750 / 75 = 250#. 250# / 8.33 = 30 gallons. 30 * 2 = 60 gallons of storage.
VERY important to remember that these calculations assumed that heat at the rate of 75,000 btu/hr can be transferred from the boiler to the indirect! This is well within the ability (even at a quite low and efficient supply temperature) of the 42-gallon (smallest) Vitocell-H 100. But not all indirects are Viessmann... Check ratings! With all else equal, a lower heat transfer ability will require more storage. This is what I was talking about when saying that the indirect should be fully capable of instantly absorbing the full boiler output!!! If it can't you need more storage and much more importantly this means that if domestic hot water priority is used the boiler will have to devote itself to DHW for a longer period of time. While this is happening you do not get space heating!0 -
Now I Need a Bit of Help/Advice re. Indirects
I'll be installing my 120-gallon Vitocell-H 300 soon.
With a domestic water temperature rise of 50° to 140° and 158° supply temp to the HX, it can transfer 133,000 btu/hr.
The boiler is a Vitodens 6-24 with maximum rated input of 91 mbh and CSA rated output of 81 mbh. Obviously the indirect could completely absorb the output of a significantly larger boiler...
The domestic hot water system uses gravity recirculation AND supplies a hydronic towel warmer. The towel warmer is always kept fully loaded. I'll estimate 1,500 btu/hr to drive the recirculation and towel warmer. Does this sound like a realistic estimate?
At 140° and at the conditions given above, the indirect stores 90 * 120 * 8.33 = 89,964 btus. 120 gallons = 1,000#
At 1,500 btu/hr load the tank temperature will drop 1½°F each hour not counting stand-by loss which I believe is assumed to be about 1°/hr.
So, let's say that the tank drops 2½°F each hour from "standby" load plus "standby" loss.
What sort of DHW settings should I use on the boiler?
Should I maintain the tank temperature quite tightly and with a quite low "fixed DHW supply temp" setting--perhaps as low as 145°F or so? Am I correct to believe that this would result in a low firing rate to meet the "standby"
while still allowing full boiler output during a peak demand situation when the tank temp is trying to drop rapidly? At 6 gpm it takes 27° temp drop for 81,000 btu/hr. Is it realistic to believe that during high demand (say 10 gpm) with a 145° HX supply temp that water would be returning to the boiler at 118°???
Will the scheme break down with normal demands (say 3 gpm) requiring an extended recovery time?
Have I flipped out again thinking I can actually heat my DHW to 140°F with 145° supply water???
Your great response should be in hot tech topics
Thanks so much. Hope Deirder's still with us. I'm inspired to go right now and buy another $10 brick to support the site. Also for Mr. Ebels post on same subject and Brad's post on an AC thread that explicitly outlines how to AC a basement with a portable unit. Hope homeowners appreciate all this free expert advice.
Thanks, I'll be digesting your post later this afternoon.
David0 -
You're quite welcome. If you find any math (or other errors) please let me know! Logic should all be correct, but it's easy to screw up a number!0 -
The large size of your 80 gallon indirect I guess allows you
to keep the water at 120deg (less fuel usage), rather than a 40 gallon tank at 140+ degrees yes? Then you don't need an anti-scald valve. Some on the wall recommend keeping water at 140 to avoid Legionaire's etc. Is that a widespread recommendation? Does the anti-scald cut down on water flow as I've heard? (though the higher temp increases output I know since you can mix more cold water with it.)
Thanks,
David0 -
Good Points...
... lower internal temperatures allow the standby losses via the water heater to be reduced. On the other hand, my 80 gallon tank will have a lot more surface area than a 40 gallon unit, so I'm not sure which would come out ahead in terms of standby losses if the insulation in both tanks were similar.
We have an anti-scald valve, just in case I go back to setting the boiler to heat the IDWH to 140°F+ every 4th boiler cycle, the way that the Vitotronic allows me to.
Any bend, fixture, etc. in the way of the flow of water will cause some pressure drop. We have a rather large Leonard valve on our hot water supply, and I'd like to think that subsequently the losses through it aren't that bad.
Thanks to the pressure pump, we now have 55psi of water pressure in the house. Showers seem to supply plenty of hot water, even with the MA-required anti-scald additional T&P valves further downstream... I guess they're there to ensure that bath-tub fills do not get too hot.0 -
Thanks All!
I was out of town for a few days and just returned to all the info posted above. Thanks everyone for all the discussion, even if a significant portion is above my head....
I have gathered that you all think I should consider something more efficient than the Trinity and add DHW storage tank.
Can you guys suggest the best combination of equipment that would be a)reasonably effecient b)reasonably priced and c)relatively easily installed by a plumber who also holds an HVAC liscence but who probably isn't up on the latest technology?
I guess the most complicated thing is my bizarre mix of radiators: 600 square feet of pex in concrete in kitchen and downstairs baths (hi use areas that we would like to keep cozily warm), 700 square feet of suspended pex (no plates) under hardwood in formal living/dining (rarely used space), traditional cast iron radiators in guest bedroom, office and sunroom (with bypass valves). In addition, we are considering adding baseboard heat and a hydonic towel warmer on the second floor (currently served by a gas furnace).0 -
it may be time to get a pro there in person
I was wondering where you were with all these posts piling up. I'm a fellow homeowner, but it strikes me that so much info has been given it may be time to get a pro down there. I know your being in Louisville may be a problem. But go to find a pro on this site, put your zip in and call a few of the pros closest to you--even if they're in different states, and ask them if they know good people around where you are. Or call the boiler companies and ask for their distributors closest to you who might know contractors or supply houses who would know contractors. However I have to say the Wall would be a better reference in my experience. You can always come back and post any plans that are offered and get wallie feedback.
good luck,
David0 -
Your mix of radiation will certainly complicate matters. I easily see a three-temperature system. Lowest will be the tube-in-slab. Middle will be the iron radiators. Highest will be either the suspended tube or the baseboard but they are unlikely to be both well-served by the same curve even if they can use the same maximum temperature. In that regard it's almost a four-temp system...
Search and search for a knowledgeable pro--it will take such to even begin to meet your goals of reasonable efficency, price and installation. Do be aware that you're talking about a rather complex system. Complexity adds to price (materials, design and labor) so meeting your other goals means that "reasonable" with regards to price is relative to that complexity.0 -
Finding a pro......
There is only one wallie within a 100 mile radius (the largest search criteria) of Louisville and they don't do boiler work.....
The companies that I have been referred to locally haven't been remotely interested in designing a system for me. Or performing a heat loss calculation. Only one came back with a bid-- $40,000 to replace the boiler and put in a massively oversized unico air system. I have found an older man who both a plumber and an hvac guy that I feel I can work with if I gave him a design.
Perhaps what I want, like so many other "cutting edge" technologies, simply isn't available in Louisville.0 -
maybe that's the way--hire a wallie to design
and have your local guy do it. from the wall and elsewhere you can probably get photos to help you out. And your taking photos of certain areas would help in the design and to check at various stages of completion. Perhaps it might be worth it to pay that 100 mile away wallie to come out once to survey. Or someone he knows near you. I think you figured out your own solution.
Best,
David0 -
PS Perhaps you can do your own heat calc
Since you seem really motivated and pretty well informed I thought perhaps you might consider doing your own heat calc. Most wallies use software, but I've been using the Hydronics Institute's Heat Loss Calculation Guide H-22 that you can do manually--a simplied version of the full Manual J. Probably need a little help from the Wall to fully interpret your input data, but it's doable in five or six hours. Even if you later have a pro do it it's good as a comparison and backup.
Before you blame the lack skill of the locals, don't forget that the system you propose as well as your stated goals require a very high degree of hydronic artistry. There will be many ways to "balance" efficiency, comfort, cost and complexity in this system with concessions made to at least one of those criterion.
Please understand that I offer the following as a sincere assessment--I'm not chiding you. I'm just trying to help you see how you must consider everything as a working, complete system.
It appears that you're creating difficulty for yourself. Isn't the slab portion new or a planned addition in the short term? If so, your choice of tube-in-slab complicates matters greatly. You're adding yet another wholly different form of emitter to a system that already seems to be pieced together.
Did you inheret the heating system in its current form? If not, what have you added/changed? The bare tube radiant floors? If so, again, this was not the best choice considering your cast iron radiators. Placing the tube in nice heavy extruded conduction plates would have been a much better choice even if the initial cost was higher.
Why the furnace on the 2nd floor? Were radiators removed or was this previously an unheated area renovated into living space? Since you already have ductwork there, have you considered a traditional A/C system for the 2nd floor? Depending on layout such may even be able to serve much of the ground floor with relatively minor modifications and only requiring a small (perhaps even a simple mini-split) for your kitchen addition.
Also, did you remove radiators in the areas with the bare-tube staple-up? If so, do you still have them? Since those rooms will be little-used, it may make things simpler (and even more comfortable) if you replace the radiators and abandon the radiant. It might also be possible to use the radiant for a "base" heat level with radiators handling high loads and/or relatively quick heat if you plan on keeping these little-used spaces cooler than the rest of the house.
I do understand your desire for "cutting-edge" technology, but such technology is MUCH more involved than just using cutting-edge equipment! "Cutting-edge" technology is system based! EVERY component must work together to produce order from chaos. With the system you propose it's a tall order just to reduce the chaos caused by your wild mix of emitters--let alone the weather and your comfort desires.
How I got into this mess.....
Mike, you bring up excellent questions. In my desire to be brief, I have left out lots of background info. Much of our system was inherited from previous owners: When we purchased the house the first floor was served by a 300,000 btu ancient gravity fed boiler and window ac. The second floor was/is served by a gas furnace and 4ton ac system (with ducts in the 11 foot ceilings). The third floor was/is served by a gas furnace 2ton ac system. The house was originally built as single faminly in 1882 and was converted to duplex in 1910. We have owned it for 8 years, renting out the first floor unit for 7 years and now converting it to single family.
We have made these changes: 7 years ago we replaced the ancient boiler with a 200,000btu Dunkirk Plymouth Extreme. The unit was chosen and installed by ONLY residential boiler man we could locate at that time.
Last year, when we began taking the house back to single family, we put in the radiant floor. The system was designed and installed by a very well regarded local contractor who specializing in historic homes. Yes, NOW I know that it was a terrible design (trying to figure out what was wrong was how I found heatinghelp.com), but I trusted the people I hired. Honestly, I think they feel pretty bad about it too (I owe them a balance of $4,500, they have told me to pay them that balance if I am pleased with the floor's performance next winter). No, I didn't save the removed cast iron radiators and reinstalling them isn't really an option. I am exploring supplementing the heat in those areas. I am ok with those rooms being significantly cooler than the rest of the home most of the time.
I don't have expectations of acheiving a perfectly balanced system -- just something more effecient that what I have!0 -
Is this the solid brick three-story Victorian?
Am I correct that the immediate problem is an underperforming system that's extremely expensive to operate?
Even your new boiler is likely GREATLY oversized for just the ground floor when there is occupied and heated space above.
If the current system is set up anything like I imagine (poorly I'm sorry to say), I can see some SERIOUS problems.
Your bare-tube radiant floors want HIGH temperature. If this is the house I'm thinking of and the rooms served are the front ones with the big, curving windows it's likely that the floors have insufficient output potential even at the highest practical supply temperature of around 190F.
What this means is that the radiant floors can't put out too much heat--WAY, WAY, WAY, less than the boiler produces. BUT, the thermostat serving the radiant rooms is likely calling almost constantly as it's rarely satisfied.
When this happens the boiler short-cycles LIKE MAD. This spells DISASTER for efficiency.
In the meantime the portion heated by radiators also needs heat. Considering this is a gravity conversion, as soon as it calls, it will INSTANTLY absorb nearly every available BTU from the boiler. Your return and supply temperature will drop LIKE A ROCK. The radiant portion that needs high supply temperature will now have almost nothing to work with.
One possible way to deal with your radiant floors is a buffer. A buffer is nothing but a tank of water that STORES heat. This is VERY similar to domestic hot water and the exact same principles apply. You can heat that buffer tank to the highest practical temperature and then draw energy for your bare-tube floor with its return going back into the tank. You'll want to store at least 30 minutes worth of energy in that tank at design load before the TANK calls the boiler for a "recharge".
See how complicated this is becoming?
You seem bright and interested. Go to www.hvaccalc.com and buy the "homeowner" version of the heat loss program. This is a VERY easy to use program! Spend some time with CAREFUL measurements and reasonable assumptions regarding construction. A well-labeled sketch of each floor plan with windows and normal ceiling height included will GREATLY assist you and such shouldn't take more than a few hours.
- 167 Indoor-Air Quality