John Cox
Member Posts: 1
I am looking to adding a 2" air separator in a bypass configuration to an existing 3" line. This will allow some of the water to go through the air separator. Will this be effective? NOte, adding a 3" directly is not possible.
0
Comments
-
Any microbubble resorber
filter, strainer, etc. in a bypass configuration will work. It will just take longer to do a full job.
Keep in mind:
1) You will need some main-line restriction to get nearly any flow through it. Hard to convince flow in a 3" pipe that going through a 2" device with a scrub-brush is going to be fun.
2) I suggest you pipe it across supply and return unless it is a condensing boiler. Otherwise assure a good bit of pressure difference in parallel with the device.
3) The presumption of using any device in a bypass arrangement is that the rate of contaminants being introduced (air for a separator, dirt for a strainer or filter) is less than the through-put of the device. In other words, don't expect to deaerate a system with ongoing leaks.0
This discussion has been closed.
Categories
- All Categories
- 87.3K THE MAIN WALL
- 3.2K A-C, Heat Pumps & Refrigeration
- 61 Biomass
- 429 Carbon Monoxide Awareness
- 120 Chimneys & Flues
- 2.1K Domestic Hot Water
- 5.8K Gas Heating
- 115 Geothermal
- 166 Indoor-Air Quality
- 3.7K Oil Heating
- 77 Pipe Deterioration
- 1K Plumbing
- 6.5K Radiant Heating
- 395 Solar
- 15.7K Strictly Steam
- 3.4K Thermostats and Controls
- 56 Water Quality
- 51 Industry Classes
- 50 Job Opportunities
- 18 Recall Announcements