what about boiler insulation???
Options
Casinojunkie
Member Posts: 36
I have an old American Standard, American Severn No. C33 Series 1BJ2 boiler. I would like to add fiberglass bat insulation to the sides and top of this boiler. I have removed one side panel of the boiler and there is room to add 3 1/2" on the side and top. Can I use fiberglass for this insulation or not?
All help appreciated.
All help appreciated.
0
Comments
-
Be very careful...
... one of my colleagues burned his lab down thinking that all fiberglass insulation is the same. It is not.
Home fiberglass insulation uses starch as a binder and starts burning at around 500°F. Not a problem under normal conditions, but if the boiler dry-fires...
... so if you place new fiberglass in there, be sure to buy appliance-rated stuff (i.e. for use up to 1000°F). McMaster Carr sells "High-Temp. Fiberglass Blankets" halfway down page 3306, which I used to good effect with an oven that I had to re-wrap due to mouse infestation.
For even higher temperatures, the Silica blankets come to mind. We used a lot of them at my old workplace and they're good up to 2000°F.0
This discussion has been closed.
Categories
- All Categories
- 87.4K THE MAIN WALL
- 3.2K A-C, Heat Pumps & Refrigeration
- 61 Biomass
- 429 Carbon Monoxide Awareness
- 120 Chimneys & Flues
- 2.1K Domestic Hot Water
- 5.8K Gas Heating
- 115 Geothermal
- 167 Indoor-Air Quality
- 3.7K Oil Heating
- 77 Pipe Deterioration
- 1K Plumbing
- 6.5K Radiant Heating
- 395 Solar
- 15.7K Strictly Steam
- 3.4K Thermostats and Controls
- 56 Water Quality
- 51 Industry Classes
- 50 Job Opportunities
- 18 Recall Announcements