Hot water boiler pressure relief valve

Options
HAB
HAB Member Posts: 11
Can a hot water heater T&P valve be used on a hot water boiler? The boiler currently has pressure relief only.
Thanks

Comments

  • JUGHNE
    JUGHNE Member Posts: 11,063
    Options
    NO, water heater tank relief valves have too high of a pressure setting, maybe 150 PSI. at that pressure your boiler could launch itself as a missile thru all vertical layers of your house.

    30 PSI is the max for most residential boilers. Pressure relief only. Temperature is controlled/monitored by 2 or more safety devices internal to the boiler system.
  • HAB
    HAB Member Posts: 11
    Options
    Thanks. I will get a 30psi pressure relief to match the origianal one.
    damitdave
  • j a_2
    j a_2 Member Posts: 1,801
    Options
    Don't just match what was there, go to the manual, put in the one it calls for, if you have any question at all in your mind....does it have a low water cutoff...
    damitdave
  • damitdave
    damitdave Member Posts: 2
    Options
    in need of low water cutoff and pressure releaf valve ?????