    Who makes a good pressure activated bypass valve? I have a client with three zones with zone valves that make a racket when closing. Or, any other ideas? I'm tempted to see if swapping a 007 fot the B&B series 100 will tame the monster!? Any thoughts? Thanks in advance.
    Adam
  • adambuild
    ZV's
    They're not, they're just fighting a big bad pump on closure!
  • J.C.A._3
    J.C.A._3 Member Posts: 2,980
    Personally,
    I like the offering from Viega and Oventrop, but why not look into something that opens and closes slower for a ZV?
    When I install the piping, I'll use a spring close ZV, when there is any doubt about the piping, I usually go with something that opens AND closes slowly.(Taco makes some nice ones, and a control that makes things very easy to wire). Chris
  • hr
    hr Member Posts: 6,106
    Will the series 100
    be enough circ to meet the load? Sounds like an expensive switch requiring yearly maintenance.
    What type of ZV's? I have always zoned on the return and never had hammer noises, even with fast acting ZVs.
    Shouldn't really need a PAB with three zones, but if it is the easiest fix... I've used the use the Honeywell Braukman, Danfoss and Caleffi.
    Be sure to include a ball valve on one side so you can purge.
    hot rod
  • adambuild
    ZV's
    The current ZV's are Honeywell V8043E1012.
  • bob_50
    bob_50 Member Posts: 306
    Adam
    a B&G 100 produces less head than a Taco 007.
  • Robert_15
    Robert_15 Member Posts: 62
    i had the same issue with banging pipes we swithed the zone valves to the return and it stopped
  • Bob Forand
    Bob Forand Member Posts: 305
    Caleffi
    Caleffi makes a great pressure by pass valves. Caleffi makes awesome near boiler hydronic materials...
  • grindog
    grindog Member Posts: 121
    taco
    taco makes a great one easy to install and adjust. we put one in just the other week.
    Try a grundfoss super brute and put it on the lowest setting maybe that will help