water heater for new tub and shower

Options
D lux_2
D lux_2 Member Posts: 230
could have a 300.oo tax credit and install next to bath room

Comments

  • LivDoug
    LivDoug Member Posts: 2
    Water heater for new tub and shower???

    I am currently having my master bathroom remodeled, and I have a 6ft whirlpool tub and a new spa shower with multiple shower heads and body jets.

    Now what I am wondering is...I currently have a 40 gallon water heater that is only a few years old, and my plumber is recommending that I install a new 50 gallon tank to just the new tub, and leave the 40gal for the rest of the house....would that make sence? or would it be better to plumb them in series? It just seems like the extra capacity of running them in series would make more sence...but I am not a plumber...so please help me figure this out....thank you
  • Brad White_9
    Brad White_9 Member Posts: 2,440
    If

    the existing house works (let's assume that it does and you have never run out of hot water) I would take that at face value, meaning you meet the demand but probably do not have much to spare. Properly done you should assess the fixture unit count of your house as it is, use diversity (Hunter's Curve). You will probably still find out that while you may have some surplus you probably do not have enough for a high-volume user like a hot tub.

    Add to that multiple heads of a spa shower (6 heads at 2.5 gpm =15 GPM. Off a 50-gallon tank that is a 3+ minute shower. Is that even enough time to play "drop the soap"? ;) )


    I would recommend piping in parallel not in series. Piped in series just takes the load off of the second heater, allows boosting of temperature and unless you put in a charging or recirculation loop, it will not add flow capacity. The common series pipe can only carry so much. Run two in parallel and your potential doubles.

    The question also becomes, what does the hot tub require? Not just the volume but the ability to heat it in a given amount of time? Will you drain it each time or heat it indirectly like a swimming pool? If the volume of the HT is 50 gallons do you have enough time to fill it before it cools? Pressure and piping sized adequately?

    Generally I concur with your plumber's recommendation that you add capacity but would also like to see them manifolded together (in parallel as stated) for back up one to the other and to absorb any surplus your existing heater now has. You may want to add storage capacity if the use is sporadic (large volume of heated water that can recover temperature over time).

    If you have a HW boiler, an indirect heater using all of the boiler capacity for a quick charge is another good idea. Especially if you do not use your tub in the coldest weather and have the capacity available. Just another thought.