Welcome! Here are the website rules, as well as some tips for using this forum.
Need to contact us? Visit https://heatinghelp.com/contact-us/.
Click here to Find a Contractor in your area.
richardson steam vent

DanHolohan
Member, Moderator, Administrator Posts: 16,653
one or more Gorton #2 vents. The Richardson had a huge hole.
Retired and loving it.
0
Comments
-
richardson vent
looking to replace a richardson vent have a system that had two someone replaced one with a main vent now house heats wrong my supplier has no idea what I am talking about0 -
Dan's right
But I'd replace both Richardson vents, since they were designed to hold vacuum whereas the Gortons are not. Vacuum worked great on coal but doesn't work well at all with an on-off oil or gas burner.
If the house heats unevenly, with radiators at the end of the system lagging those close to the boiler, adding vents to the ends of the steam mains will help.
To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"0
This discussion has been closed.
Categories
- All Categories
- 87.1K THE MAIN WALL
- 3.2K A-C, Heat Pumps & Refrigeration
- 58 Biomass
- 427 Carbon Monoxide Awareness
- 114 Chimneys & Flues
- 2.1K Domestic Hot Water
- 5.7K Gas Heating
- 110 Geothermal
- 161 Indoor-Air Quality
- 3.6K Oil Heating
- 71 Pipe Deterioration
- 999 Plumbing
- 6.3K Radiant Heating
- 392 Solar
- 15.4K Strictly Steam
- 3.4K Thermostats and Controls
- 55 Water Quality
- 46 Industry Classes
- 49 Job Opportunities
- 18 Recall Announcements