Boiler protection with P/S piping
Student_3
Member Posts: 1
Hi All,
Replaced boiler and water heater last year. New one is conventional boiler and indirect fired water heater. Several questions.
a) What is acceptable time for return temperature rise to 130 F after night setback (there are visible signs of condensation during cold start up)?
b) Right now there is primary/secondary piping in the system. Is it a good idea to provide additional by-pass piping to boost boiler temperature? Some sources (e.g. John Siegenthaler) recommend three way thermostatic valve for this purpose, but what brand? As far as I understand Cv of the valve has to be at least 10 in my case. Is it possible just to bypass close spaced Tees in primary loop and use Taco I-series two-way thermostatic valve as an intelligent bypass? I think it also might increase system's efficiency, because usually average boiler temperature during heating cycle is about 150 F
System data:
Boiler: AGA input : 75,000 Btu/hr
Heating Capacity : 63,000 Btu/hr
Primary pump: Taco 007
Secondary Pumps: Grundfos UPS15-58
Indirect water heater: Peerless PP-60 (57 gal)
It is one-pipe diverter T system with baseboards (a couple of cast iron radiators too).
You help is highly appreciated.
System data:
- 167 Indoor-Air Quality