primary/secondary pumps (how to wire the primary pump)
I'm setting up a boiler with primary/ secondary piping. 3 zones. 2 radiant and an indirect. My question is how do i wire the circ on the primary loop to run whenever any of the secondary pumps come on? I'm using a taco sr504 expandible 4 zone switching relay with priority (If i can).
0
This discussion has been closed.
Categories
- 80.9K THE MAIN WALL
- 2.5K A-C, Heat Pumps & Refrigeration
- 36 Biomass
- 394 Carbon Monoxide Awareness
- 2.6K Controls
- 1.4K Domestic Hot Water
- 3.7K Gas Heating
- 101 Geothermal
- 130 Indoor-Air Quality
- 2.3K Oil Heating
- 30 Pipe Deterioration
- 565 Plumbing
- 4.2K Radiant Heating
- 333 Solar
- 12.1K Strictly Steam
- 36 Water Quality
- 7 Industry Classes
- 52 Job Opportunities
- 7 Recall Announcements
Comments
Could use the X-X End Switch on the 504 to run this pump. If you also need a dry-contact close for your boiler, then you could have a DPDT Relay energized by the X-X terminals on 504. one N/O contact is used to switch power to the pump and the other can provide a call for heat to a boiler or reset control.
Hope this helps. If not, call the guys at TACO, they are great!!
Mike
thanks, hydronicsmike