Banging heat exchanger
Thanks, Randy, that did the trick. Took 3 tries but when he asked the lady if she heard it anymore, she said heard what?
  • John Mills_5
    John Mills_5 Member Posts: 952
    Scorched air
    11 year old Ducane oil furnace, heat exchanger and chamber gone from no maintenance. We cleaned everything, changed the exchanger which included new chamber, serviced the burner, firing at the lower of 2 firing rates. After running and just after the burner stops, the heat exchanger lets out a big bang, like a sledge hammer on an old drum. Tried another heat exchanger, same thing. Temp rise below maximum, stack temp a bit high to get 0 smoke, otherwise all looks fine. It has been suggested to yank the blower wire and let it cycle on limit a couple of times and that should stop the kaboom. Anybody heard of that remedy or heard of problems with new Ducane heat exchangers?
  • Timco
    Timco Member Posts: 3,040
    After burner shuts down, but while fan is still running? Mechanical boom (like a hammer hitting it)or like a small explosion boom (softer)? Gas valve not closing all the way when it shuts down, buildup ignites?
    Tim
    Just a guy running some pipes.
  • John Mills_5
    hammer
    Sounds like a big hammer smashing into the heat exchanger. It is an oil burner!
  • Ed_26
    Ed_26 Member Posts: 284
    hx noise
    Intertherm/nordyne once told me to find the approx. spot where the hx was flexing, & 'peen' it there. Maybe this will work for you. (if all else fails, use a bigger hammer)! Might be worth a try.
  • Randy Berg_2
    Randy Berg_2 Member Posts: 44
    Try this
    diable the blower motor, run the burner and let it cycle on high limit, let the unit cool on its own to ambient, reconnect the blower cycle and see what happens, if it still cannon's recycle again as stated above. Had this problem on a 3 millon btu oil fired air rotation unit, and their rep told me to try this, and it worked, hope this helps,