cfm
curiousity kills
Member Posts: 118
Any formula for converting btu heat to a cfm value?
Easy
CFM= Btuh/(1.08 x Delta T)
The "Delta T" is the difference between the delivery air temperature and the final room temperature (or the temperature difference across a heating or cooling coil)0 -
This only works on electric heat where BTU's are pretty much a given. Cfm must be measured in all other applications. This formula is more for calculating BTU's not CFM. Can be totally misleading and falsify the CFM.0 -
True
But for a quick estimate this will work for pretty well all heating applications. In cooling systems the issue to be considered is the latent load and the sensible load on a cooling coil and then we can play with the psychrometrics.0 -
CFM Is...
... to fans as GPM is to pumps. All fans really are, are low head pumps for moving air. The formula is valid for any heat source.
#/hr steam = CFM X 1.08 X delta-T/1,000.
The formula above for heating air with steam has been in the Spirax Sarco book "Hook-Ups" for decades. (And they likely got it from some other publication.) If you want BTU/hr instead of #/hr, just don't divide by 1,000. The souce of the BTUs is irrelevent.0
- 87K THE MAIN WALL
- 58 Biomass
- 113 Chimneys & Flues
- 109 Geothermal
- 161 Indoor-Air Quality
- 994 Plumbing
- 389 Solar
