wet rotor pumps in series

Plumdog_2
Plumdog_2 Member Posts: 873
four pumps, two in series above two more in series, and the two pairs are parallel piped. I saw it and I thought "why"? Why not just get one proper pump and quit screwing around?

Comments

  • Wet Rotor pumps in series

    When "stacking" wet rotor pumps in series, it is my recollection that you increase the GPM pumping through the system. Is that correct?
  • kevin coppinger_4
    kevin coppinger_4 Member Posts: 2,124
    I don't think...

    so..You increace Head...GPM is if you do them in parallel....kpc

    To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"
  • Brad White
    Brad White Member Posts: 2,399
    Kevin is correct

    Series mounting increases head (pressure) at about the same flow. Parallel increases flow at a common pressure. Not the same pressure as one running but a common pressure where they both settle in equilibrium.

    EDIT: As noted below, each follows their curve but stacking the circulators is no way to double your flow if that is your goal. In the end, if you need that much head, I think you have too much pressure drop. :)
    "If you do not know the answer, say, "I do not know the answer", and you will be correct!"



    -Ernie White, my Dad
  • Norm Harvey
    Norm Harvey Member Posts: 684


    That's always looked so cool to me. I think when I finally convert my new house from warm air to hot water I'm going to buy some of the tiniest tiniest circulators I can find and stack them,.. just because I CAN!

    To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"

    There was an error rendering this rich post.

  • ALH_4
    ALH_4 Member Posts: 1,790
    flow and head

    It depends on whether you have an existing system or you get to design the system the series pumps are connected to.

    If you have an existing system, you are stuck with that system curve. You can only shift the operating point along that system curve.

    If it is a new system and you get to control the system curve, you can make anything happen.
  • Uni R_3
    Uni R_3 Member Posts: 299
    Come on guys...

    Same flow at an increased head? If you put 2 pumps in series the flow will be increased. The combination will have a curve more like a larger higher head pump, but the flow will not stay the same.
  • Norm Harvey
    Norm Harvey Member Posts: 684


    Page 190-192 of "Modern Hydronic Heating" by John Siegenthaler

    It uses an example of two 7.6 gpm circs producing 10.5 gpm in series at double the head.

    To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"

    There was an error rendering this rich post.

  • bob_50
    bob_50 Member Posts: 306
    What happens when

    you pipe them in parallel and wire them in series? ;)
  • Brad White
    Brad White Member Posts: 2,399
    You are right Uni

    Not exactly the same flow but not doubled. Each does follow their curve and each curve is different. Thanks for checking in.
    "If you do not know the answer, say, "I do not know the answer", and you will be correct!"



    -Ernie White, my Dad
  • Larry Weingarten
    Larry Weingarten Member Posts: 3,590
    Um...

    ... Less. ;~)
  • Mitch_4
    Mitch_4 Member Posts: 955
    then

    you are doubling the flow at half voltage due to double voltage drops, decreasing the rotor speed at a ratio inversly proportional to the electrical resistance of each winding to a factor of 1/x where x= the inrushing current not allowing for the slight shift in phase.

    honestly don't know.

    if you cant dazzle em with brilliance..baffle em with....

    mitch
  • Jamie Hall
    Jamie Hall Member Posts: 24,837
    and the objective

    of the exercise is to match the pump(s) to the system, so that the pump(s) are operating at their best efficiency. The key to adding the things up is that if you pipe them in parallel, both pumps will operate at the same total dynamic head, and the flows from the two pumps (which will be the same, if the pumps are identical) will add. If you pipe them in series, the flow in the two pumps will be the same, and the total dynamic heads will add.

    In either case the system will operate at the point where the combined pump curve crosses the system flow/head curve; you will likely have to draw them both on the same graph to find out where that will be (I always do...).
    Br. Jamie, osb
    Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England
  • jim lockard
    jim lockard Member Posts: 1,059
    with the flow check

    open you get heat, flowchecks closed you get cold.