Recommend a circulator control?
bugaboo
Member Posts: 14
I have three heat zone circulators, a primary circulator, and an indirect. The indirect comes directly off the primary, so when it calls I don't want the primary circ running.
What controls do you recommend to run this?
Thanks!
Thanks!
more info
What kind of boiler and zone controls?0 -
Definately Need Info
Some boilers can prioritize DHW and control the operation of the primary circulator and the DHW circulator.0 -
deleted.....duplicate0 -
Primary/Secondary or injection.
I'm not sure what you are saying in that you don't want the primary pump to run when secondary pump calls...? You primary is responsible in moving enough water through the boiler, and that's step #1, #2 this is your feed to all secondary pumps off the loop and/or injection. Even if your secondary drawn off the main loop, Watch out for short cycling that will eventually kill your boiler. The primary should be sized for providing all zones with enough flow and maintaining minimum boiler flow in GPM.
Mike T.0 -
Boiler
The boiler is a Peerless WBV-03 with the stock Honywell control. I don't have the number offhand, but it has outdoor reset capability.
I don't have any zone controls yet. That's actually what I'm asking about.
I have plumbed the indirect according to the boiler manual, and what I have seen in for other boilers. Immediately out of the boiler the supply and return T. One outlet goes to the indirect, and the other continues as the primary loop, The return is the same.
This makes for two primary loops, one for space heating, and the other for the indirect. So, the indirect circulator is one primary, and the space heating has another. The three secondary loops all have their own circulators off the space heating primary.
The way they have this set up the space heating primary does not need to heat up during a call for domestic hot water. In the non-heating season this will save energy. It's the only reason I can see for them recommending this setup.0 -
What
you are describing works very well on boilers that have the ability to control primary and DHW circulators. That is not what you have, and that is not what is described in the manual. The simplest way would have been to pipe it primary/secondary with indirect as a zone.Then use something like a Taco switching relay with domestic hot water priority.0 -
Switching control
I would use the Taco Sr504 to do the job. The challenge is how do you turn off the primary circ during dhw priority? If you run the dhw circ power into a relay like the tekmar 004. You can connect the dhw pump to the normally open on one side of the relay and intercept the power to the primary circ on the normally closed terminal on the other side.
Albert Einstein0 -
Use only 504?
Could you use the 504 only and run the system pump off the ZC connection after you lift the jumper? Not sure if that would work, can't find info on what zone 4 connections do with no jumper from ZR to ZC.(I guess I could go to the shop and wire one up to experiment with)You can have it good, fast or cheap. Pick two0