Econoburn Biomass System completed.
Everything is working in perfect sync. Very impressed with the Econoburn wood boiler. The home owner doesn't even have to leave the living room to find out whether or not he needs to put wood on the fire. Put a control in the living room that shows tank temp, system target temp, outdoor temp, and whether or not the backup gas boiler is firing.
Nice!
I'm curious about the interesting symmetric piping detail you chose for the tank connections?0 -
It is approved to my knowledge. I wouldn't use it on a non gasifier. Creosote buildup and potential chimney burnout exceeding 1000 degrees vaporizing the zinc. This boiler doesn't smoke. It burns at over 2000 deg and the stack temps are around 500 to 550.0
Stephen,
Yes it was. I did have to make a lot of changes though. The boiler piping was reversed and the boiler pump was much to large. The radiant was staple up with 180 deg water running through it, mainly because the installer didn't know how to run DHW and an ODR curve from the boiler.
Got extruded plates put in the floors and added flat panel radiators to supplement were needed and bring all the zones to a common temperature. That also helped lower the required system temp and maximize the thermal storage tanks.
It has been and interesting project. Split up in 3 phases over the course of a year.0 -
Kurt,
The tanks are piped with 2" and tied together with 2" headers. This provides hydraulic separation between the boiler pump and the variable speed transfer pump to the house. It is configured in reverse return to promote equal flow through the tanks. The boiler and system are piped off the ends of the header with 1-1/4". The configuration also allows the system and DHW, more importantly, to pull directly off the boiler before the tanks start loading. This holds true as long as the system flow is the same or less than the boiler flow. If the system flow is higher than the boiler flow, mixing from the tank will occur in the header.1 -
The HO took care of getting the tanks in place. So I didn't have to worry about that. He is a retired engineer, and a very sharp fellow I might add. It is interesting to see his inventions and methods to do things.0
If that was my house, I wouldn't need anything in the living room, that would be my living room. Beautiful work you should be very proud of that.2
Tell him to read the installation instructions on that fiberglass batt in the walls. I am not sure why almost everyone seems to think the paper tab is supposed to be stapled to the inside of the stud instead of the face, but a lot do. That is a lot of hard work to do it wrong.
Your stuff looks great though!
Rick1 -
Yeah, but then when you apply drywall glue and screw the sheet onto the studs, your glue does nothing since it's adhering to stapled paper.rick in Alaska said:Tell him to read the installation instructions on that fiberglass batt in the walls. I am not sure why almost everyone seems to think the paper tab is supposed to be stapled to the inside of the stud instead of the face, but a lot do. That is a lot of hard work to do it wrong.
Rick0 -
It does compress the insulation 1 1/2" at the edge of the batt which decreases r value some. Plus it does not do its job as well as a vapor barrier........technically. I prefer unfaced with visquine. Really there is better choices than fiberglass.rick in Alaska said:Tell him to read the installation instructions on that fiberglass batt in the walls. I am not sure why almost everyone seems to think the paper tab is supposed to be stapled to the inside of the stud instead of the face, but a lot do. That is a lot of hard work to do it wrong.
Rick
On the other hand as been said if you glue your drywall then that would make for a worthless bond, all though gluing drywall is some what redundant being the paper to wood bond is quite more than the paper to gypsum bond. More screws is the better choice.
1 -
That is some phenomenal work ( thank you spell check ). Those " heavy residential " projects are more difficult than alot of commercial work.hvacfreak
Mechanical Enthusiast
Burnham MST 396 , 60 oz gauge , Tigerloop , Firomatic Check Valve , Mcdonnell Miller 67 lwco , Danfoss RA2k TRV'sEasyio FG20 Controller
1 -
Harvey, who makes those tanks?Tom
Montpelier Vt0 -
The tanks are repurposed propane tanks. They can be had for a very reasonable cost. They are also built heavy enough to act as a low pressure vessel. Only thing, no ASME rating, so they can't be used everywhere. There are a number of companies offering these types of thermal storage tanks now. http://www.smokelessheat.com/categories/thermal-storage-tanks0
That is reasonable. How is the end user insulating the tanks? Or is the user building a super insulated room around the tanks?0
Those re-purposed LP tanks are very common for wood burners. A handful of wood boiler suppliers offer them.
I have seen them wrapped with bubble foil, fiberglass batts, rigid foam boxes and even spray foam.
Here is an example from AHONA.Bob "hot rod" Rohr
Living the hydronic dream0 -
In this case, we built a box around the tanks and stuffed it full of fiberglass, The tanks loose less than 1/2 deg per hour at nominal temperature.Gordy said:That is reasonable. How is the end user insulating the tanks? Or is the user building a super insulated room around the tanks?
Spray foaming the tanks is also popular but it's expensive and looks like a hat full of butts.3 -
Thanks Harvey, very nice job as well!!!Tom
Montpelier Vt0 -
Looks great. I wonder what kind of insulation you will use on the piping? I used 1" thick neoprene with the sticky edges, but they don't stick forever, for sure. I've had to restick some with glue made for the purpose. I saw a picture of a white pipe insulation-probably jacketed fiberglass-maybe not as insulating as the neoprene, but it looked gorgeous.0
Have you tried this double seal insulation. It has a nice sticky flap over the seam seal. Most of the insulation manufacturers off this type now.Bob "hot rod" Rohr
That insulation is great that Hot Rod posted we use it all the time for low temp refrigeration.0
Looks like you only have one circulation pump, there should have one for the boiler and one for the tank. How are you keeping the boiler temperature up to avoid thermo shock and creasote build up?0
The boiler is protected from cold return water with a bypass controlled by a Caleffi Thermomix protection valve. In that configuration, only one circulator is needed.Grattan said:Looks like you only have one circulation pump, there should have one for the boiler and one for the tank. How are you keeping the boiler temperature up to avoid thermo shock and creasote build up?
I am experimenting with different temp elements for the valve. I just put in a 160° element which should allow the tanks to stack at setpoint on the first complete water change.
I saw as much as a 100° difference in stacked temp when first loading the tanks. Easily 50° at various points in operation.
- 86.9K THE MAIN WALL
- 57 Biomass
- 109 Chimneys & Flues
- 5.7K Gas Heating
- 105 Geothermal
- 70 Pipe Deterioration
- 975 Plumbing
- 6.3K Radiant Heating
- 387 Solar
- 15.4K Strictly Steam
- 44 Industry Classes