Chimney liner sizing
Options
Rich_29
Member Posts: 20
The ibr is 64000 btu's. This is oil fired and will be the only appliance using a chimney. Thanks
0
Comments
-
Chimney liner sizing
I'm having a Buderus G115-21 boiler installed in the basement of my ranch (approx. 17ft. tall chimney).
What diameter flue liner will be necessary to properly vent this boiler. All responses much appreciated. Rich.0 -
Do not know
Model #'s How many BTU's and do you have a gas water heater(BTU rating) useing the same flue? I assume boiler is gas fired.Best Wishes J.Lockard0 -
NFPA-31 P. 48 & 49.
.60 GPH/ 88% Steady State (300* gr stack temp)/ 20' vertical stack/ 4' lateral/ 5" listed metal liner. 86% (370* gr stack temp)/ 4' or 10' lateral/ 5" liner.0 -
Ron
Thank you. Rich0