vent lengths of mod con boilers
Options

rumn8r
Member Posts: 104
for the info.
0
Comments
-
vent lengths of mod con boilers
Can someone explain why vent length recommendations vary so much (20 ft for Vitodens to 100 ft for Buderus and others)? What compromises are made by extending the maximum vent length?0 -
It boils down to this:
The fan.
The controls that are dependent on that fan, to safely function.
The engineering capabilities of the manufacturer, given the restraints the marketing (a/k/a price "points")/bean counters demand.
And finally, what the contractor/installer is willing to settle for.
The fact that "the greatest boiler maker on earth" cannot and will not make their "premier" boiler vent over 20' may provide insight as to just how the relationship between engineering and marketing inter-act.
Simply stated: "Great marketing will overcome mediocre engineering every time; typically in a ratio of 2:1"
Bottom line, find a manufacturer who makes a product that meets your vent length requirement, and fawgettabowt Vitodens for this one. Make sure whatever you install, also has threads that are NPT, not "straight-cut."
Let us know how you make out, please.0 -
vent lengths of mod con boilers
I'm not sure I understand. Are you saying that modcons allow longer vent lengths are better engineered and that there are no trade-offs to allow the greater length?0 -
So Ken...
I am real curious. Just wondering, if you were the King of All Things Hydronic, and you could make the "Ultimate Condensing Appliance", how would YOU market it?
Would you wait for the world to beat a path to your door, or would you go out and promote it?
Would it sell itself, or would there be a need for a marketing and sales program?
Don't you have a Viessmann in your new home?
What exactly is it that Viessmann has done to get your goat?
Where exactly did the quote you use, "Great marketing will overcome mediocre engineering every time; typically in a ratio of 2:1" come from? Is that Kenism or is it attributed to someone else?
I've seen their products, and I've seen most of the other products that are their competition, and in my opinion, their (Viessmann) products ARE the best that I've seen, and in the opinion of their competiton, their products are far superior. I sell EVERYTHING on the market, from V to M. Their product is not in every persons price range, but neither is Mercedes Benz...
What gives, why all the negativity towards what is obviously preceived by thier competition and other casual observers as this worlds top of the line boiler?
Please keep it civil. I really truly want to know your opinion, without the vehemence.
By the way, their Vitodens boiler can be vented in longer considerations... You have to read the manual and install it exactly as it says, but it is not as limited as you have stated...
Their concentric venting limitation is based on sound mechanical engineering, not marketing as you have implied.
ME0 -
Viessmann options
You knew I'd be here didn't you Ken.
Here's the Vitodens venting options:
http://www.viessmann.ca/web/canada/ca_publish.nsf/AttachmentsByTitle/docVitodens-Venting-ii.pdf/$file/5285-268-Vitodens-Venting-ii.pdf
Viessmann's coaxial Polypropylene ventign system is restricted to a maximum length in order to ensure their "Balanced Flue" design works as it's supposed to. This design will compensate for almost any atmospheric conditions short of a hurricane. It also compensates to an extent for variations in gas/burner pressure. It's an excellent system and worth considering relocation of your boiler if needed. There's more to it than what I have described here and I have the tech paper saved on my computer somewhere. If I can find it, I'll post it also.
In light of the fact that we've had some discussion here regarding the suitablilty of PVC as a venting material, it's interesting to note that the inner/exhaust pipe is polypropylene instead of PVC. IIRC, Buderus uses a similar system on the GB as sold in Europe. I think there is something to be said for the use of the Polypro instead of PVC. The only other option Viessmann endorses for extended vent lengths is AL29-4C stainless.
My experience with Viessmann has shown that marketing is not even on the radar when the issues of proper function and safety could be compromised in any way.0 -
coaxial Polypropylene
I beleive that coaxial Polypropylene is the pipe of the future here in the states. The discussions of not using PVC for venting has good arguments but when we look at the coaxial Polypropylene with a max vent temperature of 120c what can compare and give us the peace of mind on safety?0 -
That's exactly...
what I'm saying!0 -
Vent length for Vitodens
I have a couple of questions about venting the Vitodens that Steve or others might be able to answer. The Viessmann sales rep has not been able to get an answer from Viessmann. The venting manual says that the maximum vent length for side-wall vents is 20' for all models while the maximum vertical vent length for the 11-44 is 33'. Although it includes diagrams for vertical venting that show that part of the 33' can be horizontal, it does not include guidlines for how much can be horizontal. One possibility for me is to go through the wall it will be mounted on with a ~9' horizontal run to a 90° upturn and go through heated garage space and through the roof an additional 16' for a total of 25'. Is this possible?
Another possiblility for me is to have a 10' run against the outside of the house, through a large overhang and out through the roof. Will this cause freezing of the condensate? Will insulation help?0 -
For you Mark?
And, despite the fact that you should already know the answers to all your questions, Lord knows I have posted the reasons I feel as I do enough times to never have to repeat them again... If for some reason beyond my comprehension, you missed them all, I will respond yet again.
And Mark, telling someone to "keep it civil" and "without the vehemence" - before they even respond, is like putting a red cape in front of a bull and suggesting he not pay attention to the person waving the cape in his face, tormenting the daylights out of him. If you really want an answer, you're going to have to consider to whom you request it. One more thing. You have certainly shown yourself to be more than a tad obtuse on occassion. Let's not get too high up on the soap box, Laddie.
To respond, if you are truly curious (not merely grandstanding for the already breain-washed "Viessmann uber alles" faction that is part of an openly verticle marketing scheme), I will do so for the umpteenth time, for you - point by point.
1) I respect the heck out of the way HTP/Munchkin markets their stuff. Given that all companies have finite financial resources, I love the way they run their company and the products they make. Whatever their marketing vs. engineering budgets are, I honestly can't recall ever seeing an ad or cadre of "verticle marketeers" or "'A'-list installers" having to rally the wagons to support them here - or anywhere else for that matter. Knowing the praise I see about them is NOT from a bunch of "sanctioned and on the list" self-promoting and self-serving "partners" eliminates the hype and gets me into a warm and honest dialogue with the company and product - WITHOUT ALL THE MARKETING DISTORTIONS.
2) Asking if I would wait for "them to beat a path to my door or, go out and promote it," is like asking, "How many times a week do you beat your wife"? I would do what most do. Do market research and get soft commitments, BEFORE PRODUCING ANYTHING! Then, attempt to exploit those who seemed willing to commit prior to production and get them to evaluate the product in beta testing. If the product delivers as promised, little marketing is required. The product (not unlike Buderus, W/M, HTP/Munchkin, Burnham, Peerless, et al) require no "captive, installer, referal based verticle marketing scheme" (like Viessmann, Lenox and EK) and compete by virtue of mechanical excellence, coupled with very competitive price points; which, benefit everyone involved - not just the manufacturer.
3) No, I don't have a Viessmann in my own home. They didn't not know how to make a condensing, oil-fired boiler, in the BTU range my heat-load calls for. Nor did they know how to make a simple NPT connecting point for supply and return, for "our" country.
4) Viessmann has succeeded in displaying incredible marketing skills by verticle marketing schemes, something I choose not to partake in. They are not competitively priced, poorly adapted to our standards and are no more durable or efficienct than comperable models that are superior in basic functionality for the purposes of heating an American home. Unlike a few who would advocate them over anything on the planet, "snobbery" (the very basis of their marketing scheme) never impressed me as a sound basis for praise. Truly great engineering however, does.
5) "Great marketing will overcome mediocre engineering every time; typically in a ratio of 2:1" is a "Kenism." I coined it. Perhaps at "Wetstock-I"? Feel free to use it as you feel the need. Yes, I coined it.
6) If the V is "top of the line" in your mind, just remember, it is only your mind. Some of us, find even better products at better prices. The word "value" is the key word. The major play on "vanity" and terms like "the best" are so overused and so thin on substance, I am amazed that the legendery marketers at Viessmann still use the by now trite phrasing, they still use. "Best" by what standard? The Volvo is one-third the price of a Benz, yet has a better safety rating! But the Benz will do 0-60 in 5 seconds, the Volvo in 7. (I'm making a point, the data may be totally bogus). We always seem to make claims of superiority based on what THE MANUFACTURER CLAIMS, NOT THE REALITY OF EACH JOBS SPECIFIC NEEDS (or the customer's system and financial needs)!
7) Mark, I know all too well the Vitodens venting constraints. I am also aware of what it's like to work with their "customer support" group; especially when you are NOT one of their "exclusive members-only" installers. Their installation guides are among the worst I have ever read.
8) Suggesting their "concentric venting limitation" is BASED on sound mechanical engineering is like saying the improper threads they continue to export to the U.S. is also based on sound engineering. You want to market to the U.S. market? Consider the fact that a typical American house has a basement, and two floors above, and a roof. Also consider "good engineering" would suggest NOT using already heat laden house air for combusion, but rather un-conditioned cool air from outside; MANDATING concentric venting. Since a typical North American house would require a MINIMUM concentric vent at ~4' for the basement wall mount to the first floor joists, then 8 more feet for the first floor run, then 8 more feet for the second floor, and finally SOME of the roof line to exit; and we've EXCEEDED any typical install for all of N. America! Great engineering? Exporting an overpriced boiler that will not work in the typical home it would be installed in?
Okay, we could always side vent, or limit sales to ranch houses only. Nothing anyone would mind in a 1.5 million dollar "jumbo," watching a giant plume of condensate obliterate the knock-dead view you thought you had, looking out at the Aspen ski slope...
A 20' concentric limit on the best engineered/greatest boiler on earth"
I'm not buyin' it; any of it(:-(
Now, is that civil enough for you sweetheart?0 -
Read the post above.
Does it not say what I have said over and over again?
"rumn8r" writes, "The Viessmann sales rep has not been able to get an answer from Viessmann." Blame the rep? Of course. Blame the confusing euro-speak installation instructions? Of course.
Better yet, blame me!
I suspect, Viessmann INTENTIONALLY uses vague and contradictory installation (especially with regard to venting) instructions, because it goes to their agenda of verticle marketing, and allows interpreted variations of those vagueries to be used against "non-member" installaters, if the customer has pre-bought Viessmann by virtue of the hyper-marketing they deploy.
It was PRECISELY that experience thet our client endured, (and we as installers did as well) in our most recent Viessmann debacle/install. Yet one more reason to use anything but a Viessmann boiler in our own experience.0 -
Best Engineered.....
Ken:
You make some good points about the differences in engineering standards.
Here is my take on the situation as a homeowner and an engineer who did his own research on the different mod/con options that were available to me. While I am a "genrealist" as an engineer (I've dealt with many things from structural to fiber optics as a "plant support" engineer) - my expertise is heat exchanger design and longevity - ranging from millions of Lb/hr steam boilers to single coil seal or bearing coolers (and my job title is HX Testing Engineer). I had no knowldege of the distribuition or marketing stratagies of any of the companies.
The heart and sole of a boiler is the HX and the burner; all the rest are repairable or changable accessories. The available control system is then what allows the boiler to operate efficiently.
From my perspective the Vitodens HX is the best designed HX being offered in the mod/con world. The burner is top of the line as well.
From a control perspective - the Vitodens seemed to be the only boiler which came with a very advanced control system as part of the boiler; and had the necessary optional parts to adapt it to a variety of situations. No other boiler that I looked at was even close. Yes, I am aware that you can buy "other" non-boiler company control systems to run some of the other boilers.
I also believe that their concentric vent system really is great for several reasons.
Of course, you are right in that their are engineering issues: I spotted five things that I consider engineering limitations with the Vitodens.
1) The lack of a smaller unit: Why not a 3-12, and a 4.5 - 18. Cost of the unit is not much of an issue here - just being able to get better efficiencies at lower loads is the issue.
2) The installed pump on the 6-24 and the 8-32. This may work for a new heating system where you are designing from scratch; but is woefully inadequate for retrofit applications (such as my monoflo T system). Why in the world do they not have a pump that has the ability to move say 10 GPM at 10 Ft of head? Then they could vary the speed to match the system. This I suspect would work for most systems without the need for a LLH or additional pumps (except where each zone needs its own pump).
3) The vent system limit. Why 20 ft for a horizonatal concentric application?
4) The use of European threads for their export machines.
5) The lack of a USB port to read the computer and monitor boiler performance (or other standard computer port: Firewire - or even 9 pin).
As to why these exist:
Marketing and engineering choices in designing the boilers.
I think that Viessmann (and many others) is really missing the marketing boat on item 1 (mod/con sizes). They should have smaller mod/cons available (yes I am aware of the Munchkin, but am not impressed with it from a design standpoint).
Item 2 (pump capability) has me scratching my head - I just don't understand their choice on the capabilities of the built in pump. Because of that I needed a LLH, a secondary pump, and an expansion module in the power supply. Perhaps $1000 in parts and additional installation cost as well. Makes no sense to me. Also, some new installations could use that kind of capability as well.
Item 3 (Vent system limit). This is clearly an engineering/marketing choice. How big a fan did you design in - what is the market applications. I think they made a reasonable choice here. It covers most new and a number of retrofit applications. Very few products are designed to cover the entire market - most products are designed to cover a segment of the market. I feel the choice was reasonable - dispite the fact that I had to relocate my boiler in order to install it with the concentric vent - due to the vent length limit.
Item 4 (Threads). Viessmann seems to have adopted the idea that they are producing one boiler that the sell - in exactly the same configuration - arround the world; and then sell adapters (fittings and power supply) for applications in other countries. North American pipe threads (or even a metric equivelent tapered thread) are used in many places in the world. I presonally believe that they might do better by producing several versions of the boiler (and hot water tanks) that differ only in the fittings for at least the most common sized boilers and hot water tanks. US standard voltages are also common in the Americas (and some other countries) so that I believe they could also have a Vitodens export controls module that worked without a power supply adapter (just plug into the wall).
Item 5 (computer monitoring). I'm surprised that the boiler mfr's have not adopted this. I've had lower cost medical equipment for almost a decade that allows setting and monitoring via computer. There would be many advantages to having this.
All that being said: I chose the Vitodens for my house due to its better engineering and better controls. No, I do not think any US manufacturer had a comparable product. I expect the Vitodens HX and Burner assembly to outlast the others on the market. The rest, will have to be repaired or replaced as needed.
In the end, all products have design choices in them. That does not make them either the worst or the best products. It does limit your options with that product.
I also agree that those design choices can be agravating at times.
Perry0 -
Market limitations of the Vitodens 6-24 & 8-32
As a follow-up:
How much has the limited pump installed on the Vitodens 6-24 & 8-32 limited the use of the boiler. A larger pump that might increase the product cost by a hundred dollars or two would make the boiler usable in many applications that now requre a Low Loss Header, secondary pump, and power supply expansion board + the cost of installation of those items. That is quite costly.
My guess is that they could potentially double, tripple, or even more the market penetration if they had a larger pump as part of the boiler.
In my case my system would have worked with a pump that could put out about 8 GPM at 8 Ft head. That's not a very large pump. But I think a pump capable of 10 GPM at 10 ft head would have a lot more use - and still not be a very big pump.
The existing pump may be idealy designed for the boiler; why not chose a pump that would work for most systems by itself? Why increase the cost of an install?
Perry0 -
Clarification for U rumn8r
Here's what I know about Vitodens venting.
As the manual says, when venting horizontally the max developed length, including 45 and/or 90* ells is 20 ft.
For vents with a vertical termination the max developed length is 33'. Of that 33', the max horizontal length cannot exceed 50% of the total developed length.
So lets use you scenario as an example: As I read your post you would have 2 90* ells, 9' of horizontal run and 16' of vertical including the termination above the roof.
The easiest way to noodle that out is to start with the total max length (33') then deduct the equivalent length for your ells (2=3' equiv.) so you have 30' left to deal with. Deduct the horizontal length (9'= 21') remembering you must have less horizontal length than vertical, and finally deduct the vertical (16'= 5') So you have a margin of 5' left that you could use if you had to. Your plan will work given the parameters as I understand you.
Just remember the 33' total equivalent length and the vertical rise must exceed the horizontal length. Each 45 is worth 1' and each 90 is worth 1.6' IIRC You should be good to go.0 -
Perry,
Loved your honest response and appraisel. I suggest Viessmann never supposed you would hook their boiler up directly to a heating system. It is implied by almost all mod-cons I am aware of that a P/S pumping array is "standard."
Given the relatively high Cv ratings of the boilers in THAT category, P/S IS the fundamental design premise.
As an ASHRAE member, I recall the topic of one meeting where the caveat that "proper engineering" suggests "over" engineering is as poor a choice as "under."
In America, we cater to conditions of homes ranging from 200 years old to ultra modern commerciual spaces. Leaving the boiler controls "off" the product in many cases is better engineering! That's because we apply boilers in a far more "custom" application than the Viessmann product line affords!
I propose the Viessmann is over-engineered on a few points, and grossly underengineered in others. I suggest over, or under, engineered products are inferior. The former because over-engineering wastes money and generally makes things more complicated than necessary, and under-engineering result in quality compromises.
Unlike most, I want my cake, and to eat it. I find most American boilers, be they 1 HP mod-cons or 500 HP Clever Brooks to be more aligned with "spot on" engineering far more frequently than anything out of europe. Buderus being the lone excpetion out of Europe, so far.0 -
Thanks. The info I was missing is that "the max horizontal length cannot exceed 50% of the total developed length". Where is that in the Technical Data Manual or in the Venting Manual?0 -
Not in mine either
And it should be in the venting manual. (hint to Viessmann)
I got that info from the Viessmann rep a year or so ago when I ran into the same situation on a job. It's also covered in their training classes IIRC.0 -
Ken - I've been thinking on this
and I have to largly disagree with your contention that the Vitodens is mostly under engineered with a few things overengineered.
I will agree witht the concept that in general over-engineering is not good (a waste of money), and underengineering is just plain bad because the thing does not work properely or does not last.
In Europe they are dealing with buildings much older than the US - and a huge variety of heating systems as well (although forced air was never as big in europe as the US).
The problem I have with the concept of overengineering is that the concept really only applies to short lived items. Keep in mind my background is power plants where we run equipment for many decades - and the key equipment is designed to run for 50 or more years (with proper care and maintenance). I have never seen an "over-engineered" product for long life products. I have seen lots of underengineered "cheaper" things that don't cut it.
A home heating boiler should last decades. Thus, I don't see how you can overengineer it.
The Vitodens control system is adequate to handle most of the situations that occur in a home and small commercial radiant heating system. For very complicated systems you bypass it with an external controller.
I don't think it is over-engineered at all; and I think it offers a great value to many customers by not having to buy and install another box.
I believe that the reason that most US boiler companies don't want to go there - with a good built in control system - is that they want short product life cycles and don't plan on stocking spare parts very long. Afterall - aftermarket control systems can always be replaced.
The problem is that I believe you will find a number of boilers not installed with the kind of controls that would make them most efficient - because just a basic control system is the cheapest to buy and install.
The biggest issue in the US is the number of heating contractors who only want to do it "the old way" - and a boiler with integrated controls is not the old way (even if they are highly flexible); nor is using mod/cons, nor is pumping away, etc.
I am disapointed in the built in circulating pump, and the requirments to use a Low Loss Header and secondary circulating pump - and I suspect you are right that Viessmann never intended the boiler to be hooked directly to many heating systems.
Other than that I think the Vitodens is a highly engineered product that can be used in a variety of applications (and was designed to be used in a variety of applications). I don't see any overengineering that is not appropriate for something that should last decades.
The fittings - thats more of an inconvience and disapointment - marketing has chosen not to serve the needs of this market. It's not an engineering issue as US threaded fittings is only a choice with no significant cost or function consequence.
The biggest think affecting the cost right now is the value of the dollar compared to the euro (the exchange rate). That has a tendency to change.
As you say, you wish to have your cake and eat it too... In the real world it dosn't work that way in the long run.
I suspect within a few years the concentric venting will become standard for boilers.
I also think that the Aluminim heat exchangers of many of the US mod/con boilers are going to fail in a significant number. Please note that I have looked at a few of the warranties - and the Mfr will not be responsible for anything. Afterall - the customer did not maintain proper water chemistry.... (like why don't you design a HX that doesn't need constant water chemistry control?) I call this just plain bad engineering.
But like you say, Marketing will overcome poor engineering most of the time.
Perry0 -
Hear Hear!
The Vitodens is a neat piece of engineering and the compromises that were made reflect the markets it's most often found in. The EU has 400MM inhabitants and is 97%+ hydronic heated. The US has 300MM inhabitants, and 7% hydronic heating systems.
As a rule, product engineering usually attempts to cover the largest markets, not the niches. EU systems, by and large, have TRVs on every radiator, very few circulators, and a lot of house mass to play with (stone homes combined with standing/hanging rads). Thus, these systems can play with wide ΔTs and low flow.
US homes, for the most part, are wooden construction, relatively low mass, and some of the emitter choices are very low mass as well (baseboard, hydro-air, etc.) Thus, flow rates needs can be much higher to deliver the required number of BTUs as the house temperature roller-coasters up and down. In a high mass-home, the rise and fall in temperature will be much more gradual.
The variable-speed pump built into some Vitodens' reflects the energy-efficiency aims of Viessmann, IMO. When a US lab compared the Vitodens to its competition, it had a 8x lower power consumption annually than the likes of an Ultra, for example. Using a variable-speed circulator is a large part of that equation.
That circulator (and the required power supply) undoubtedly add $$$ to the cost of a Vitodens. Having more circulators to choose from would be nice, but it could also defeat the ΔT the controller seems to be looking for. Never mind the legal raminifications of trying to get a boiler with multiple pump options certified via the myriad of federal, state, and local agencies.
I'm with you though on the point that the Vitodens is beautifully engineered to do what it is supposed to. Plus, once you pipe a bypass as Brad suggests (back into the supply header upstream of the pump, not the return), the extra pumps needed to run US systems on the other side of a LLH will no longer have a negative impact on the energy efficiency of the boiler.
As for the vents, these boilers reflect the trend in the EU to put these sorts of boilers under the roof in new construction. Who says a boiler has to be in the cellar, particularly if it runs on gas?0 -
Do you ever seem to have some issues with Viessmann Ken... Perhaps some are well-grounded, but others seem based on personal prejudice.
Nothing at all unusual at multi-level marketing and protected distribution in the US. I deal with such ALL THE TIME in my "real" lines of business (small retail and club-style bars). As my familiarity with different wholesalers/manufacturers and sales volume have increased, I'm offered more and more incentives--you'd proably call them "perks": nice catered meals, open bar parties, airfare reimbursements, not to mention what I consider "better" service from sales reps and greater overall discounts. If you want to talk "protection", you probably can't imagine beer and liquor. Here in MO (as in much of the country) you have ZERO choice from whom you buy and everyone pays the same thing and receives the same very nominal discounts for relatively small quantities, e.g. unbroken cases. This causes Wal-Mart fits, and while they're doing everything in their power for a change to laws to allow them to pay less than anyone else, the wholesalers (and Anheuser Bush) have managed to keep the changes from happening.
Marketing and selling in the US is quite different than in Germany. Even Wal Mart sold their German operations as they could not compete on price! They actually offered too much service! (I guess German general merchandise stores are rather like Aldi grocery stores here in the US.)
With so little market share in the US, manufacturers of ALL boilers cannot market direct-to-consumer like furnace mfgrs. They're forced to market to supply houses and installers. Guess what? Both are even more demanding than consumers when it comes to service and "perks". "Hey. I've been using/selling X for years. No problems. What are you gonna' give me to change? Besides, I've been burned by 'high-tech' before, are you gonna' spoon feed me through my first installs? Your group training sessions are nice, but you know I'd really prefer one-on-one help 'cause you're forcing me to change my ways."
You may consider the Vitodens both over- and under-engineered, but I simply cannot agree. You may think the bean counters had much to do with its design, but it sure looks to me like the engineers were given virtual free reign with the bean counters saying, "If you're gonna' start from scratch and make the ultimate, it HAS to be modular with as much as possible shared by all in the line. You can do anything except create a stocking nightmare for distributors."
When comparing the Vitodens to any other boiler (including mod-cons), it seems more like comparing a steam locomotive to a diesel-electric. They perform the same function, but the way they do it is completely different.
When designing the Vitodens, Viessmann seems to have started with a blank slate with the intention of completely re-thinking how a boiler works in a heating system, with the goal to make that boiler the most efficient, least polluting and most reliable and completely system-integrated space heating device ever produced.
Given those ideals can you at all blame them for considering the most prevalent type of system (TRVs and rads of some sort) in the wealthiest area of the world (western Europe) where hydronics overwhelmingly dominate?
They succeeded so well in their goals that I believe the Vitodens to be the only boiler available that can match output to load on a virtually moment-by-moment basis. Wouldn't that be your goal if you were trying to produce the ultimate boiler?
Are there limitations? Of course! While I suspect most come from physical laws and limitations of current manufacturing/materials technology, I'm sure that there are a few instances where complexity and cost had to be considered.
With a little forethought, even the limitations are not terribly restrictive. Vertical venting with the boiler in the basement of any rational new American home is no problem. Similarly the flow ability of the single VS circulator on some models really no problem if you design for such and use TRVs. Even with radiant floors it's possible to use just the single circulator if you design carefully and use FHVs and a highly conductive method of heat transfer to the panel.
0 -
Does it not
trouble you that the "best engineered boiler in the world," can't even get the basic installation instructions down properly?
Doesn't part of the basic equation of good engineering begin with good documentation?
I rest my case!0 -
Connie, your points are intersting but...
Viessmann came here to our shores to market to us here. If you're going to market a boiler to the U.S., would it not be wise to understand the needs of the client/market place before doing so?
No one "made" or invited them to come here. They came to make money. And, at the prices they charge, they certainly do make money.
The number of people involved in the marketing and shipping costs is where most of the overhead/expense is expended, certainly NOT in engineering! Having seen the production line first hand, it sure as hell ain't in the quality of the employees that make the stuff!
If an American maker had the budget Viessmann has for staff and marketing, they too could play the "snob appeal based on price" alone game.
I also question your data that implies the EU claims 97% hydronics, then infer high quality manufacturer's somehow share substantially in that percentage. I can honestly say, in the five or more visits to Germany, Austria, and Ireland (where two train stations had NO HEAT AT ALL!) the equipment was hydronic, but crap, capable of maybe 70% s.s. efficiency, implying AFUE's of ~ 65%. Hardly anything to brag about. In addition, I saw not one Viessmann installed!
0 -
I found the "basic installation instructions" both comprehensive and quite adequate. With regards to venting I found it rather obvious that horizontal and vertical were different.
With horizontal, it was "keep it short". With vertical it was "keep it vertical as much as possible up to 33' equivalent length".
My only real beef with the instructions and technical data (at least provided in the US) is that systems with a single, directly connected heating circuit (e.g. no low-loss header) were described only by exclusion. I still consider such to be the TRUE method envisioned by the Vitodens engineers with everything else an efficiency concession (no matter how slight) to their original vision.
BTW, I could have used vertical venting in my application in a big old 2 1/2 story home with the boiler in the basement. Problem was that I'd already used some otherwise "wasted" space next to the chimney in my master suite closet to house a little cube refrigerator and tiny high-faucet sink to fill the gallon water jug.0 -
Ken
Do you have any idea how many pages of "instruction" are shipped with a Vitodens? Probably not, or you wouldn't be spouting the nonsense you are.
I respect your knowledge and experience on a lot of things hydronic. Your experience is wide and long and deep but to hear you speak the way you do regarding Viessmann/anything European makes me wonder about your objectivity.0 -
Ken
Ahhh.... I studied the manuals for a half dozen boilers (and still have them) when looking at boiler options for my house. Some I downloaded from the internet - others I emailed the companies and they sent me one (with their sales literature). I even got Viessman to mail me stuff in addition to what I downloaded from their site (and I have the general access password to get to all the manuals and technical information).
There is no comparison - the Vitodens manuals are in a class by themselves. To say that they miss a tiny bit here and there... is an indication of where Viessmann did wrong -- compared to what you consider the "better and right engineered" US boilers is laughable... Based on your previous arguments I know that you believe that The American boiler Companies supply only what the American market needs - and only what the American heating installer needs. Obviously, not only the top notch professionals (many represented on this site) but the average ones and even the lower ones can easily install those American boilers correctly - with often scant instructions and technical information. Heck, these boilers are so easy to install that half the questions asked or situations on this site (over and over again) - must be the work of shills... Either that or you read a different forum than I do.
Are you implying that the great Instruction and Technical manuals from Viessmann - in your opinion - another example of Viessmann "over" engineering their product?
Perry0 -
Perry,
I doubt there is any point in debating the good vs. evil aspects of Viessmann with Ken. He's convinced they're only as good as their marketing, etc. and pointing out the obvious flaws in his arguments gets you nowhere. For example, he has yet to prove his claims about the marketing vs. engineering budgets at Viessmann despite being repeatedly invited to do so.
If Viessmann has figured out a better way to make money in the heating business, then I suppose other manufacturers would rather follow suit than continue to earn the same 'paltry' returns they always have. Hence the Opus from Burnham and other attempts to bring out premium appliances, private-labeling EU products, etc. Sometimes it works, sometimes it doesn't. Bottom line is: everyone in business tries to make money.
Your observation re: US boiler companies is quite astute and explains perhaps why so few US boilers are being sold in the EU and so many (comparatively) EU boilers and components are sold in the US.0 -
Is a vertical run outside the house allowed?0 -
With a Vitodens? NO!!!!!!!! NEVER!!!!! EVER!!!!!0 -
Didn't think so. What if it was boxed and insulated?0 -
NO!
If you have to shift horizontally do it INSIDE--NOT OUTSIDE!!!
If you're in a non-arctic climate I suppose you could put an exterior horizontal in an extremely well insulated box-type sleeve for a distance within the limits and still using the Viessmann horizontal termination and cover.0 -
Chimney
You can vent either material in an abandoned chimney.0 -
OK, just remember... (for Kens sake)
To clear the air on the "Marketing Question:" Everyone keep in mind that that I purchased my Vitodens 200 without ever having seen a Viessmann Advertisement (other than the literature they sent me when I requested some information - similar to what several other companies sent me).
I had to go find the information on the boiler (some on the Wall helped with that); I had to find information on other boilers, etc. I didn't even start the search looking for a mod/con. I started researching cast iron boilers and decided first that I liked the Crown and a Burnham (Spelling?). I literally spent days on the web, and then hours looking through all the manuals once I got them.
I didn't see a Viessmann boiler at the local home shows either.
The engineering - and completness of the package (including manuals) is what sold me (even when it cost a lot more to install).
I had to find and then call the regional rep as well. There are no local installers here with the product.
So I have seen nothing to indicate a big marketing push.
I did see very good engineering - even if I don't understand why they sized the circ pump how they did.
On the other hand - I do agree with Ken's statement that good marketing overcomes bad engineering. I think that a lot of US companies depend on that.
I sure hope I am wrong about Aluminum boilers... unfortunately the research I did indicates that the Alumimum block boilers has a record of disintegrating in Europe and leaving a hard to clean out Al based slime in the pipe and radiators when water chemistry is not proper on a mixed metal system (I also found that you can buy Aluminum radiators in Europe now to go with a AL boiler so you don't have a metal mismatch. Not sure what they do for fittings in that case, but PEX would be a no brainer for piping to avoid the galvanic issues).
Perry0 -
So how do you vent through uninsulated attic space?0 -
Heh!
I didn't get a visit from the local Viessmann voodoo doctor either to sell me on the benefits of Ms. Vitola... like you, I went through the literature out there, asked some questions here, and then made my selection. In the end, it was a choice between the Buderus G115, the Opus O1, and the Viessmann Vitola because I wanted to stay with oil heat.
At the time, heat loss calculations, my installer, and the OTT folk convinced me not to go with the Monitor FCX. The Opus O1 was too new and unproven, IMO, even though Burnham has a stellar reputation (four or five months after the decision-day, the Opus experiment was discontinued by Burnham). Given the BOP in the house, the Viessmann Vitola was a more logical choice than the Buderus G115, since it could handle lower return water temperatures.
After making the equipment selections, I elected to take a couple of courses at Viessmann. I paid the fees, took the courses, and was treated like every other professional around the table. As a result, I have a deeper understanding for the products in my home and an appreciation for the engineering approach that Viessmann takes to designing their product. I also got to meet a couple of Wallies, which was a treat.
Viessmann is quite vertically integrated compared to many US mod-con boiler manufacturers. For the Vitodens, they make their own HX, designed the burner, etc. Currently, many mod-cons sold by US companies are private-labeled EU product that was adapted to run on 115VAC. With few notable exceptions (Burnham and S/F come to mind) the rest are made of mostly foreign parts that are assembled on US manufacturing lines.
Considering that labor makes up about 10% of the total cost for most appliances that I have torn down, I wonder how a product whose manufacturing cost is made up by more than 50% foreign parts can be truly declared as "made in USA". Not that the boiler industry is alone in this regard - the WSJ recently ran an article where a Toyota had more domestic content than the Ford Mustang.
So its quite possible that the US boiler industry has spent more money on marketing their mod-cons than the engineering to get them off the ground. Considering that SG&A usually runs 3x or more than R&D in most mature companies, it would not be a big surprise.
Your points re: Al blocks in heating systems interest me... Could you be kind enough to point out a resource or two re: Al slime in heating systems?0 -
How in THE heck did I miss your response to me...
I suspect a glitch in The Wall, because I've been awaiting your response with great anticipation.
Ken, arguing with you is like wrestling with a pig is a cesspool. The more I wrestle, the more you like it, and in the end, REGARDLESS of ANY ONES perception, in YOUR mind you are the winner. So I'm not going to waste a whole lot of time responding other than clarifying some of your misgivings and disinformation.
I must admit, you made me go to the dictionary when you threw out the use of the term "obtuse". I could really care less about your use of the term as it pertains to me, and I suspect that you meant the "bluntness" of some of my comments, and I may be blunt to some people regarding certain commonly questioned applications, like "pumping away", but I can guarantee with great certainty that even homeowners who have been hit in the face with my "bluntness", who have applied my "bluntness" have ended up with the positive results I guaranteed.
Your opinion of me does not carry much weight with me, nor does your alledged handle of the English language. Keep your $2.00 words to your self...
To the point(s).
1. HTP has had their share of "issues", and I guarantee you that they will have more, some more serious than others. As for people not having to clamor to protect them, as you have stated, BUNK, there is a thread currently running where I personally jumped in to give them credit where credit is due, and I have and will continue to do it for ALL of the manufacturers whose products I use who provide me with the support I deserve. You are standing out in left field on this one pal. By yourself. As for an "A" list, yes Virginia, there is an "A" list, and I am on it because I took the time to go get certified as a "Vision 1" factory approved contractor.
2. Viessmann brought their product to our market LONG after is was conceived and proven in THEIR field. I don't see you dragging any of the other alleged "Eurocrap" manufacturers through the mud for using the straight BSP threads. You telling me that FRENCH boiler you have in your home has tapered threads on it just to keep people like you who don't know how to deal with a straight threads happy? And what is all this crap about vertiCAL marketing? I've never heard of the term and do not see any relevance between the product and how it is marketed. I don't read the marketing literature, the retail customer does.
3. I stand corrrected, you have a FRENCH Eurocrap (your words) boiler (Sorry Pete, no offense meant) in your house. Now THERE'S a country with whom I'd place a lot of trust, engineering or otherwise...
4. Again, your use of the term vertiCAL marketing. Irrelevant to me, the installing technician, important to the consumer. If the consumer is not sold on the product, they will not buy. They are obviusly buying this product, i.e. Perry and many others who have the ability to see and comprehend a quality product. Not everyone on the market is some poor person looking for the cheapest way to get some "heat" as you imply. Again, they brought their existing product to OUR market, and said "here it is, and here is how is must be installed". You would prefer that they bring their product to the market and say "Install it however you like, we don't care how it performs in the field, or if people are exposed to dangerous conditions?" Not me pal. It's not right for every application or every customer. Apply with caution, where appropriate.
The few who would advocate them over any other product are obviously dedicated to the product. I've been to their factory training, and I do not sell them exclusively. I am not brain washed as you imply. I was impressed with their product, their training and facilites, and most of all with their product. It is far and away SUPERIOR to any other product on the market. If you refuse to see that, or can't comprehend, that is your problem, not theirs. They are doing as good a job (marketing, training, product development etc) as they can. As for price point, it is what it is, and the company stands behind profitability, unlike some American companies who are just barely making it by on single digit profit margins, with no room to breath, and absolutley no money to be able to market their products they way they would LIKE to market them, because of their perception of what the "market will bear" and what the American contractor is willing to pay.
The American boiler market is based on competetive pricing and not reasonable profitability, and that is the reason it is in the unenviable postion it is of having to export Eurpean technology in order to compete on the efficiency forefront. There are obvioulsy a FEW exceptions to that statement, but they are FEW and FAR between... Prove otherwise.
5. I thought so. Don't hold your breath waiting for me to use it. I don't believe it has any application in this situation, and if all consumers are so easily misled, then we are ALL a bunch of dupes. I don't think you are giving enough credit to the public at large.
6. No comment, other than to say your mind is obviously closed to the Viessmann product line, and so be it. They don't need you to survive, but they also don't need you out there bad mouthing them for all the wrong reasons.
7. I don't know where you come off with this "members only " attitude. Viessmannis available on the open market in no less than 4 or 5 different wholesale supply houses here in the Colorado area, and you don't have to be carrying a card to get inside. I have found Viessmanns support to be EXCELLENT, and I'm not some card carying member as you so wrongly put it. Are there issues with their installation manual? Of course there are. There are issues with EVERY freaking manufacturers installation manuals I've ever read. And any time you are attempting to make a lietral translation between foreign languages, there will be barriers, but at least Viessmann addresses them instead of ignoring them in hopes that the right thing gets done.
8. Obviously, it is not the right product for you. You have to THINK about the application PRIOR to applying the product. Not go blindily into the situation and attempt to shoe horn something into place to satisfy someones need for "heat".
All in all, I would say your discourse was generally civil. You are obviously set in your ways, and so be it. But I think it is unfair to the many good folks behind Viessmann, or any other product for that matter, for you to sit behind your keyboard and harrass just to satisfy your ego and need to use quips which you came up with.
Ken, you and I have known each other for a LONG time. We've broken bread and drank wine together, but when you get on a tirade on your keyboard, you are a COMPLETELY different person, and not one that is the same that I've spent time with in a social setting.
It is your perrogative to do as you please, I just ask that you stop for a second and think about what impact your words might have on the targets of your verbage.
Think before you type. And please don't refer to me as sweetheart. I'm not your type.
Enough pig wrestling. Gotta go wrestle with some Christmas lights.
ME0 -
Mike,
The evidence of posters here suggests you may be one of the few who find the instructions even "marginally adequate."
Your opinion and the facts are at odds. Which seems to dominate the mindset of those who are so enamored of the marketing hype the company has so successfully engaged.
Think what you must. I am hardly alone on this issue, however...0 -
Had I known
you you would be challenged by the word "obtuse," I would have saved you $2.00.
I am not ashamed of waiving the flag. And Mark; that would be the American flag, just for the record.
Had Viessmann made a condensing oil boiler in te BTU range necessary for my load, they would have had a horse in the race.
The boiler I used to heat my home was engineered so well, there is no thread issue; merely four 3/4" pairs/sets of high and low temp female copper connections. I stuck a piece of 3/4" M copper tube in each, and took off from there.
At least this euro maker actually demonstrated some semblence of competent engineering, unlike the brand you seem so transfixed by!
I know. I know. Now you'll have to look up another $2.00 word.
0 -
The number of pages in
the installation manual is interesting...
WHAT THOSE WORDS SAY, IS EVERYTHING!
Printing 40 pages of poorly written text is nothing to brag about. It is a purely a waste of trees.0 -
Plus...
... there are a number of beautiful technical aids at our disposal these days... phones, fax machines, digital cameras, and computers! So many ways to get in touch with technical support, paint a picture, get some straight answers.
As for the completeness of manuals, remember all the trouble that Ron Jr. went through for installing a drop header on a steam boiler? How explicit does a manual have to be in its assumptions about the knowledge of the installer/inspector?0 -
I still consider you...
a friend.
To each his own, my friend.
ME0 -
AL Boiler HX degradation in Europe & US Mfr's Limitations
Constantin:
Months ago when researching boiler options I spend a good number of hours researching Aluminium block HX's in Boilers. What I found was interesting - and enough to tell me that I did not want to retrofit one into my existing system.
Because I did not answer all the questions I had - I planned on someday finishing the research - and due to other items of more importance at the time - did not post what I had found.
To find information on the European experience where they have been used for about 15 years I constructed a search to look over there - and then paged through 20, 30, 40 (or so) google pages to find comments and information on the experience in Europe with Aluminium block HXs - and then intended to construct searches off of the results, but only did a few of those searches.
Unfortunately I do not have a list of all the sites I visited. But here is one that I can recover - a review by a commercial boiler installer (plumber) in England of a SS mod/con (Keston 25).
www.dooyoo.co.uk/archive-house-garden/keston-celsius-25-modulating-domestic-condensing-boiler/433028/
Because websites have a tendency to disapear I am attaching the complete review, and note the following statement:
"Keston have wisely chosen stainless steel as the material for the boiler heat exchanger. I always advise customers to insist on this material when choosing a condensing boiler. Aluminium heat exchangers have a tendency to rot away with time and leave a slimy mess for the service engineer. Keston guarantee the heat exchanger for five years."
I also found several other post (or reviews) from boiler installers or service technitions that reflect the degradation of Aluminium block HXs and the mess they leave in the system. I cannot recover those post at this time and am not going to try to reconstruct my search.
I do note that it seems that warrantee practices in Europe (and for boilers) in general are much different than common US practice - so don't be put off by the 5 year warrantee statement.
However, the impression I was left with after doing my search... Installation of Aluminum block HXs on existing systems with iron (or steel) piping and radiation was where most of the problems occured. Aluminium radiators were available and recommended for new installations where Aluminium block boilers were going to be used. I was curious if Aluminium fittings were also available such that you could construct a system purely from Aluminium (or galvanically compatible materials) - which would eliminate one of the most obvous problems with using Aluminium and Iron or steel in the same system (and I'm not sure how Aluminium and Copper react). However, I did not get that far in my searching.
Aluminium block boilers only represented about 2% of the 2004 and 2005 European market and were not growing in market share. Cast Iron or steel boilers dominate (my memory was 70-80%), with SS boilers next. My memory is also that SS boilers were growing in market share.
When I saw the web literature for the first Aluminium boiler I jotted down 4 or 5 engineering questions or issues that I had on the material being used in a boiler. While 1 or 2 of them were answered by further research - the others were not; and the "degrading and sliming up the system" comments from Europe largly fall into line with some of my initial questions.
If you look at the limitations that the US Manufactures have imposed you can see that they are aware of the issue (but are not overtly telling people). My general take after reading up on the issue this summer was that to ensure an Aluminium block HX would work:
First, you have test the system and chemically treat as necessary (anticorrosin additives seem to be highly recommended).
Second, you have to annually test the system and then chemically treat to get the system to where it needs to be chemically.
Third, they exclude warranty coverage for any Aluminium HX degradation caused by the system not maintained with proper chemistry. An example:
Wells McLain Ultra 80 warranty:
"This warranty does not cover boilers operated with combustion air contaminated externally by chemical vapors or with improper fuel additives, or with water/ system conditions which may have caused heat exchanger failure."
It seems that other companies have adopted some kind of wording about "chemistry" into their warranties when talking about Aluminum block HX's (although they may have just added it into their general warrantee). Companies that offer lifetime warranties for cast iron only offer limited life warranties for Aluminium.
So my question is: How many people or heating contractors are actually going to properely test and chemically treat their boiler water up front when the boiler is new. Only the best. Many heating contractors in the US will not do it (they've never had to do that in the past).
How many people are going to properely annually test and adjust their system chemistry.... My guess is only a few. Even the best heating contractors - those who understand and are willing to do it - are limited by people who do not want to pay an annual service call.
How many boiler companies will pay for a degraded Aluminium block HX after it degrads due to improper system chemisty... (seeing how every company that I have checked on specifically exclude this from their warrantee). Zip.
Who is going to pay to clean up a "slimed up" system?
Lets look at a common example of Aluminium in a HX. An automotive radiator. Why do you need a routing cooling system flush and refill (every several years). Not because the antifreeze goes bad - but because the additives (anti-corrosion) get used up and go bad. Ever see a radiator or Aluminium head that has run for several years beyond the life of the additives. This is the biggest cause for sale of new radiators... Heads usually are OK only because they have more material to loose; but I know of cases where the head had to be replaced as well.
So that is what I know.
This portion of this thread started largly becaus Ken has a saying that marketing overcomes poor engineering. I agree.
If you hear that an Aluminium HX transfers heat better than SS (steel, or Cast Iron). That is marketing, not engineering. It is true that for the same thickness that Aluminium transmits heat faster than the other materials. The problem with the way the statment has been used is the cast aluminium block HXs are much thicker - as such, a thin SS based tubed HX transferes heat better.
If you hear that Aluminium is highly corrosion resistant. That is marketing, not engineering. Only in the right environment is an Aluminium corrosion resistant. Given the warnings about improper chemistry and oxygen from make-up water and non-barriered PEX, and the experiences in Europe where some of these have been installed long enough for the problems to start to appear... you've got to wonder how they can claim this with a straight face. That is marketing.
There is only one reason that Aluminium block HXs are being used. They are cheaper to Mfr than SS ones. round SS tubes have limits on heat transfer due to geometry, and odd shaped tubes cost more to Mfr yet. A very nice thin SS casting would outpreform the Aluminium block HXs - but would be expensive to produce because you can only get the thinness and details needed with a lost wax process casting.
Now my guess is that an Aluminium block boiler installed on a new system that does not have any Iron in it (and are Aluminium fittings available) will probably do well.
I doubt that they have a long life as a retrofit into an iron piped and radiator system - unless a lot of chemical monitoring or treatment is done.
Perry0
This discussion has been closed.
Categories
- All Categories
- 87K THE MAIN WALL
- 3.2K A-C, Heat Pumps & Refrigeration
- 57 Biomass
- 425 Carbon Monoxide Awareness
- 115 Chimneys & Flues
- 2.1K Domestic Hot Water
- 5.7K Gas Heating
- 107 Geothermal
- 160 Indoor-Air Quality
- 3.6K Oil Heating
- 70 Pipe Deterioration
- 983 Plumbing
- 6.3K Radiant Heating
- 389 Solar
- 15.4K Strictly Steam
- 3.4K Thermostats and Controls
- 54 Water Quality
- 44 Industry Classes
- 48 Job Opportunities
- 18 Recall Announcements