Solaroll, new boiler and furnox
Options
carpjim
Member Posts: 4
Hey all,
After 30 years it's time to replace my Laars mini therm 75000 btu boiler and circ pump.
Question is.. Flushing old brown sludgy water and adding furnox to new system.
I have heard that it's not good to have any additives with a Solaroll type system.
Any recommendations?
After 30 years it's time to replace my Laars mini therm 75000 btu boiler and circ pump.
Question is.. Flushing old brown sludgy water and adding furnox to new system.
I have heard that it's not good to have any additives with a Solaroll type system.
Any recommendations?
0
Comments
-
Where did you hear that about not adding additives?
I can imagine that some additives may be deleterious to some epdm tubing....
Not the major players though.
A call to the MFG of either Fernox or Rohmar would be a good plan though.
Dwight at Rhomar is pretty well in knowledge in the odd tubing I imagine...since there has been more odd stuff on this side of the pond.
Where is this tubing? Slab or Staple up?0 -
Tubing in slab. Heard from contractor, glycol additive would be a killer for Solaroll, that has created a little paranoia about adding anything outer than..water. But still it would be nice to know all the junk was flushed out before the shiny new pump and boiler started cranking.0
-
Mainly you need to keep all ferrous components out of the loop. Even those copper tube boilers has some metal in them.
Make sure you get every loop flushed clean, that in itself can be a job as those manifolds didn't have isolation for the loops.
Make sure the system holds pressure.
If you isolate all the ferrous metal from the hose, there will be no corrosion induced sludge forming.
The hydronic additives do offer other good benefits to the system, make sure they are blended with good quality, low TDS water.Bob "hot rod" Rohr
trainer for Caleffi NA
Living the hydronic dream0 -
Thanks for the information. The new components will be installed Monday. I'll be sure to reiterate your comments.0
-
It is a small diameter tube, high pressure drop. If you add glycol the pumps may need to upsize. It is an EPDM tube and should get along fine with glycol, but O2 does migrate through any non barrier tube. So the glycol additives will need to be boosted occasionally. Good hydronic glycols contain oxygen scavengers, that is the component that gets depleted, then corrosion is possible.
It was one of the most comfortable radiant systems. The loops were short, spacing was tight and it was a counterflow layout, so the floor surface temperature was amazingly consistent.
You should have a plan B in mind if or when the loops fail, especially if you are spending $$ to replace the boiler and components.
Often the tube would go bad right at the manifolds, maybe the UV would weaken it over time, you could rip through it with a finger nail! Try not to disturb the manifolds, it was a funky, hard to duplicate fitting there.Bob "hot rod" Rohr
trainer for Caleffi NA
Living the hydronic dream0 -
Solaroll EDPM tubing did not have an oxygen barrier. You'll need to use stainless pumps and/or separate the new boiler from the tubing with a flat plate heat exchanger. Cleaning the sludge from the tubing is essential, and a chemical treatment with both a cleaner and O2 scavenger will help.0
-
Paul,
What cleaning fluid / 02 scavenger would you recommend?
"Cleaning the sludge from the tubing is essential, and a chemical treatment with both a cleaner and O2 scavenger will help."
Thx.
0 -
There are 2 separate chemicals, the cleaner and the O2 scavenger and treatment. The cleaner is usually injected prior to the new boiler installation and allowed to circulate for 2-5 days, depending upon age of system and/or amount of sludging. It is then flushed and removed from system. The final additive is added to the new system after the new appliance is installed and purged. Either Rhomar or Fernox makes the chemicals.2
-
FWIW...
I would in no way add any glycol/ antifreeze to the system
Just stick w/ the Fernox or Rhomar.
0 -
These kits make it easy to clean, flush, and add conditioner. I think they do a 30 gallon system.
I agree, glycol only if absolutely need for freeze protection.Bob "hot rod" Rohr
trainer for Caleffi NA
Living the hydronic dream0
Categories
- All Categories
- 85.7K THE MAIN WALL
- 3K A-C, Heat Pumps & Refrigeration
- 49 Biomass
- 424 Carbon Monoxide Awareness
- 72 Chimneys & Flues
- 1.9K Domestic Hot Water
- 5.2K Gas Heating
- 92 Geothermal
- 149 Indoor-Air Quality
- 3.2K Oil Heating
- 59 Pipe Deterioration
- 848 Plumbing
- 5.8K Radiant Heating
- 372 Solar
- 14.5K Strictly Steam
- 3.2K Thermostats and Controls
- 50 Water Quality
- 48 Industry Classes
- 47 Job Opportunities
- 15 Recall Announcements