zone valve rating
Michael J. Brennan
Member Posts: 29
Hey Carol, my question is which amp rating am i looking for w/a honeywell zone valve model V8043E1012, to figure how many of these zone valves i can put on a 40VA transformer, the only amp reading i can find on this valve is 4.4A... Is this the right rating? or does this valve have another rating that maybe i am not seeing?? This number seems kind of high to me, 4.4A X 24V = 105.6VA.. I must be missing something here, hope you can help...thanks
0
Comments
-
4.4A
Must be the end switch rating. The motor is usually around .35A 40/24= 1.66A 1.66/.35=4.74valves - I would use 4 valves per.0 -
Mike
The 4.4 is the end switch contact rating @ 120 vac. This particular valve's power consumption is 7.7 VA each valve. Honeywell.com has a great web sight that you can fill the model zone valve you have and it will give you all the info you need on that valve.
MIke T.0 -
The V8043E1012 is .32A. Multiply that by 24V and you get 7.68VA. Divide the 40VA of the transformer by 7.68VA for the zone valve, and voila, you get 5.2, which rounds back to 5 zone valves.
Sort of related is this thought--VA and watts are exactly the same thing--volts x amps. It seems that when we have a resistive load, the industry calls it watts, and when it's an inductive load (motor) it's called VA.0
This discussion has been closed.
Categories
- All Categories
- 86.2K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 99 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 915 Plumbing
- 6K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 53 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements