Slinky Ground Loop Spacing Equation
Options
klaus
Member Posts: 183
Josh, We do 720'/ ton with slinkys, 50% overlap, 6 to 7 feet between loops. Depth depends on location but GENERALLY the deeper the better, we do a minimum of 4' - 5', 7' is better, (diminishing returns and all that) and of course depends on soil.
0
Comments
-
Doing my first slinky job.. All others up to this point have been straight horizontal loops.
Anybody know the spacing equation between coils? Need to calculate over-lap.
Thanks!!0 -
spacing
I run 36" diameter loops with a 50% overlap. Hope that is what you are looking for. Bryan0 -
I think it depends upon your soil structure...
Sand is different then wet clay.
No?
ME0 -
Assume soil structure, pipe length, and ditch length and depth are known. I believe the term for what I am looking for is called "Pitch."0
This discussion has been closed.
Categories
- All Categories
- 87.3K THE MAIN WALL
- 3.2K A-C, Heat Pumps & Refrigeration
- 61 Biomass
- 429 Carbon Monoxide Awareness
- 120 Chimneys & Flues
- 2.1K Domestic Hot Water
- 5.8K Gas Heating
- 115 Geothermal
- 166 Indoor-Air Quality
- 3.7K Oil Heating
- 77 Pipe Deterioration
- 1K Plumbing
- 6.5K Radiant Heating
- 395 Solar
- 15.7K Strictly Steam
- 3.4K Thermostats and Controls
- 56 Water Quality
- 51 Industry Classes
- 50 Job Opportunities
- 18 Recall Announcements