Grundfos Alpha circ

See why I'm both humbled and awestruck by the Dead Men? See why it's so easy to fu¢% up these amazing systems if you don't have a good understanding of how they worked to begin with? See why I'm eternally grateful to Dan Holohan and the wonderful people at Heating Help? 12 years ago I <I>probably</I> could have identified a hydronic system as either "hot water" or "steam"--if I spent some time observing things...

Modern hydronic engineers have it VERY easy by comparison!
«1

Comments

  • Mike T., Swampeast MO
    Mike T., Swampeast MO Member Posts: 6,928


    Wow! 6 watts typical consumption! Of course they're considering a systems with TRVs. I wonder if it could deal with on-off zone valves... Certainly looks too expensive for cost-effective zoning via pumps.

    Only available in Europe I suppose?


  • Rich Corcoran_36
    Rich Corcoran_36 Member Posts: 1
    The Alpha Pro

    combines cutting edge motor design and optimized hydraulics to reduce power consumption.

    The pumps operating principle lends itself well to application with zone valves.

    Stay tuned!

    RC
  • Brad White_56
    Brad White_56 Member Posts: 9
    I was hoping

    that this was (and maybe it is) a magnetic bearing motor. I saw a chiller by McQuay, 150 tons with two 75-ton compressors. The rotor/impeller was suspended by a magnetic field and took 2 amps of staring torque. No lube system, no "bearings" to wear. And when "off" the rotor parks itself. Magnetic bearings have been used for years on boomers (nuke subs) for their quiet running. And this chiller certainly was quiet.

    So my hope was that this technology made it down to the lowly circulator. I will have to check these out. Available when, where and at what cost?
  • Weezbo
    Weezbo Member Posts: 6,231
    the Hotel was a lot better off after i left *~/:)

    sorry....i was feeling kinda like doing some work so i installed all the pumps....oops:)
  • Brad White_9
    Brad White_9 Member Posts: 2,440
    That was you, Weezbo?

    I think I got there before you did. When I came back all of my circulator installations were red-tagged... trying to tell me something?

    :^)>
  • Ron Schroeder
    Ron Schroeder Member Posts: 995


    It looks like 6 watts to 25 watts, but that still beats normal pumps. Have you seen pump curves yet?
  • Mike T., Swampeast MO
    Mike T., Swampeast MO Member Posts: 6,928


    Hard to give a curve for a pump that varies itself...

    I COMPLETELY understood the statement of "no more noise from your TRVs".

    I used to have some noise in my TRVd system using a B&G 100. ZERO noise EVER after the variable-speed pump of the Vitodens.

    Pump in the Vitodens is called "weather responsive". This one seems to be responsive to the instantaneous load on the PROPORTIONALLY CONTROLLED system.


  • Cosmo_3
    Cosmo_3 Member Posts: 845


    I'm itchin for a chance to get one in my hands!!!

    Cosmo Valavanis
  • Weezbo
    Weezbo Member Posts: 6,231
    Hot Rod Told us not to,.....

    those pumps were working fine when i left :)

    the management put special tags on mine from the highest eff rating the EU has for energy saving equipment.

    i forget the DIN rating it's 2006 so it is kinda new.

    i know that is what management put on your circs too. :) it was a different mechanical room :)
  • DanHolohan
    DanHolohan Member, Moderator, Administrator Posts: 16,653
    I'm

    impressed!
    Retired and loving it.
  • S Ebels
    S Ebels Member Posts: 2,322
    What's different...............

    Having seen neither one, what's different between the Alpha and a VS Wilo?
  • Constantin
    Constantin Member Posts: 3,796
    What would make these pumps really interesting...

    ... for the US market is reliable, slow-acting zone valves. The integrated ΔP controller is tasty, the power consumption meter is very cool, the installation/substitution is easy. Yet, they are optimized for a control system (TRVs) that is not widespread in the USA.

    Another possible innovation is using these pumps as TRV-like devices, i.e. adjusting the flow with a PID controller to deliver BTUs as needed. That would allow for a very energy-efficient (and expensive!) constant circ system. Such a setup does not seem yet possible, as I see no mention of external control.

    For those of us who actually like reading I&O manuals, here is a link to the Alpha Pro Installation Instructions.
  • Dave Yates (PAH)
    Dave Yates (PAH) Member Posts: 2,162
    Grundfoss at ISH in 05

    Pics from the trade show floor at ISH - Germany

    Side-by-side live demo showing energy usage.

    To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"
  • Paul Pollets
    Paul Pollets Member Posts: 3,669
    10 year itch

    I saw these pumps demonstrated 10 years ago at ISH. Still, we wait for the goodies. The US market does not seem to support the costs of exporting the smart pumps.

    With Wilo about to distribute in the US, let's see if they're willing to put up the big bucks for the smart pump exports. BTW, are techs willing to pay $400-600. for the pumps?


    I think we're being teased....


    To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"
  • Weezbo
    Weezbo Member Posts: 6,231
    Thanks for the pic *~/:)

    that idea appeals to me so it may have to be incorperated somewherewhen... who makes those snazzy brass valves ?


    You Sure about that Brad :) '.....'~/:) just thinking out loud :)
  • Brad White_56
    Brad White_56 Member Posts: 9
    Brass Valves

    I think those are German, known as der Paddlewheelenflowmeterindevisen

    :)
  • Ron Schroeder
    Ron Schroeder Member Posts: 995


    Yes, But I would at least like to see a curve for full output and minimum drive.
  • heatboy
    heatboy Member Posts: 1,468
    I'm with you.

    While I embrace this as much as the next tech head, trying to sell this in a country where cheap-**** radiant is becoming the norm..............

    There was an error rendering this rich post.

  • S Ebels
    S Ebels Member Posts: 2,322
    HB and Paul

    I'm afraid it's going to be up to you and I to drag our customers out of the stone age, probably kicking and screaming as the go. This IS the flippin' US of A for cryin' out loud!! We're supposed to lead, not follow!!
  • heatboy
    heatboy Member Posts: 1,468
    I've been banging...

    .....the drum (and my head) slowly for almost 15 years, Steve. That is the entire reason I started this business. I must admit, though, the war has worn me down. I have actually installed my first open system this year (he says with his head hanging low). PAH, please forgive my sins.

    hb

    There was an error rendering this rich post.

  • S Ebels
    S Ebels Member Posts: 2,322
    Hang in there dude

    The day is coming soon ($4.00 fuel) when customers will think efficiency first and foremost. Those that didn't take the best possible system will be cursing themselves.
    Hind sight is ALWAYS 20/20!
    Off season price here is now $2.30/gl.
  • John Ketterman
    John Ketterman Member Posts: 187
    would they work in a gravity system?

    If I understand Constantin's post correctly, these pump controllers monitor the delta-p across the pump. How would that work in a converted gravity system, where the necessary delta-p is very small and so hard to detect and control? Would these pumps run flat out all the time, which would make them useless?
  • Brad White_57
    Brad White_57 Member Posts: 22
    I would tend to agree with you, J.

    Of course the boiler might suffer with any turndown, bypass or not.

    Now, if the same circulator could maintain a constant delta T, that would be something useful.

  • Constantin
    Constantin Member Posts: 3,796
    Well,

    If I read the manual correctly, they do have a number of different system settings, including for systems with very low flow resistance.

    I like what the pump can do in terms of a flat pump curve, etc. If only zone valves could be made as reliable as pumps, these kinds of pumps could offer a great leap forward in energy efficiency while handling microzoning and/or TRVs rather nicely..
  • Brad White_57
    Brad White_57 Member Posts: 22
    The danger if you will, of a flat pump curve

    is that a very slight pressure difference, point to point, will yield a very wide flow difference. Grab the flattest pump curve that you can find and take a look.

    Granted the most appropriate pump is the one that will do the specified duty with the least HP/Amps, but one still has to allow for "predicted" versus "actual/real life" installed conditions.

    But this is why I would hope such a circulator would also allow taking into account temperature factors including differentials. Pressure differentials in a pump system are incidental and an indirect way to control a system. This is heating; it is all ultimately about temperature, whether in the pipes or, the objective, in the space.

    I yield the floor :)
  • Weezbo
    Weezbo Member Posts: 6,231
    hb ,That must have hurt you to the very fiber of your being

    to do....think positive...now that you have had the experience the next wood boiler should be a breeze*~/:)
  • Plumb Bob
    Plumb Bob Member Posts: 97


    A good way to operate is to have a fixed flow rate in any branch whether other branches are open or not. For example, suppose there are two parallel radiators with open TRVs, say there is some appropriate flow rate. Then if one TRV closes, the pump should detect the change in head pressure and drop the flow rate to half, so that the open radiator has the same flow as before.

    How can this be achieved using intelligence at the pump, given a complex and unknown system of mismatched radiators, some in series and some parallel? Beats me.
  • Brad White_57
    Brad White_57 Member Posts: 22
    I think we are on the same page, J.

    We do agree that a fixed flow point is ideal (but only if temperatures can be adjusted to load is the underlying principle. One or the other, how to marry both.

    In my system here at home, TRV's mind the temperature at the room level while the circulator runs at a constant. A PRV (Honeywell D146) bypasses the excess around the circulator.

    (I disabled my "constant delta-T" experiment because it had too few variable and would lose it on morning warm-up.) Ever learning.

    I need to learn more about this circulator and it's application. The low power consumption indicates low turndown to me but is that consistent with space comfort and how? That is my question.

    How this appears to adapt does seem to be with maintaining a constant delta-P such that if a TRV closes, the pressure increase is detected and the RPM reduced to maintain the set delta-P. All things being equal the flow should be proportional all the way across each emitter but is done delivering overall less flow.

    Still, very interesting and adaptable technology.
  • Ron Schroeder
    Ron Schroeder Member Posts: 995


    Hi Brad,

    Why do you think that it has a low turndown? The power consumption can vary from 25 watts down to 6 watts.
  • Mike T., Swampeast MO
    Mike T., Swampeast MO Member Posts: 6,928


    If I'm reading and converting the pump curve in the installation manual that Constantin provided correctly, the largest model has a flow ability of about 13 gpm with very little head loss and operating at max speed.

    A "wide-open" gravity system is sized bass acwards with the lowest closest rads having the least restrictive flow path and the highest farthest the most restrictive. To get reasonable flow balance you have to move significantly more water under forced flow than moved under gravity. 13 gpm seems rather low for this purpose except in quite small gravity systems. If they would work I suspect they would require 100% speed and would NOT vary speed because any changes in differential pressure caused by adjusting hand valves would be exceptionally slight. TRVs on all radiators would be highly desirable--required flow will plummet and with the only head loss being provided by the TRVs themselves the circulator will be able to operate at quite low speed in most conditions.

    I suspect that the pressure transducer(s) are extremely sensitive and use that "restriction" adjustment to determine what magnitude of change to look for when adjusting speed--the less restrictive the smaller the pressure differential change required to make a speed adjustment. The more restrictive the greater the pressure change required to change speed--this would avoid excessive speed "seeking".
  • Ron Schroeder
    Ron Schroeder Member Posts: 995


    Found the curves for full output for the 3 models in the manual. Similar max flow as a Grundfos 15-58 or a Taco 007. But a lot of other data seems to be lacking in the manual.
  • Brad White_9
    Brad White_9 Member Posts: 2,440
    Hi Ron

    I call a 4:1 ratio a low turndown. Subjective determination of "low" aside, I think that is reasonable. Of course given the cube function of flow to HP/Watts, it may not translate into significant flow reduction. Do I gather your thinking correctly? Curious.
  • Brad White_9
    Brad White_9 Member Posts: 2,440
    Of wide open gravity systems...

    One point of information, Mike-

    I can see your point if the gravity system you cite is direct return (that is, the first radiators both supply and return are closest to the circulator and the furthest are the furthest). You would be correct in that the first served would take more in proportion than the downstream ones, although the effect would be minimal with larger pipe sizes and especially if they are extended at larger sizes.

    IOW: Say a 2-inch main carrying 5 gpm. Velocity is less than 0.5 FPS (yawn) and head loss is about 0.074 feet per 100 feet of pipe (double-yawn). Branch one drops off a gallon per minute. Your next segment carries 4 GPM at a velocity of less tha 0.4 FPS. Head loss drops by the square to 0.047 feet per 100 feet of pipe.... etc.

    Point being, each segment has minor head loss to begin with as you often pointed out. When the pipe size is extended as a trunk as often is the case, the losses drop exponentially. Sort of a regain situation (as recent reminded lessons in Bernoulli's Principles have demonstrated). Even if the pipe size is reduced, the losses are pretty teensy. (Scientific term, smaller than a mole.)

    So I think there is room to turn down even direct-return piped systems.

    Now, if the system is piped "reverse return" (first radiator served starts the return run) then all piping differentials are essentially equal anywhere in the system (assuming of course that the radiators or terminal units have equal pressure drops). Then I would respectfully submit that a gentle ramping up and down of the circulator would be rather beneficial and not default to a high speed especially.

    Random thoughts...

    Brad
  • Mike T., Swampeast MO
    Mike T., Swampeast MO Member Posts: 6,928


    Don't forget to think vertically as well as horizontally Brad. They tried to keep velocity in all of the vertical piping constant regardless of elevation. To do this piping to 2nd floor rads intentionally had about twice the restriction as those on the ground floor. On the third floor the difference becomes about three times. The absolute differences are tiny, but the relative differences are orders of magnitude... I believe that a wide-open gravity system with a circulator has to move water rapidly enough to produce enough head loss in the entire system to make make those differences tiny in the relative perspective as well. Sizing down the near-boiler piping will help, but I'm not sure if that alone is enough.

    Are reverse return gravity systems at all common? I kind of thought that overhead systems were the "upgrade" from standard two-pipe direct return.
  • Brad White_9
    Brad White_9 Member Posts: 2,440
    Rise and restriction

    I would submit that rise and restriction cancel each other out, Mike. Minute or not they compensate for one another.
    That was the intent, to thwart the upstairs from over-heating and to make it all quite even.

    That said, the motive force at whatever level should have a proportional result, that being even heating or at least even distribution of what is in the pipe. My "main" focus (pun partially intended) was just to illustrate the effect on the piping least effected by thermal bouyancy.

    The best systems I have seen have been reverse-return. Self balancing under power or under gravity influence. This included a 1910 mansion near me in Chestnut Hill, MA, fired by an H.B. Smith boiler. Indirect CI pin radiators with outside air to the nursery, big CI radiators (to which I applied TRV's). I do not recall if it was top-down, but I think it was. 6-inch piping and the returns collected around the perimeter and followed the basement walls (warming it thank you) for a final cooling effect to increase flow contrast. Very elegant.
  • Mike T., Swampeast MO
    Mike T., Swampeast MO Member Posts: 6,928


    would submit that rise and restriction cancel each other out, Mike.

    But it's the static pressure that does the job of lifting in a closed and pressurized system. Closing and pressurizing a gravity system are essential parts of the conversion process to forced flow. The circulator just circulates--up, down, over are irrelevant leaving only velocity and restriction.

    Not saying that this circulator family wouldn't work on a wide-open gravity system but I'm quite confident that if it did work that it would not vary its speed as there would be no feedback mechanism of sufficient magnitude for the pressure transducer(s).
  • Brad White_9
    Brad White_9 Member Posts: 2,440
    Sorry to break this too you, Mike... :)

    Static pressure does nothing for the dynamic side of things by definition. All static pressure does in a closed system is get the water to the top with sufficient surplus pressure to force the air out. It fills once, then is closed off.

    After that it is only the circulator and/or gravity forces that induces water to move. In forced systems we do our best to prohibit ghost flows with flow-check valves and in gravity systems we do our best to facilitate that effect.

    Static is just that, a body at rest. You are right about the circulator just moving the water (creating a dynamic force known as differential pressure) such that the water in the closed system acts like a ferris wheel.

    We do both agree that this differential pressure gradient will be very small, hence my leaning toward a temperature based control; speeding up or slowing down the circulator to maintain a constant delta-T for example. This would have the effect that upon reaching warm-up, the circulator would slow down and dribble in boiler water much like an injection loop circulator would. Not the same but as close an analogy as I could come up with in the moment.
  • Mike T., Swampeast MO
    Mike T., Swampeast MO Member Posts: 6,928


    Not too difficult but you have me confused Brad.

    I thought that the one thing that static pressure does affect on the dynamic side is that it makes elevation irrelevant to the circulator with it taking no more effort to move water above the circulator than beside or below it. Such has certainly been stated and written many times.

    Granted systems can be subject "ghost flow" via gravity but only when the circulator is off. Correct?

    Since I'm not going to remove my TRVs to test this (even opening them wide wouldn't be valid as they still have much more restriction than a big old hand valve) I can only imagine. While you could use delta-t to vary the circulator speed, lowering the speed would only exacerbate any balance problem caused by insufficient flow.

  • Brad White_9
    Brad White_9 Member Posts: 2,440
    Let's see....

    I guess I would say the only effect that static pressure has on the dynamic side, Mike, is that it cancels out any effect static lift might have if it were a truly open system, meaning one where the water actually had to be lifted against gravity as part of it's circuit. An open cooling tower would fall into this category.

    JUST occurred to me: When you use the term open gravity system, I took it to mean that it was "open" in terms of having little pressure drop. Is that what you meant?

    That aside, the principle is the same: So long as the system fill volume completes a circuit over the high point and down to the returns, the net "ferris wheel" effect is the same.

    "Ghost Flow" indeed is attributable to unwanted gravity flow in a forced system and when the circulator is off, correct.

    Lowering or raising the speed (flow) will not effect the balance in and of itself in any system.

    When a system is balanced (such as with fixed dampers in an air system or valves in a water system), the flow is "X" at a given head or inches of water in an air system. When you change the flow, the gradient changes across the system by the square of the flow. But the net effect is the same on any one branch because all started from the same point. If flow is reduced by half at the pump (or fan) and all other things remain equal, each branch will deliver half the original flow (or whatever proportion of the original it carried relative to the new sum total of the system).

    In a system with TRV's (or VAV boxes in an air system by analogy) there is a different dynamic afoot: Pressure. The system pressure differential changes, supply to return (or supply to atmosphere, again in an air system). The pump or fan then raises or lowers it's speed in response to the pressure change, to maintain it as a constant. Some more sophisticated systems we design actually RESET that starting pressure so as to not maintain an artificially high pressure differential. How's that?

    Hope this helps, Mike- As always I enjoy the discussion!

    Brad