Instant water heaters being used for heating

2

Comments

  • EJ hoffman
    EJ hoffman Member Posts: 126
    Dip tube

    Dip tubes in water heaters do two things cold to the bottom and stir/suspend particles Sediment goes out the faucet

    Radiant heat company and plumbing compny is what Hoffman Hydronic and Plumbing is.
  • EJ hoffman
    EJ hoffman Member Posts: 126
    What are you sayng about max temps?

    I don't design for 140 in the floor more like 100-110 un less it is hydro air. But per recomendations a water heater at 140-160 with a mixer kills legionella after 20 minutes.


  • and you have no problem with all that stirred up sediment travelling through your heating system?


  • I see what you're saying, and I'm sure you have a good point there. But, why would I want to have to run a heat source 30 to 60 degrees higher than I need to heat the home?

    does that strike you as particularly efficient?
  • Ray Darby
    Ray Darby Member Posts: 20


    It might be easier to digest the sediment issue (pun intended) if we consider a standard DHW heater. Every time its used, fresh, mineral laden water enters. A small amount typically settles in the tank each time, building up over time. The manuf's are using swirly-tubes to stir it up so it doesn't build up over time. The cold incoming water is what swirls it up, then it comes out your hot water faucet.
  • Ray Darby
    Ray Darby Member Posts: 20


    PJO,

    My own system is shown in basic schematic format here:
    http://www.radiantec.com/systems-sources/open-system.php

    The schematic is a bit oversimplified relative to mine in that it doesn't show multiple circuits, one of which is mixed down (stamped conc floor) and it doesn't show exp tank, thermometers, flow meter, etc. But it gets the point across re fresh water entry.

    I'm getting ready to leave this post as its transforming from educational to hostile - but I'll check back for your responses on Radiantec (Man oh Man, have they rumpled some feathers out there or what?) From some of the posts its hard to believe they haven't been shut down after ticking so many other installers off over the last 27 years!).

    I've learned my lesson though - bring up the open combo system and people can get downright crazed! Since they share so much in common with a water heating system using PEX (see my previous posts) I'm wondering how all these peeved off folks have remained calm so long when thinking about standard DHW systems?!?!?


  • ...provided it doesn't get stuck in all those nice mineral deposits building up in your heating system as it circulates, waiting for the next DHW demand to flush it out and bring in more ;)

    Seriously Ray, it's not very common, but I have seen systems gum up from this. The first time you have a client have to abandon the system your company provided for them, you might wonder how happy they are about that few hundred they saved up front. With my previous employer, that was what made me realize that maybe the wisdom of that course of action was questionable. I only fielded a couple of calls like that... I have no idea how many more may be out there that were with second owners who didn't know the company... But even a couple was enough for me to think "not worth it". That's a truly major disaster when it happens.

    Again, it's cheap insurance to use a HE, even without any potential health concerns at all.


  • well, dave yates hasn't ;)

    for my point of view though, for the health issue, just do a little math. Compare surface area within the heating system pipes to surface area in a DHW system's pipes.. compare that ratio to the amount of water.. then think "concentration levels".
  • Ray Darby
    Ray Darby Member Posts: 20


    I appreciate what you're saying about the gumming up issue. The first thing I thought of after reading your post is I see the gunk inside old faucets. I changed one recently in a (standard) DHW system and it was absolutely disgusting to think about the occupants drinking the water that has been flowing through that gunk all these years!

    That's one reason why I like PEX for hot/cold plumbing (I'll probably get beat up on that statement too, but I'm getting used to it), especially after seeing what CU pipe looks like in most DHW systems after 15-20 years, especially with poor water quality.

    In a combo system, as long as my (relatively few) parts are brass and CU, if they get gunked up at some point I'll simply replace them (just like I'll need to do with my hot/cold water plumbing).


  • Sure, at a cost probably similar to doing an HE in the first place ;)

    What happens if that gunk is caustic to your system and causes a real integrity failure? Brass and CU can corrode under the right conditions as well (they are non-ferrous, not invulnerable).. one of those conditions being the application of a catalyst such as heat, yes?

    Again, this isn't common. When it's your house, you can keep an eye on things. What I'm saying is when you are designing for homes in radically different locations, you cannot be aware of the factors on the ground to the same degree you *MIGHT* able to in your own home. As such, you're gambling.
  • Ray Darby
    Ray Darby Member Posts: 20


    You're right, Rob, running a heat source at 30-60 degrees higher than necessary to heat the home (like say a radiant loop that needs 110F water) isn't efficient at all!

    Efficiency guidelines have for years been telling us to set our water heater at 120F. Legionella bateria are the reason given to run 140 or higher in DHW heaters which then requires a anti-scald valve for safety. Maybe UPC should require water heaters be (literally)unable to be set below 140 and require anti-scald for the whole hot water distrib system (instead of just showers,etc).


  • Again, Dave would say yes. I'm not sold on that yet... but there is a big difference between a storage tank and 50 feet of hot water pipe, and a couple thousand feet pex PLUS a storage tank and 50 feet of hot water pipe, in my mind.
  • Ray Darby
    Ray Darby Member Posts: 20


    I guess I'm still strugling with the idea that an open loop combined HRF is significantly different than a DHW system with copper and brass fittings. The main difference is longer (PEX) pipe runs, but I'm not concerned about degradation of the PEX (or sediment in the PEX) like I am with the CU and brass parts.

    The reason I was given by WH manuf's for tanks lasting longer in a open combo system is because the sediment is stirred up a little more than with DHW alone. It seems reasonable therefore to assume a combo system will have *less* sediment than a standard DHW system, not more, and the parts within will get less gunked up.


  • Well, take a look at most radiant systems and differences should be pretty easy to spot ray. it's usually a lot bigger, for one (re the health issue). there are usually a lot more items to potentially gum up and fail, for two, and they are more expensive items as well, and are not generally seen as often as, say, the bathroom sink might be where you would see leaks starting before something bad happens.

    You'll have less sediment sitting in the tank.. fine. But the same amount of sediment is coming in through the water, and you're circulating it along with whatever mineral content the water heater THROUGH THE HEATING SYSTEM.

    I suppose in super dumbed down, large diameter PEX systems (which I would also generally oppose for good design reasons), this might be less of an issue. It would take a heck of a lot longer to gum up a 7/8" pipe fitting, leaving just corrosion as a possible issue. But, again, that involves a lot of design tradeoffs that really don't seem to me to be in the client's best interest (wider on centers, higher water temps, to name two).
  • EJ hoffman
    EJ hoffman Member Posts: 126
    Just finished a 5300 sq ft ranch post and beam

    the water pipe potable just the hot side was 1200 ft with a recirc on it it looked like a suspened tube radiant system ho put in forced air furnace
  • EJ hoffman
    EJ hoffman Member Posts: 126
    per reccomendations from here

    we put mixers on water heaters and turn our heaters up to 140 just for the potable so instead of two appliances we have just one
  • EJ hoffman
    EJ hoffman Member Posts: 126
    Have not found 1 case linked to an open system

  • EJ hoffman
    EJ hoffman Member Posts: 126
    why wider spacing?

    why wider spacing. I use 1/2 inch but I use constant circ on the radiant water doesn't have a chance to sit and grow bacteria or collect deposits
    7/8 tube could still be put on 6-12 spacing and then lower your water temp just design for what spacing you want some use 7/8 tube to cheapen a system I don't play that game I design for comfort and effeciency not for cheap to compete
  • EJ hoffman
    EJ hoffman Member Posts: 126
    Constant circ with injection mix

    Circ runs 24/7
  • hr
    hr Member Posts: 6,106
    The plumbers mission is to \"protect the health of the nation\"

    Installing open hydronic/ dhw systems seems to ignore the spirit and intent of the plumbers code.

    All the various mechanical codes I have worked under are quite clear about backflow protection devices to keep the potable side safe from the heating side.

    Furthermore heating manufactures go to great lengths and expense to have their equipment listed to ASME. Not many, if any instantantanous heaters have that listing.

    Swapping simplicity and low up-front cost for integrity and liability seems a foolish way to make a living.

    I question any licensed, experienced, and insured master plumbers willing to make this compromise, with the almighty buck being the only driving force. Especially when your customers health is at stake :)

    hot rod

    To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"
  • PJO_5
    PJO_5 Member Posts: 199
    Interesting...

    I perused the Radiantec website:

    "Legionella bacteria cannot stand temperatures above 115F" (he had a lower case "o" after the 115 that I removed).

    That one struck me...others included many general references to heating demands and using HWH's. NOT ONE MENTION OF A PROPER HEATLOSS CALCULATION! (Sorry for the shouting)

    I put in a system in '98 as my house was being built, and my problems were only in the heating area because - as mentioned earlier - I would never use a combined system.

    I called several times for advice - on my dime of course - and also was given more narrow plates than what I ordered. They only had one size despite showing two at the time. They also said my cast iron boiler would be fine with non-barrier tubing. They also said I would get plenty of BTU's for my 118,000 heatloss calculation...if actually was about 20% less than that and it STILL couldn't keep up in the three radiant zones and I put in more insulation than they recommended.

    My tubing was turning a lovely orange color from the O2 eating away at the system, and the mixing valve was after the pumps - as per Radiantec spec - and I don't think my radiant was pulling 10,000 btus from the boiler...for about 2,400 sq. ft. (including a 500 sq.ft. garage slab).

    I found The Wall after six months of searching for other answers...I was a newbie on the 'net in '99 but it was like a religous experience when I started looking around and getting help.

    I re-piped my boiler w' primary/secondary, put in a heat exchanger for the radiant loops (an Ergomax for the buffer), a smaller nozzle - but still kept the stack temp. at about 350F, new mixing valve in the right place, and other stuff.

    My baseboard upstairs always worked pretty well, but that was even better. The radiant was better too, but I still am short in a couple of areas of the house that I was worried about from day one. The output of the radiant is still WAY below what I was told, and I cannot imagine what an older home (remember mine is new and tight) would be like.

    Enough for today...Go Eagles!

    Take Care, PJO
  • Ray Darby
    Ray Darby Member Posts: 20
    PJO's experience

    Patrick,

    Your shouting (all caps) was entirely appropriate in this case. In fact, bold print and italics in addition to all caps would be appropriate if that capability were available! :-)

    I'm sorry to hear about your bad experiences with Radiantec. My own experiences with them were circa 1981-1986 and were exclusively with a man by the name of Bob Starr, who I'm pretty sure ran the place at the time. Maybe the guy you dealt with was an overcondident newbie? A new owner at Radiantec?......I honestly don't know.

    At the risk of sounding like I'm making excuses for them (not my intent), I've had similar experiences with some of the finest HVAC (forced air) companies in my area - its had to do with turnover, the fact that supervisors can't oversee everyone all the time, etc. Still, there's NO excuse for the seriously (horrendously!) bad advice and corresponding headaches you encountered. It's just plain wrong - very wrong.

    At the risk of stating the obvious, a cast iron boiler should never be used in an open system - your orange PEX and boiler disintegration being two bad results (I bet the disintegrating boiler heat exchanger material clogged up a bunch of other small-orifice components as well).

    A heat loss calculation is the first step for any heating system....only an incompetent, untrained person would say it's not necessary (or, second worst, rely on Btuh per square-foot-based estimates)!

    Then, mixing valves after the pumps (?!?!?) I'm almost inclined to think you mis-dialed their number and was connected to a home for the criminally insane!?!? I am so sorry to hear about your experience! It's probably too late now, but my inclination would be to send Bob Starr an email (or a phone call) and ask him to review these Wall comments. If nothing else it may help encourage him (or whoever is running the place, if anyone) to keep an eagle eye on any newbies.

    My experience with them dates back to 15-20 years ago. But I have suggesting them to people since, including right here on The Wall less than a week ago (blushing heavily). I value your comments (and others too) on Radiantec. If it makes you feel any better, and I hope it does, I'm too embarrassed to consider sending anyone to them ever again. :-(

    For whatever its worth, my sincere condolences on your Radiantec experience - I completely understand why you feel the way you do about them!
  • Dave Larsen_2
    Dave Larsen_2 Member Posts: 53
    EXACTLY!!

    Touche' Hot Rod.......couldn't have said it better myself!
  • What are you implying???

    Just wondering what it is that you're implying about the water heater I have in my second home. What does age have to do with it? What does water hardness have to do with it? Did you know that the bacteria responsible for LD is omni present? You are correct in that it is not an "open" space heating system, but it IS an open potable water heating system, same as millions of people throughout this country have. I'm sorry, but it appears that you are trying to pooh pooh my contracting of this deadly disease based on the age and condition of my water heater.

    Are you serious about wanting to have water samples tested? Are you certain you want to know what's in the water? If it WAS found that the bacteria responsible for LD were present in your combination system, would you change your way of doing business, or will you stand by your position until a lawyer shows up at your door?

    Allow me to debunk some myths about "protective" actions as it pertains to combination open systems...

    1. Flushing. Certain "system" manufacturers claim that due to their required method of plumbing, causing all DHW cold water draws entering the dwelling to enter through the hot water distribution system, that theoretically all bacterium are continuously flushed out of the system.

    Some systemdesigns I have seen require ALL incoming water to be introduced through this system. This results in hot water being flushed down the toilet, and in some cases out on to the lawn. Neither of which is a wise use of a precious (energy) resource. It may also result in extremely cold floors due to cold water being introduced through the floors before it is brought into the home. In situations whereby they make claims of "free air conditioniing", I would also expect to get free mold growth due to the natural propensity of cold water to cause condensation on the outside of all cold water pipes.

    As it pertains to flushing, if you and your family leave for vacation at any time of the year, the water lays in the pipes, laying around, feasting on the omni present food source, breathing the O2 through the walls of the tubing, having a good time, multiplying,,,

    When you and your family return from your trip to Wally World, you have most probably been exposed to numerous virus carrying passengers on the pay per ride germ tube (Air Plane) and your immunity system is fighting that infection. You get home, take a nice hot shower, thereby flushing copious amounts of bacteria into the shower where it enters via the water mist droplets, and breath deep, trying to break up the congestion, thereby deeply inhaling the bacteria ito the deepest recess of your lungs, where it can attack in the form of bacterial pneumonia. You become deathly ill, thinking "It's probably just the flu". Eventually, your lungs degrade to the point that breathing is nearly impossible. You feel like you are drowning and you are constantly coughing so hard that you nearly herniate yourself. If you happen to be lucky enough to have a wife who is as persistent as mine, you force yourself to go to the doctors office, only to be diagnosed as having bacterial pneumonia. When I was told that, I said "As in legionairres disease!?!" to which my MD said, "Most probably, 90 percent of the bacterial pneumonia cases are LD related..."

    When queried as to why they don't diagnose more cases of LD, the MD said it was easier and faster to treat it than it was to wait for the test confirming LD. In other words, we can give you broad spectrum antibiotics and nip this thing in the bud now, or you can wait an additional 5 days for the test results to come back and take a chance on getting even sicker and possibly dieing from the exposure...

    2. Pumps and Timer: Some "system" manufacturers claim that they have a pump timer on the system that keeps the infloor water from becoming stagnant, or that there are pumps which keep the water "fresh"... Although stagnation does enhance the growth of the bacteria, it is not a requirement for the bacteria to flourish. If the timer or pump should break down, the theoretical benefits are gone, and trust me, these components do fail on a regular basis. Essentially, during the summer months, the pump/timer copmbination insures that the bacteria are flushed out of the floor and into the tank where they can be inhaled, as well as providing fresh oxygenated water and food to the bacteria to support its growth.

    It is my recommendation, as a licensed master plumber charged with protecting the health of the nation that you NOT consider this potentially deadly system. No potential dollar savings on up front system costs is worth the risk of compounded exposure to this known, deadly disease.

    LD is THE most mis-diagnosed disease in the world, and thousands of people die from it every year under the mask of bacterial pneumonia, don't become a victim yourself.

    BTW, I am aware of two other people who have contracted LD from systems identical to the system you are considering, both who almost died, but survived and are in the process of converting their sytems to true closed loop systems.

    There are lawyers involved...

    I am also aware of two identical senior citizen retirement centers with RFH systems in them, one an open combination system, and the other a conventional closed loop system. The building with the open system has twice as many residents with serious lung ailments, and a continuous entourage of oxygen purveyors coming and going into and out of the open loop building. To boot, their floors go cold every morning when all the residents get up to take their shower.

    Not many happy campers in that place...

    And again, there are lawyers involved.

    If you want to continue promoting this potentially deadly system, that is your perrogative. But given the body of evidence, a person would be a fool to continue down this deadly path, And trust me when I say it is deadly...

    I damned near died from it. And I WILL do everything within my power to make sure that it ceases to happen to anyone else.

    Consider this the year of changes.

    Mark Eatherton
  • DanHolohan
    DanHolohan Member, Moderator, Administrator Posts: 16,582
    Bravo!

    Retired and loving it.
  • Ray Darby
    Ray Darby Member Posts: 20
    What IS he implying Mark?

    Mark,

    I didn't read EJ Hffmans comment as implying anything derogatory about you but rather properly noting the probable relationship between your water heater and your Legionella. EJ, or anyone else that cares about you, should be praised for bringing this up, not hammered on an unrelated issue to YOUR health. The age and water quality supplied to your water heater is **very** important as it may have everything to do with it! Before I get off subject with open system chatter, please be sure to read the sidenote at the end of this post.

    I'd like to understand how YOUR hot water system was able to harbor Legionella and almost kill you? Do you have an explanation or possible cause? This issue hasn't been flushed out to my satisfaction but, since learning of what happened to you on this forum, I wanted to know. I have a few ideas that seem to be supported by scientific research on the subject:

    1) If your heater was electric, even a higher (140F) water temp setting might not be enough as electric tanks can be much cooler at the bottom of the tank (and still allow Legionella to survive). Interestingly, instantaneous water heaters (the orig subject of this forum) may be a healthier alternative to tank heaters.

    2) Tank heaters in general are more likely to harbor Legionella because age, and/or sediment and/or corrosion reduces efficiency, heat transfer, thereby lowering water temp and allowing Legionella to survive!

    What follows are several quotes to support these points from A Canadian web site I referenced in an earlier post (www.sickkids.ca). But first, it may help to understand who these folks are and ask about credibility (with all due respect to Mark, a Master Plumber, and everyone else in this forum, myself included, we aren't the authorities on this important subject. Maybe these Canadians have done their homework? According to their web site -

    ** The Hospital for Sick Children (SickKids), affiliated with the University of Toronto, is Canada's most research-intensive hospital and the largest centre dedicated to improving children's health in the country. As innovators in child health, SickKids improves the health of children by integrating care, research and teaching.**

    Here are some excerpts from their report on this subject -

    ** The type of water heater and mineral content of the water are also important factors that affect the growth of legionella. 22, 23 In Canada, electric water heaters have been shown to harbour higher concentrations of legionella, compared to gas and oil-fired tanks.24 This is due to the tank design: Cooler water pools at the bottom of electric tanks where mineral deposits also collect, creating a productive breeding ground for legionella. Improvements to water heater design and the use of new technologies, such as on-demand (tank-less) water heating, are needed to better prevent legionella growth in water systems in the future.**

    ** Tank-less heaters also dramatically reduce the risk of legionella infection from hot water because there is no storage tank to harbour large colonies of the bacteria. **

    ** Store high – deliver low: a balanced solution
    One way to balance these risks is to set hot water tanks at 60C and – through the use of mixing valves or other plumbing devices – ensure that hot water is reduced to a safer 49C before it gets to household taps. This solution is supported by Health Canada18 and Quebec’s National Institute of Public Health. **

    ** We also conclude that, for most households, there is minimal disease risk from reducing storage temperature to 49C in water heaters fuelled by oil, gas or propane. For electric water heaters, temperatures within the storage tank can vary widely, resulting in pockets of cooler water that create good conditions for some kinds of bacterial growth, including legionella. Where there is any concern about possible infection, households should reduce scald risk by installing tempering valves or point-of-use devices, instead of lowering the thermostat setting of their water heater. **

    Side note: Legionella is an airborne kritter and is killed by high water temperature. Is there any scientific evidence to support the idea that, once killed and the dead-legionella bacteria get stuck in an open system piping network, that they can spring back to life? - Or that they can enter non-oxy barrier PEX tubing (as in open system OR - and this seems important - a PEX DHW system)? I'm not interested in opinions, I'm interested in cold, hard facts supported by science (I don't presume to give or know the answer - I maintain an open mind that it may be possible - I honestly don't know).
  • boatloads of evidence for those who seek

    Too much emphasis on just the point of source (tank) being expressed Ray. There are two more pieces in the potable hot water stream to consider as sites that harbour bacteria: the Distribution Netwrork of piping; and Points of Use (or distall sites, as referred to in medical journals detailing LD cases.

    Danfoss performed a study years ago to find out why super-heated 180F 15-minute flushes only offer a temporary reduction in culture numbers. They determined that the Legionella bacteria survive - ready for this - in the outer fringes of biofilms in the Distribution Network of piping and recolinate the entire system.

    You keep asking for proof, yet state that we're not qualified to speak to this issue. The proof is easy to find that details Legionella, their needs, and what constitutes an amplifier for the bugs. An open system, by its very design, is a bacterial amplifier. It simply can't avoid being one & a pretty perfect one at that.

    Taking the 30-year water heater argument a step farther, let's look at the longevity of plastic tubing & consider the long-term ramifications.

    As ME noted, lawyers are already involved with a number of cases. Law students are being taught how to prosecute LD cases because they see the looming cases and recognize the lucrative nature.

    According to Stoudt and Yu, Legionella leave footprints much like our DNA leaves undeniable traces for forensic folks to follow. They claim that if tested within a reasonable time-frame, the LD can be positively traced to its exact source. Two deaths from water heaters in Pittsburgh residences were traced in this manner.

    As for testing samples submitted by someone who supports the use of open systems? Not interested. Random samples from customers' homes who have open systems - absolutely. But, I'll lay my money on the bet that the open system supporters will absolve their systems of any/all responsibility and blame the water heater.
  • Rich Kontny_3
    Rich Kontny_3 Member Posts: 562
    On Demand Heater as Heat Source

    It is being done already, there will be a system on display at the AHR show in Dallas.(January 29-31) Look for the Navien America Booth.

    I have ran two test installations for them here in Wisconsin. They work great! One with a Rinnai unit and one with a Takagi.

    Contact me for details

    Rich Kontny
  • Ray Darby
    Ray Darby Member Posts: 20


    Dave,

    I didn't mean to imply people on the post don't know anything about Legionella - I was making the point that scientists studying the issue know more than we do....at least I hope so!

    I don't think too much emphasis can be placed on the tank. Whether its a sidearm tank in a boiler config or a gas or electric water heater, the tank is the point of entry and that is where the Legionella can be killed if the temperature is high enough.

    In terms of the distribution system, there is ample evidence to support your statement re Legionella surviving in the biofilm. That's true in both copper and PEX piping systems. Various organizations (ie, Legionella.org, ASHRAE Guideline 12-2000, and more) indicate that running water temperature high enough and long enough to kill Legionella in the tank ** as well as the piping system ** is effective in killing Legionella (depends on a variety of factors as you point out, including the residency time of the high water temperature on the biofilm). Chemical treatments of the distribution system appear to be even more effective if Legionella is already present in the biofilm.

    If the orgin of the water to a distribution system (ie the water heater) is Legionella-free, and the piping is Legionella-free (it takes some operation time to develop the biofilm - new pipe doesn't have a biofilm) a high water temperature will (eventually) kill the Legionella. And once it is dead, if any new Legionella bacteria is reintroduced by fresh incoming water, it will also be killed by a high water temperature - in the tank, and be unable to enter the distribution system.

    The only exception to this conclusion I can think of is a configuration where an anti-scald valve introduces cold water to the domestic hot water supply - Legionella would likely survive the mix and end up in the distribution system....

    My conclusion is that Legionella killed at the tank cannot then establish itself in the distribution system (except in the case above). Your thoughts?

    Thanks Dave, I appreciate your experience in this area.
  • facts need to be straightened

    Ray,

    For starters, the Legionella point of entry is the cold water supply & that's the jump-off point for introduction to a potable water system. Not to digress too far, but this is also why heat pumps that utilize the municipal water system in a real twisted approach for open system construction were shot-down by our local water company. They're not much different than the open systems being promoted in this thread - just using the neighbors' water instead!

    I wish the tank were the only issue. Sure would make things easier. If a tank were held above 133F throughout its entire cycle and no water could exit prior to a 20-minute contact-time, your point would be much more valid. The reality is that there are multiple cycles where tank temps are substantially below 133F, where the bug first begins dying off, and contact-times are brief before the potable water gets an opportunity to be whisked off to the Distribution System and/or Points of Use - not to mention an open-loop hydronic system where all conditions that present an ideal amplification await the bugs. So, the argument that simply raising the storage temp resolves the issues does not hold water.

    What chemicals? Chlorine at 2- to 4-PPM (what's seen in municipal systems that utilize Chlorination as the bactracide of choice - a practice that dates to 1918 when Chicago became the first to use Chlorine and Typhoid & Cholera disappeared - almost overnight). Chlorine concentration levels would need to be increased by a factor of 10,000 to effectively treat for Legionella. Chlorine also dissipates as water is heated, so it's pretty much gone in the hot water side of the system. Chlorine Dioxide and copper-silver ionization work well, especially the copper-silver ionization systems as they have a residual kill affect & it's the only system that offers complete eradication. For the average Jane & John Doe, there are no economical, reliable and redily available chemical treatment systems that will put a dent in Legionella bacteria. So, what is available? Hot water pasteurization with a system-wide approach (this includes treating the Distribution Network, constant recirc & Points of Use). While hot water pasteurization with temps elevated to 133F+++, constant recirc and appropriate scald-guard devices will not eradicate Legionella, it will keep colonies at levels low enough to save thousands of lives each year - every year. Aids patients and critical care folks whose immune systems are compromised will still need to avoid use.

    Again, the Danfoss study clearly demonstrated that high water temps will not eradicate - they only kill off the free-roaming bugs & suppress culture numbers. Biofilms form within weeks/months & plastic piping has been proven to offer a better environment during the so-called clean phase before copper gains a film granting a barrier from direct contact. As noted before - the tank is not an iron-clad barrier that offers any guarantees for blocking the bugs from entry to the potable system and, most certrainly, not blocking bugs from entering the open hydronic system.

    In the proposal put forth in the Watts film, the Distribution Network is maintained at 133F (or higher) to keep the entire network pasteurized. While this can't prevent biofilm activity, it does ensure free-roaming cultures are kept in check.

    I am no expert, not by a long shot. However, I don't believe you need be an expert in microbiology to read and comprehend what the experts have said about this bug, the diseases they cause and what's required to foster their growth. On the other hand, I've been a plumber for almost 40-years and have a better understanding of what takes place inside the dynamics of a potable water system than do those same experts. So, armed with what I can understand that they've stated as fact, I can only come to believe certain things regarding their bugs and our plumbing systems. It's simple logic and no one yet has been able to find any credible evidence to the contrary - including me & I've looked for years.

    I think we spoke a number of years ago on this subject (if memory serves). If so, I was much less sure of my stance regarding this issue then than I am today. Mark's experience is not unique - not by a long shot. What is unique about his LD, is his making what appears to be a full recovery. Many who contract LD never fully regain their health. Somewhere between 3% and 15% (for CAP - Community Acquired Legionella-based Pneumonia. Nosocomial - hospital acquired - LD death rates are much higher.) quit breathing entirely and move to the other side of the lawn. (According to the experts, the numbers are somewhat fuzzy because tissue samples are not regularly cultured.)

    One other method utilized in Europe: UV steralization, but with a twist. Upstream from the UV, they include ultrasonic bombardment to break up cysts of one-celled critters utilized like a Trojan Horse by Legionella & exposes the bugs that would otherwise get a free-pass while shielded from the UV rays as they floated along. They also include a solenoid valve that snaps closed in the event of a power failure.

    This is a circular argument. The facts exist to more than adequately support the notion that open systems should be banned to protect the potability of our customers' water and to enhance their prospects for remaining healthy. You, and anyone else who wants to, can choose to ignore the facts and believe whatever fantasies suit your desires - be it free A/C or "enhanced" efficiencies.

    Meanwhile, we'll be pushing for code changes to restore some common-sense to the installation of potable hot water systems. While we strive for those changes, there will continue to be more than 100,000 hot-water scald cases seeking medical treatment, dozens of hot-water scald deaths and, depending on who you want to believe - from the CDC to any number of other credible sources - somewhere between 4,500 and 35,000 legionella-based deaths acquired from residential potable hot water systems - every year.

    Sure seems to me that if there is a reasonable, reliable, and relatively innexpensive manner with which we could reduce, to a point where these issues would be virtually eliminated, the existing risks, we'd be fools not to pursue them and do our best to get the codes changed.
  • Rich Kontny_3
    Rich Kontny_3 Member Posts: 562
    Please pay Attention

    Guys you are getting a little sidetracked here as I have stated in another thread. The concerns listed above have been addressed with the add on "Heating Box" that is a closed loop system. It recommends the temperature from the on demand heater to be around 180 degrees than it steps it down with the domestic side tempering valve to a range from 110 -155 depending on your requirements. The hydronic side is also completely separated by flat plate heat exchangers.

    The cross over concern has been addressed,the legionella threat has been addressed (this bacteria is killed at about 132-135 degrees)

    I am talking about an engineered and currently manufactured add-on device called the "Heating Box" that sits alongside qualified on demand heaters (Rinnai,Takagi,Noritz etc)

    This thread is another long thread about reluctance to change! Which is good until all your concerns are answered!
    The add on "Heating Box" addresses all your concerns above.

    My biggest concern is that the HVAC people will get the jump on this because they are already doing radiant and many have marginal plumbing licenses that will allow them to install these.

    Rich K.

    Make Peace your passion !
  • Internet radiant and Viagra

    Every time I open my e-mail box, there are a multitude of spam messages encouraging me to buy their "discount" Viagra. The thought struck me while reading this thread that there is a corelation between Internet sales of radiant systems and the bogus Viagra. It won't matter if either of the products work, the only one getting screwed is the buyer!
  • Ray Darby
    Ray Darby Member Posts: 20


    Excellent post, Dave. Thank you for taking the time to explain these concepts so well and for remaining patient with me (and others) during the process. I've learned a lot and I'm sure I'm not the only one! We're lucky to have you here.
  • Conditions surrounding my near death experience and exposure ...

    Ray, My scenario was this. I maintain a summer home in the mountains of Colorado. This home has a 30 gallon LP fired DHW tank. I'm in the process of getting ready to build a new retirment home up there, and being the energy conservationist that I am, I had turned the operating temperature of my tank to a low of around 115 to 120 degrees F in an effort to stretch my current tank of propane out over 2 years to avoid having to refill the tank, and having to either pump the tank out prior to moving it, or attempting to move a full tank.

    During the week, when the place is un-occupied, I was turning the tank to PILOT only to save fuel. Upon return on Fridays, one of the first things that gets done is to fire up the well and water heater.

    Late this summer, I had gone on a trip to Rhode Island for some training. As usual, the plane was full of people hacking and splooting germs all over the place. I contracted a head/chest cold. While up in the hills, the head/chest cold got the best of me, and I decided to take a nice hot steamy shower to see if I could break up some of the congestion. I had the water in the shower turned to full hot, which was just barely hot enough to generate a mist. While in the shower, I was intentionally doing deep breathing exercises, trying to bust loose the congestion.

    Shortly thereafter, I came down with what I thought was the flue and damned near died. Simple as all that. Once I put 2 and 2 together, I put energy conservation in the BACK of my mind, and cranked the heater up to kill the bacteria. I still turn it to pilot during the week, but I sanitize thermally when it is on.

    I think a poerson has to stop, sit back and ask him/herself, "What's in it for these guys (Yates, myself and all the other Legionella warriors) to make them want to fight so hard against these systems? I have no monetary horse in this race, nor do any of the other warriors. I have the health and welfare of my customers in mind. It is not my goal to do things as expensively as I can, heck if someone comes up with a better, more efficient less expensive way of doing things, we'd be FOOLS to not jump on that band wagon...

    While you're sitting there contemplating that question, you must also ask "Why does their opposition feel so strongly FOR the use of combination open systems?"

    Quite simply, because they are looking for the cheapest way to perform the same function of delivering heat to maintain reasonable human comfort, and are ignoring the potential health implications in the process.

    Our job, as the plumbers creedo states, is to protect the health and welfare of the country. And so we will. Through code changes and education. Just like we always have. Unfortunately, this one slipped past the powers that be, but it is never to late to reverse a decision with the AHJ's.

    And as Paul Harvey sayas, "Now you know the REST of the story..."

    BTW, I've not fully recovered yet. My lungs are ultra sensitive to environmental dust, and I wheeze like an old steam engine most of the time. I'm just greatful to be alive...

    ME
  • Ray Darby
    Ray Darby Member Posts: 20


    Hey Rich -

    If it makes you feel any better, and I hope it does, I checked out the Heating Box immediately after being notified via email of your post.

    Yeah, this forum topic has been *all over the map* but I don't see it about *reluctance to change* (which is true -damn humans!) so much as *wanting to understand how to avoid Legionella* and understanding what that means to us in terms of design, installation and operation of hot water systems (hydronic, domestic or combined). Its been extremely enlightening! I have a new respect and understanding of that little Legionella critter - it's downright pervasive and almost impossible to eliminate!

    I'm sure you can appreciate that the Heating Box is something we could make up from off-the-shelf parts. What do you see as the advantages and disadvantages of buying the box versus making the config up yourself (besides labor savings)?

    I don't know enough yet about the fine details of the Heating Box but my major concern is non-standard or proprietary components or fittings that might prevent me from performing a quick, affordable service call?

    For example, have you ever used the Infloor Zone Control module (that is no longer made). I've replaced three (about 20 yrs old) in the last month because the mixer failed and the 180F water stressed the thermoplastic body into splitting open, leaking and making porridge out of the gypcrete floor topping! It was fairly expensive to eliminate *this box" and replace it with new mixing valve, pump, valves and thermometers (replacements take up a lot more *Real Estate* than the compact Infloor Zone Control did). Same issue with the Infloor manifold blocks themselves. These, and many more out there, are all being replaced with off-the-shelf brass and copper components. (Note - I personally never liked the use of plastic parts in plumbing - very glad I never * bought into * using any acetal fittings back in the polybutylene days!)

    Another concern with similar such concepts I've had in the past is that one size doesn't fit all. For example the pressure drop at mid to high flow rates for instant wtr heaters varies a lot. Rinnai is lowest, by far, but Takagi, Rheem, Noritz and others have much, much higher pressure drops. And I can buy a Munchin for about $1,200+ more and get 7 to 11 percent higher efficiency. And Rinnai, while they'll bless its use with a pumped flow going through it, they'll drop the warranty from 10 to 3 years.

    Your thoughts?
  • Ray Darby
    Ray Darby Member Posts: 20


    Glad you're still with us Mark. Please see my latest reply to Dave Yates - same to you (thank you) for your posts.

    Open systems aside (I've see the light and it's an oncoming train) some documents I've read (referenced in my previous posts) and conclusions I've made as a result, make it sound nearly if not completely impossible to completely remove Legionella with (really) hot water alone.

    Be careful out there - sounds like you might still be more sensitive than most to Legionella!
  • You're welcome...

    We are here to learn AND educate.

    One possible thought I've had for possible complete erradication is to have a tank on the inlet to the system that would be chilled to just above freezing. Size this tank such that it would be twice as large as the demand tank. Utilize a water source heat pump to super chill and kill the bacteria on the first tank, and transfer the heat removed from that tank to a preheat tank. This way, little to no energy is wasted, and the bacteria is effectively eliminated. The real question is, is the bacteria killed, or just sent into a chilly dormancy...

    By the way Ray, tell us a little about your self. You seem to be fairly knowledgeable in the mechanical field. What's your back ground?

    ME

    ME
  • Rich Kontny_3
    Rich Kontny_3 Member Posts: 562
    Thanks

    I have been very involved with the testing and marketing of this product and concept.It has been a very long and difficult process with good test results.

    Due to the computer problems I have had the last couple daysI was getting very frustrated.I tried to post at the beginning of this thread with nothing but lost messages.I finally got things working and tried to play catch up with my info.

    I don't want to be miss understood as I want the scrutiny and input from the professionals that use this website forum. I have come to respect a great many individuals here without even having met them face to face.

    I would not recommend something after 38 years in the mechanical field if I did not feel it was of value. One of my biggest concerns is that HVAC firms who have taken on radiant will see this as an inroad to getting the domestic water side of things as well. (If they are properly licensed and trained I have no problem with that.)

    My preference would be for plumbers and radiant contractors to find applications for this before our friendly scorched air rivals do.

    Test site pictures will be posted shortly.

    Rich K.
  • Rich Kontny_3
    Rich Kontny_3 Member Posts: 562
    Less Chance!

    There is far less chance producing an environment for Legionaire's disease in an instataneous heater than in a tank type heater kept at the recommended 120 temperature.

    Mark Eatherton posted just several weeks ago about his exposure and subsequent outbreak of Legionaire's disease . You don"t lose efficiency at all as you heat up a smaller amount of water to past 140 degrees and then use cold to temper it!

    The efficency is relative to the old BTU definition!
    The heat required to heat 40 gallons of water in lets say a 40 gallon tank far exceeds the small amount in an on demand gas heater.

    Even heating the water up to 180 degrees and then tempering it back down to 125 is far less costly than heating that forty gallons to 120 degrees!

    If I had you all in a classroom for an hour I could show you this in that amount of time!

    I have ran all the numbers and worked with engineers who design and build these units.

    If all of you are still not convinced that on demand heaters are not feasible, why are all the major water heater manufacturers putting on an instataneous line?

    It is the same scenario as our car manufactures they are set up for tank type heaters in their manufacturing facilities and don't want to retool or admit to the public yet that tank type heaters are about to become the next dinosaur of the plumbing industry.!

    Prepare for the change!

    Rich K.


  • Rich, the only difference between tankless and tank heaters is standby losses. That's it. Once you heat up that "40 gallons", you're heating the same amount of water either way... what is used.. plus whatever is lost in standby for the tank. Don't confuse the issue.

    Water temperature does affect efficiency, I believe due to the nature of heat transfer. HIgher water temps = higher exhaust temps = less efficiency. Now it may not be a LOT depending on the unit, but it is something.

    As many of the smart guys around here are using BUFFER TANKS on heating systems, I would say if using a water heater makes sense (because you have a very low load in which a more efficient heat source would not pay for itself) that it's unlikely that an on-demand is a better choice than a tank water heater which has its own buffer already built in. If the load is big enough to make the ODWH operate well, then it's big enough to use a better heat source, IMHO.

    For domestic usage alone though, I have no problem with tankless units.