Steam heat - how much oil are you burning?

Gene_3
Member Posts: 289
really wrong, 30-55 minute run time??????????? wholy moly, is there perhaps a ton of mud in the system??, is the pressuretrol working????? all of the pipes and the home insulated, all storm doors/windows closed?
your burner should come on, run @ 10 minutes and shut off when it builds up .5-2lb steam max, once you have a head of steam up the burner does not need to run. make sure the pressuretrol is set for .5 and 1 on the differential for starters,is the pigtail plugged?, flush the lwco and the boiler and returns for mud, clean water makes steam efficiently, mud takes forever=longer run time, don't go by the gage glass and do not refill a hot boiler with cold water but to get a good flush you need to do it while it is warm/hot not steaming, you may need to have the boiler skimmed.
your burner should come on, run @ 10 minutes and shut off when it builds up .5-2lb steam max, once you have a head of steam up the burner does not need to run. make sure the pressuretrol is set for .5 and 1 on the differential for starters,is the pigtail plugged?, flush the lwco and the boiler and returns for mud, clean water makes steam efficiently, mud takes forever=longer run time, don't go by the gage glass and do not refill a hot boiler with cold water but to get a good flush you need to do it while it is warm/hot not steaming, you may need to have the boiler skimmed.
0
Comments
-
still suffering with high fuel bills
So I'm still suffering with my high fuel bills and two odd radiators that don't want to heat well (they are pitched properly with no venting problems and the radiator valve heats up nice and warm very early in the cycle).
I've decided to not replace the near boiler piping since we'd like to save up enough money to be able to replace the boiler at the same time we add radiators to part of the downstairs and attic that presently have no radiators. (400 sq ft on the first floor is presently heated by a gas wall furnance and most of the third floor is unheated).
I wasn't able to find any historical threads where people talked about their oil usage. Here's the information on my 1-pipe steam system, Waltham boiler, Riello burner.
From 10/18 - 11/19, with the house temperature set between 62-64 my system ate 142.7 gallons of oil (avg approx. 4.5gal/day). During a good portion of this time, the system was short cycling, mains were uninsulated and unvented, pressuretrol was set to 2.5, thermostat had a messed up anticipator, and the boiler chamber was full of soot with the back wall collapsed in - these issues are all resolved. There was also about a week of warm days during this period.
Since 11/19 with all of the above issues resolved and the house temperature set to 64, there have been many cold days and about 70 gallons of oil have been used up (avg 8.75 gal/day).
The oil is used to heat about 1800 sq feet of space spread across 2 1/2 floors, with limited (if any) insulation in the walls.
I'm interested in hearing how much oil your system is burning, what kind of space it's heating and what temperature your thermostat is set at. I'm unclear if the large amount of oil I'm using up is normal or not since I can't find any data to compare it to.0 -
I installed a new WM SGO-4 this summer. I installed an interval meter to track oil usage, so I can give you some accurate info for Boston area for the last week or so.
From 11/22 to 11/27, my burner ran 13 hours with a 1.1 gph nozzle, or 14.3 gallons of oil. I keep the temp at 69* from 6AM to 8AM and 3PM to 10PM on weekdays and 8AM to 10PM on weekends and holidays. Night-time setback temp is 62*, but the house rarely gets that cold. My home is well insulated with tight windows. I have around 1800 square feet of space, heated with steam except for one 12x16 foot room with cathedral ceiling that is heated with water baseboard driven off the steam boilers with a heate exchanger.
My plan for this winter is to track degree days, sun versus clouds, and wind speed to get a good handle on energy use and be able to have hard data of relative energy savings versus my 70 year old ex-boiler.Steve from Denver, CO0 -
Pete, check out this article on comparing energy usage. You need to get the heating degree days to figure it out. Then you can tell where you are, roughly. More importantly, it will let you know if you need to spend your money and time on tightening the envelope and insulating.
http://www.homeenergy.org/consumerinfo/benchmarking-energy-usage/index.html0 -
waltham boiler
so Pete are you going to live with the banging pipes all winter long?
To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"0 -
no more water hammer
Interestingly enough, the water hammer has been basically non-existent since the chamber was replaced on the boiler. Since the main vents were added, the radiators no long choke on air and make hissing sounds. The system has been extremely quiet for a few weeks, you wouldn't even know it's on.
The largest annoyance right now is the excessively high fuel usage which I'm having a difficult time determining if it has something to do with the boiler/near-boiler piping or if it's just related to the fact that the house is mainly uninsulated.
There's still of course the 2nd floor radiator which although it gets steam very early in the cycle, it just won't get hot enough even though it is vented fine and the radiator itself is pitcher properly.0 -
jealous
Wow, I'm jealous that you can heat your whole house for 5 days on 14.3 gallons of oil when I burnt 50 gallons in the same time period with the thermostat set many degrees cooler. Do you have any sense how much oil you burnt in a cold week with your old boiler/burner, even if the days weren't totally comparable? My boiler is 25 years old and for what it's worth, the oil company 'claims' that it is 80.5% efficient.
Out of curiosity, how long are your typical steam cycles and approx. how often is the system kicking on? Since I stopped the short cycling, my system is kicking on every 2-3 hours, but the run-time is significantly longer than it used to be (it is often between 30-55 minutes), always turned off by the thermostat. Previously it would turn on 3-4 times an hour and run for only a few minutes each time (and this was during days that weren't very cold).0 -
burner doesn't kick off until thermostat is satisfied?
I'm going to have to sit at the boiler/thermostat and time it again, but this is what I was seeing.
I have no idea if the pressuretrol is working, the gauge never appears to move and the pressuretrol is set to .5 and 1 on the differential (correction: just double checked). From what I can tell, I have never seen the burner shut off before the thermostat is satisfied, basically the burner appears to run non stop from the time the thermostat calls for heat until the thermostat is satisfied.
I'm sure this is going to sound stupid, but how would I know if the pigtail was plugged?
All of the steam mains are now insulated, the home has limited (if any insulation) and all of the storm windows are down.
I don't think the boiler has even been cleaned in 25 years, the oil company does not use tsp or similar chemical. The only thing I've been doing is letting the yucky water out every few days and refilling it.0 -
just double checked pressuretrol
> I'm going to have to sit at the boiler/thermostat
> and time it again, but this is what I was
> seeing.
>
> I have no idea if the pressuretrol is
> working, the gauge never appears to move and the
> pressuretrol is set to .5 and 1.5 on the
> differential (doesn't go to 1). From what I can
> tell, I have never seen the burner shut off
> before the thermostat is satisfied, basically the
> burner appears to run non stop from the time the
> thermostat calls for heat until the thermostat is
> satisfied.
>
> I'm sure this is going to sound
> stupid, but how would I know if the pigtail was
> plugged?
>
> All of the steam mains are now
> insulated, the home has limited (if any
> insulation) and all of the storm windows are
> down.
>
> I don't think the boiler has even been
> cleaned in 25 years, the oil company does not use
> tsp or similar chemical. The only thing I've been
> doing is letting the yucky water out every few
> days and refilling it.
0 -
hmmmmm
It's hard to say from here, the only real way to see if the pigtail is plugged is to remove it.
before service it ran a certain cycle and now runs long?? I'm starting to wonder if they changed the nozzle or downfired it??something changed. It should be running more efficient now not worse. A lower firing rate will cause the burner to run longer, it may look good on paper with a low stack temp but the reality is we need steam and we need it now. From what you say you have an old behemoth with a Riello, rule of thumb is to downfire a flame retention burner @10% from the old rate because it is a hotter fire. Did they remove any baffles?? Is the draft regulator stuck closed?? something had to change in the wrong direction for you to end up with these results, logic dictates it.
How are you determining how much oil you've burned?? could you calculations be off??0 -
Long story short (sorry, not short enough)
We're new to the system, this is our first winter in the house. Here's the progress we've made in just a couple of months with help from folks on the board and our local heating experts.
When we started, the system was constantly short cycling and not heating most of the radiators. Fuel was being burned at a high rate when the temperature outside was only in the mid 50s. The system would come on and off 3-4-5-6 times or more an hour and fire up for 3-4 minutes each time without ever heating most of the radiators (it appeared that the thermostat was shutting down the system at this time because the radiators near the thermostat were getting all of the steam).
We tried adjusting the anticipator setting since it wasn't set properly for steam heat, but then the thermostat never stopped calling for heat and the temperature was being overshot.
There were so many other problems at this time:
The mains were unvented, so the radiators were choking on air and heating in the house was very uneven. The two long main runs are now each vented with a Gorton 2.
The mains were uninsulated, so the basement was a huge radiator and about 30 degrees warmer than the rest of the house. All of the mains are now insulated with 1 inch fiberglass with 1/2 inch insulation on the radiator runs that were reachable.
The boiler chamber back wall had collapsed in and was full of soot so the fire was bouncing off of the back wall of the chamber. The boiler chamber has been cleaned and replaced, and strangely enough, this has basically eliminated a loud water hammer that was popping up to the left of the boiler where whoever installed the system decided to use the skim port to take steam out.
Most of the radiator vents were non-functional and had been painted shut. These have since been replaced with new Gortons and Varivalve Heat-Timers.
The pressuretrol differential was set to 2-2.5. It is now set at 1.
With the new thermostat (t87 digital round set to steam cycle/1 per hour per manual) and all of the other changes, the thermostat is calling for heat a lot less often (once every 2-4 hours, sometimes even longer depending on how cold it is outside). However, it is taking much longer than it used to for the thermostat to be satisfied (the system is much more balanced than it used to be and all of the heat isn't ending up at the radiators near the thermostat). It doesn't appear the system is ever being shut down by the pressuretrol, but I don't really have any way of knowing. One thing that hasn't appeared to improve drastically is the oil usage.
I see the burner fire up and run non stop until the thermostat appears to stop calling for heat because the thermostat is happy. Given that this is the first time I've ever had steam heat and a boiler, I had made an assumption this was normal.
The only way we have to measure oil usage is by looking at the gauge on the tank, but it appears to be right on since it's a 275 gallon tank, the last delivery was for 142.7 gallons and the tank gauge was about 1/8 to 1/16 under the 1/2 full at time of delivery. Last delivery was on 11/19 and the tank is now reading about 1/8 under the 1/4 mark.
When the oil company came out to rebuild the boiler chamber, I didn't see them touch the nozzle. When I asked about the fire he seemed to state was that if it wasn't set up right, it wouldn't be firing up, he seemed 'pleased' that it fired right up. He did notice a small oil leak inside of the Burner and tighented up a bolt which appears to have corrected that.
The draft regulator is new (as of August) and is not stuck closed.
One of the steam experts we had out pointed out that the near boiler piping is off since there are only 17 inches from the water line to the header vs. 24, so based on our clearance we would need a dropped header built. We have decided against doing this since we would prefer to hire him once we can afford a new boiler, 3 additional radiators and his time to connect them up.0 -
Interval Meter - Attn: Steve Garson
Hi Steve:
I saw your post in response to Pete and I am curious about the interval meter that you mentioned. I would like to install one as well in order to monitor oil usage more accurately.
How much do they typically cost? Is there a particular brand or make that you would recommend? Is it easy to install or should a professional do it. Thanks again for any info and I am also jealous of your highly efficient system. Take care.
Steve0 -
Hi,
I'm far from a steam heating expert, but did have steam heat in my old appartment. When the thermostat requested heat the boiler would kick on and it would run until either the temp had been reached or the pressure would tell it to turn off. Sounds like you either don't have enough pressure to have the pressure regulator kick in or the pressure regulator is broken.
Michael0 -
It sounds like they down fired your boiler or your pump is no longer building enough pressure (smaller nozzle or lower pump pressure) can you look at your plate and see what pump pressure,Gph and degree they call for. This should be the way the mfg found the best efficiency and the rated output for your boiler. It would be a good idea to compare what the mfg called for to what you have. The water hammer stopping and the longer run times sound like a down fire. If you raise it back to the old way, It might start to bang again if your piping is wrong. Did you ever remove the vent on the rad on the 2nd floor? If it won't heat with the vent out take the radiator union off at the valve and see if the valve will blow steam. It sounds like you either have a plugged radiator or a radiator valve that is not opening. Best of luck.0 -
burner
The plate on the burner says 0.63 Gph, it doesn't say anything about pump pressure and degree.
On the service tag, the oil company wrote:
Size 100 Angle 60 Spray W
I wouldn't know what way to turn it to raise it back the old way since I'm not sure what it was set at/what it is now set at.
I have removed the vent on the radiator on the second floor and the radiator does not heat up any better than with the Heat-Timer set to max-open or Gorton D.
I haven't tried taking the radiator union off the the valve, but the valve does get extremely hot from the steam as well as the first few inches on the first radiator section.0 -
What is the proper cycle? Should the pressuretrol kick in?
The thermostat is requesting heat properly on temperature and when it kicks off, the temperature is not being overshot.
Since all of the changes have been made to the system, it definitely takes much longer for the room with the thermostat to heat up to temperature. I just figured that this was happening since the system is now much more balanced vs. before all of the heat was ending up in the room with the thermostat and nowhere else in the house.
I am waiting for the system to kick on again today so I can time how long it stays on for.
Is it normal or abnormal for the burner to run non stop from the time the thermostat calls for heat until the time its temperature is satisfied or during normal operation would you expect the pressuretrol to kick in prior to the temperature being satisfied since there's a point in time when you've filled the mains with steam and you're no longer accomplishing anything by keeping the burner running even if the thermostat is still getting up to temperature?0 -
Hi,
Don't think you can use time as a valid comparison value. Each setup will be different. Mine was an example a small boiler with only 5 radiators in ~1000sqft or so.
The main vent should only vent air until steam hits it then the steam should move forwards to the other pipes/radiators which then will vent until steam heats them.
You should have a pressure gauge on the boiler. I'd monitor that one and notice what the pressure actually reaches. I'd also pay attention to the main vents as well do they ever close.
The real pro's on this web board (not me) will be able to guide you on what pressure readings you should see.
Michael0 -
more hmmm
you stated--"When the oil company came out to rebuild the boiler chamber, I didn't see them touch the nozzle. When I asked about the fire he seemed to state was that if it wasn't set up right, it wouldn't be firing up, he seemed 'pleased' that it fired right up. He did notice a small oil leak inside of the Burner and tighented up a bolt which appears to have corrected that."
when a chamber has collapsed the burner needs to be thoroughy checked out, it may been subjected to intense heat. Any oil system must be serviced annually, vac, noz, oil filter, oil pump, check settings check oil pressure, check chimney etc etc. if they just did maint and returned for the chamber that's one thing but to just replace a chamber and leave???? unless that was your request
this part{if it wasn't set up right, it wouldn't be firing up, he seemed 'pleased' that it fired right up.} should have your attennae up
if it is not set up right it may or may not light, I too am pleased when they light however it sounds like his was a sigh of relief, it could be he was unfamiliar with Riello or just nervous because the customer was present or both
my advice at this point is to shop for new service
you also stated-- the last delivery was for 142.7 gallons and the tank gauge was about 1/8 to 1/16 under the 1/2 full at time of delivery. Last delivery was on 11/19 and the tank is now reading about 1/8 under the 1/4 mark.
do you mean under 3/4?? because if you are under 1/4 now you burned 200 gallons in 10 days
bear in mind the tank has an air space at the top, they never take 275, maybe 240 when new, if you're under 3/4 now you burned maybe 40-50 gallons that is if it was full, thanks to our govt we now have dye in our fuel oil that makes it foam more on delivery and your whistle goes off before it is full, so the top 1/4 is not the same as the bottom, plus tanks are curved top & bottom, you have more oil in the middle that at either end.
The most accurate way to tell is to go from delivery to delivery.
0 -
Pete, can you get a copy of your burner setup and your boiler install guide off the web? The factory desired setup should be in the guide.0 -
manuals
Waltham (boiler mfr) is out of business and I have been unable to find any of the manuals online or in paper format. I will see if I can find any information on the Riello 3KA unit.0 -
manuals
Waltham (boiler mfr) is out of business and I have been unable to find any of the manuals online or in paper format. I will see if I can find any information on the Riello 3KA unit.0 -
Maintenance
They had supposedly done all of this maintenance in August, but the level of their work is definitely suspect when the boiler chamber wall had completely collapsed and was full of soot and they called the chamber "good" on their check list. He didn't appear to do anything to tune the burner after putting it back in place. He seemed happy as I stated that it lighted up and he centered it.
Sorry, yes, I did mean 1/8 under the 3/4 mark.
Agreed that best way to judge consumption is from delivery to delivery.
--
Outside temp is currently 49F, thermostat is set to 64F and is at 64F, thermostat has not needed to call for heat in the last 5 hours. Once it calls for heat again, I will time how long it takes for the mains to heat up and for the thermostat to be satisfied.0 -
Pete,
You can install an ac hour meter in series with the burner motor. This will track how long the burner is running, just multiply the on time by the nozzle size to get gallons burned. If there is an oil valve with a pre purge then just hook the hour meter in series with the oil solenoid. Only attempt this if you know what you are doing. Get another service tech, ASAP! You can't tell that a burner is firing properly without doing a combustion analysis. Sounds like to need to start working on tightening up the building envelope at this point. Hope this helps.
0 -
Nice trick, but won't you need to know your pump pressure and a nozzle chart to figure the consumption?0 -
cycle time
So unfortunately I had to step out so I don't know exactly when the burner kicked on, but the latest run time was at least 27 minutes (could have been as long as 40). This was a fairly cold start given that the last time it fired up today was early this morning.0 -
Good question. I've just been assuming a 1.1 gph nozzle will use that much oil. Not true?Steve from Denver, CO0 -
Good question. I've just been assuming a 1.1 gph nozzle will use that much oil. Not true?Steve from Denver, CO0 -
Pete,
You are going to make yourself crazy. Forget about timing this and that and cyles. It means nothing. No, really. Every house has a different heat loss, different insulation values, etc. Every day is a different temperature, the sun is in the sun is out the wind is blowing or it is not. See where I'm going? Many factors, many variables.
The boiler is old, the system might not be just right. You seem to be on the right path in fixing it. Insulation is the key. You could have the most efficient boiler in the world but if your house leaks like a sieve you will have high energy costs.
Just because a burner starts it does not mean it is adjusted properly. This can only be done with combustion testing equipment, any "good" oil man can do this.
The 17" thing is not the end of the world either. While not ideal or "perfect" it should work . It has been for years. If you change the boiler then this can be addressed.
Don't stress out over this, it won't change a thing. Check out Dan's books;
http://www.heatinghelp.com/shopcart/product.cfm?category=2-3
http://www.heatinghelp.com/shopcart/product.cfm?category=2-3
To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"0 -
agreed
I had a customer once, he just retired from being a nuke plant engineer, he had every gage, timer, weather station etc and had an office in the basement where he tabulated all this info everyday and if it didn't jive we got a call that something was wrong, he even timed the blower, return air, supply air, humidity in and out, you name it he checked it.
that said, it is wise to keep an eye on usage and you are right to do so, if every customer did we could send a couple of tankers back, just don't go crazy.
Call a couple of companies and see if they'll send out a tech to do a free analysis for the opportunity to get a new customer, it may bring you some piece of mind.0 -
oil co
I had them come out and look at increasing the fire based on the long period of time it's taking to produce steam and feedback from this thread. (The fact that it's taking a good 20+ minutes to get steam and 25-30+ to begin to fill the main and begin heating the radiators).
He said that it is firing at 1.0 and the Riello 3KA puts out 145 ?psi?. He said that in the past someone had accidentially put a 1.1 nozzle on it and the unit built up soot and had to be cleaned out and a 1.0 needed to placed on it (he showed me the service tags when this happened). He said that given the physical size of the boiler (amount of water it has), the only way I'm ever going to get the oil usage down is to get a new boiler, but perhaps I would still have burnt 8 gallons per day on those cold days vs. 10.
Per the advice in the thread, I had another oil co come in since the guy was very nice and is also a paid advertiser on the board. He looked at the size of the unit, piping, burner, etc and he felt based on my description that it needed to be fired at 1.25 gph to produce steam much faster given the size of the boiler, but he did not turn on the burner to see the fire.
The boiler is feeding ~428sq ft of EDR.
From a cold start, how long does it take you to produce steam and then how long is it taking to get to your radiators? What size radiation are you feeding? I am still unsure of how long I should expect the oil to burn away before the boiler starts making steam.
I think the most amazing learning experience from this process is that I haven't once found two experts that agreed on the same solution to a problem
Thanks again for all of your help.0 -
Waltham and Riello
The Waltham is a 1960's vintage boiler. That Riello 3KA was last mfd in 1981 and parts availability stopped in 1991. That may be why the tech gave a sigh of relief when it fired. Nozzles are available as they haven't changed but I'm not sure about pump screens.
Save your money and get an up to date system. Is this the boiler with the smoke pipe coming out the bottom?
Leo0 -
lucky me
My wonderful 1960's vintage Waltham beast and the 3KA were installed in 1979-1980. I definitely want to get a WM SGO, but need to get some money first
The smoke pipe comes from the center top.0 -
Waltham
I could be wrong on the Waltham as I have only seen the old ones. I know the burner date though.
Leo0 -
Interval meter
Steve:
You can use an old mechanical alarm clock connected to the power feed to the burner ignitor or fuel pump. If you're not experienced with wiring, have someone else do it. There is often a lot of wiring in a tight utlity box and you don't want problems.Steve from Denver, CO0
This discussion has been closed.
Categories
- All Categories
- 86.9K THE MAIN WALL
- 3.2K A-C, Heat Pumps & Refrigeration
- 57 Biomass
- 425 Carbon Monoxide Awareness
- 110 Chimneys & Flues
- 2.1K Domestic Hot Water
- 5.7K Gas Heating
- 106 Geothermal
- 160 Indoor-Air Quality
- 3.6K Oil Heating
- 70 Pipe Deterioration
- 978 Plumbing
- 6.3K Radiant Heating
- 387 Solar
- 15.4K Strictly Steam
- 3.4K Thermostats and Controls
- 54 Water Quality
- 44 Industry Classes
- 47 Job Opportunities
- 18 Recall Announcements