O2 Barrier
Simply Rad_2
Member Posts: 171
I spoke to Viessmann and they said warranty is voided with barrier tubing. Tech said it would probably work but warranty is voided. HR Have you installed any stainless units you can use non barrier tubing.
Jeffrey
Jeffrey
O2 Barrier
I have a boiler replacement job coming up. The customer wants the best-mod/con wall hung unit first for efficienicy and second for space. The problem is that the orginal install used non-barrier tubing a Voyager heat source with cupernickle heat exhanger and Bronze pump. I talked to boiler manufacture and without O2 barrier there is no warranty. Now what are my options-a copper fin boiler?
Thanks Jeffrey0 -
Plenty of options
Use a flate plate heat exchanger to separate the boiler from the system.
Darin0 -
Flatplate is an option
Flatplate is definately an option but with a mod/con boiler you are losing efficiency. I guess in this situation you have to make due with what we have. A lesson to all USE barrier tubing!
Jeffrey0 -
A stainless boiler won't work?
With a stainles or bronze circ and one of the new expansion tanks that are coated?
hot rod
I don't want to rock
the Viessmann boat by any mean. Depending on the load and flow rates you may find a small 30 gallon indirect would work if you do want to go flat. plate hX that is
I do know several of the other stainless mod cons are now listed for DHW heating use, so obviously O2 is not a concern.
hot rod
Give me the mod/com
HR
Lately, I have only used the Vitodens so what mod/con manufatures are rated for DHW.
Thanks Jeffrey0 -
For sure
Munchkin is available in DHW versions. I've been told the Knight from Lochinvar is or will be very soon.
hot rod