Copper Tube Exchanger Noise
Drew_2
Drew_2 Member Posts: 158
Received a call from a customer that asked, Why his copper tube heat exchanger, when used with antifreeze, was making poping noises?
As I remember from a previous thread, it had to do with flow rate? Can someone expand on this?
  • ALH_4
    ALH_4 Member Posts: 1,790
    copper hx
    > antifreeze, was making poping noises? As I
    Copper tube boilers have a very low water content, and generally the passages are relatively small. Adding glycol increases teh viscosity of the fluid and slows the flow. Slowly moving fluid through a heat exchanger will low fluid volume will cause the fluid to start boiling in localized areas, and cause all kinds of problems. These boilers must be piped primary/secondary, and sometimes require a larger pump on the primary loop. The manufacturer's installation manual should have the required information to correct this problem.
    What concentration of glycol is in the system?
  • ALH_4
    copper hx
    What brand/model boiler is it? What concentration of glycol is in the system?
  • S Ebels
    S Ebels Member Posts: 2,322
    Andrew is right
    Copper tube HX's transfer heat at an astounding rate. If the GPM going through the HX is to low, it basically spends too much time in there and soaks up too much heat. What you're more than likely hearing is some of the fluid flashing to steam. There can be other causes but that's the most likely. Copper tube boilers should almost always be piped primary secondary in order to ensure adequate flow through the HX.