Steamhead redux
William Faust
Member Posts: 168
I want to install steam main vents. Main #1 begins with 32' of 4" pipe and ends with 14' of 3" pipe (46' total). Main #2 has 32' of 3" pipe until it does a "T". The left branch has 14' of 2" pipe and the right has 14' of 2-1/2" pipe.
When the heating season is done, I also want to install top-of-riser vents.
How do I figure needed venting in each instance?
When the heating season is done, I also want to install top-of-riser vents.
How do I figure needed venting in each instance?
0
Comments
-
Get Gerry Gill and Steve Pajek's e-book
"Balancing Steam Systems" available in the Online Store of this site. It has the capacities of almost every vent currently available as well as a bunch of older ones. Once you know the cubic feet of air in each main, you can choose vents that will pass that amount of air in a minute at 1 ounce pressure.
You'd do the risers the same way, but size the vents for 2 or 3 ounces so the steam would distribute thru the mains first.
To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"0 -
Aha!
Okay - Main vent(s) must pass main's c.f. of air in 1 min. at 1 oz. pressure; riser vent(s) must pass riser's c.f. of air in 1 min. at 2 or 3 oz. pressure. I got the mentioned .pdf file today and I see that you are named in the introduction or preamble.
By the way, where venting the risers is concerned, okay to vent them not at the very top of the riser but within a couple of feet of the top? This is a logistical issue (getting at the pipe).0 -
That venting location
should work fine.
To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"0 -
I'm stuck on the math
Using the formula 3.14 x radius squared x length for each pipe diameter (3.14 being Pi), I calculated volume of 500 cu. ft. for steam main # 1, 270 for #2 and 294 for #3. A Gorton # 2 will pass air at 1.1 CFM at at 1 oz. pressure (my max. operating pressure). I obviously can't put 500 Gorton #2's on this main. I don't understand this - what am I missing?
0 -
cubic ft vs cubic inch
I am guessing you have pipe volume in cubic inches and so if you take the Gordon #2 at a cubic foot that equals 144 cubic inches. Now that should help in sizing. Good luck, Tim0 -
Cubic Schmubic
A board foot has 144 cubic inches. A cubic foot has 1728 cubic inches. Easy to mess that one up!0 -
True, but Tim...
still made me cringe. I'm a dope. Okay, now where's that calculator again?0 -
i can't believe I messed that one up.
Sorry about the misinformation. duhhhhhh0 -
here are my sizing results
0 -
here are my sizing results
On a 2-pipe pumped system, would it be bad to use a Gorton # 1 (.33 CFM) to purge a main that has only .07 Cu. Ft. of air in it?
Alternatively, my risers have from .01 to .05 Cu. Ft. of air in them. With those low figures, would venting the risers really add much in the way of performance or energy savings?0 -
Ignore last post
Ignore last post - bad data due to error in spreadsheet.0
This discussion has been closed.
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 64 Pipe Deterioration
- 917 Plumbing
- 6.1K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements