wet rotor pumps in series
Plumdog_2
Plumdog_2 Member Posts: 870
four pumps, two in series above two more in series, and the two pairs are parallel piped. I saw it and I thought "why"? Why not just get one proper pump and quit screwing around?
  • Wet Rotor pumps in series
    When "stacking" wet rotor pumps in series, it is my recollection that you increase the GPM pumping through the system. Is that correct?
  • kevin coppinger_4
    kevin coppinger_4 Member Posts: 2,124
    I don't think...
    so..You increace Head...GPM is if you do them in parallel....kpc
  • Brad White
    Brad White Member Posts: 2,399
    Kevin is correct
    Series mounting increases head (pressure) at about the same flow. Parallel increases flow at a common pressure. Not the same pressure as one running but a common pressure where they both settle in equilibrium.
    EDIT: As noted below, each follows their curve but stacking the circulators is no way to double your flow if that is your goal. In the end, if you need that much head, I think you have too much pressure drop. :)
    -Ernie White, my Dad
  • Norm Harvey
    Norm Harvey Member Posts: 684
    That's always looked so cool to me. I think when I finally convert my new house from warm air to hot water I'm going to buy some of the tiniest tiniest circulators I can find and stack them,.. just because I CAN!
  • ALH_4
    ALH_4 Member Posts: 1,790
    flow and head
    It depends on whether you have an existing system or you get to design the system the series pumps are connected to.
    If you have an existing system, you are stuck with that system curve. You can only shift the operating point along that system curve.
    If it is a new system and you get to control the system curve, you can make anything happen.
  • Uni R_3
    Uni R_3 Member Posts: 299
    Come on guys...
    Same flow at an increased head? If you put 2 pumps in series the flow will be increased. The combination will have a curve more like a larger higher head pump, but the flow will not stay the same.
  • Norm Harvey
    Page 190-192 of "Modern Hydronic Heating" by John Siegenthaler
    It uses an example of two 7.6 gpm circs producing 10.5 gpm in series at double the head.
  • bob_50
    bob_50 Member Posts: 306
    What happens when
    you pipe them in parallel and wire them in series? ;)
  • Brad White
    You are right Uni
    Not exactly the same flow but not doubled. Each does follow their curve and each curve is different. Thanks for checking in.
  • Larry Weingarten
    Larry Weingarten Member Posts: 4,071
    Um...
    ... Less. ;~)
  • Mitch_4
    Mitch_4 Member Posts: 955
    then
    you are doubling the flow at half voltage due to double voltage drops, decreasing the rotor speed at a ratio inversly proportional to the electrical resistance of each winding to a factor of 1/x where x= the inrushing current not allowing for the slight shift in phase.
    honestly don't know.
    if you cant dazzle em with brilliance..baffle em with....
    mitch
    Jamie Hall Member Posts: 27,260
    and the objective
    of the exercise is to match the pump(s) to the system, so that the pump(s) are operating at their best efficiency. The key to adding the things up is that if you pipe them in parallel, both pumps will operate at the same total dynamic head, and the flows from the two pumps (which will be the same, if the pumps are identical) will add. If you pipe them in series, the flow in the two pumps will be the same, and the total dynamic heads will add.
    In either case the system will operate at the point where the combined pump curve crosses the system flow/head curve; you will likely have to draw them both on the same graph to find out where that will be (I always do...).
  • jim lockard
    jim lockard Member Posts: 1,059
    with the flow check
    open you get heat, flowchecks closed you get cold.