Help............................Need Sq Ft Rating
TK03
TK03 Member Posts: 54
Thanks Dan. We at Burnham thank you for all you do.
  • TK03
    Help ..................Need Sq Ft Rating.
    I have a customer which is looking for a rating and I cannot find anything on it. He claims to have called Dunham Bush and they did not have the ratings. Does anyone have the sq ft rating for a Dunham Bush V400H Steam fired unit heater.
    Thanks
  • Brad White
    Brad White Member Posts: 2,399
    Maybe a dumb-@ss-umption but
    400 MBH at 2# steam pressure? So 1,666 SF? Nomenclature assumption only :)
    I checked my D-B catalog and there is a tab card saying "Unit Heaters Out of Stock!", so no telling.
    The cabinet unit heaters are listed by nominal CFM so while the 400 MBH seems huge, 400 CFM seems hardly worth it, so I would go on the 400 MBH assumption.
    "If you do not know the answer, say, "I do not know the answer", and you will be correct!"
    -Ernie White, my Dad
  • DanHolohan
    DanHolohan Member, Moderator, Administrator Posts: 16,706
    I have it.
    At 1060 rpm it would be 96,000 Btuh
    At 840 rpm it would be 85,500 Btuh
    Retired and loving it.