sq ft EDR for baseboard steam?

Phil_6
Member Posts: 210
cast iron baseboard is 3.4/linear foot
slant fin type with 1-1/4 steel element is 4.0/linear foot of element
slant fin type with 1-1/4 steel element is 4.0/linear foot of element
0
Comments
-
How do I...
calculate the EDR (sq feet) for baseboard steam? The steam radiators are easy enough with the tables at various sites (height, number of columns, sections etc), but I don't know what to use for bb steam/ linear foot.
This is a one-pipe steam system, with mixed radiators/baseboard. I'm trying to get an idea of how big a replacement boiler I might need.
Thanks for any info.
Bill D.0 -
Thanks
Thanks for the info.
Bill D0