Weigh in of charges
TGO_54
Member Posts: 327
I will check the sub-cooling (TXV valve) after seting the charge by weigh in.
<A HREF="http://www.heatinghelp.com/getListed.cfm?id=278&Step=30">To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"</A>
<A HREF="http://www.heatinghelp.com/getListed.cfm?id=278&Step=30">To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"</A>
0
Comments
-
Weigh in of charges
Hi Professor,
When using the weight in method of charging do you need to figure the suction line as well as the liquid line? Will this change with different equiptment? I read through the installation guide for a new system, and it gives a chart for the addition of refergerant as .60 oz per foot of 3/8" liqid line but nothing for the suction line. What's the right thing to do?
Thanks
To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"0 -
Liquid
Although the entire system as a whole counts, you are only adding measureable ref. weight to the system as per manuf. charts because the liquid is measureable. Suction line is vapor so it is not considered. The addition of length to the L.L. is the actual chart you are adjusting to. Exmp...Longer or shorter. Keep in mind that the only true way to check is to measure sub-cooling or supper heat which ever applies.
Hope this was helpful.0 -
Thanks Mike
> Although the entire system as a whole counts, you
> are only adding measureable ref. weight to the
> system as per manuf. charts because the liquid is
> measureable. Suction line is vapor so it is not
> considered. The addition of length to the L.L. is
> the actual chart you are adjusting to.
> Exmp...Longer or shorter. Keep in mind that the
> only true way to check is to measure sub-cooling
> or supper heat which ever applies. Hope this was
> helpful.
To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"0 -
I don't trust the factory
I've seen them come low & high. Yesterday's unit had 50' lineset so you'd think we would have to add. Yet the superheat chart said remove some. I've never bothered with weighing in. Start it up and use the mfrs. chart to adjust.0 -
For the most part...
For the most part, the factory charge is reliable, biut I have come across a number of instances where the charge was not correct.
As you mentioned, Tom, definitely check the other system operating parameters to make certain that, once YOU are finished, you know for a fact that the system is charged properly.0
This discussion has been closed.
Categories
- All Categories
- 86.2K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 99 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 915 Plumbing
- 6K Radiant Heating
- 381 Solar
- 14.8K Strictly Steam
- 3.3K Thermostats and Controls
- 53 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements