Prepping boilers for the summer?
Big Ed
Member Posts: 1,117
Punch the tubes and fill the boiler to the supply pipe with water...
What should I do to prep two 1 million btu steam boilers to sit through the summer?
Thanks
Matt0 -
What is "punch the tubes"?
Thanks0 -
Brush out and vacuum the flue passages in the unit. Soot that is left in a cold boiler will absorb moisture and become very corrosive.0 -
It may also be helpful
to fire the boiler to almost the boiling point to drive off any excess oxygen, or add an O2 scavenger chemical for the duration. Then flush before you start up again in the fall.
Other technique: Purge and charge the drained boiler with dry nitrogen to about 5 psig.0
