New Mod-Con Question

Options
Latest? entry to the field. Manual allows DIRECT connection without primary/secondary.

Mfgr and model please...

Comments

  • Mitch_4
    Mitch_4 Member Posts: 955
    I believe

    you are talking about the New Utica UB95M 200
  • Boilerpro_5
    Boilerpro_5 Member Posts: 407
    That one has been around awhile...

    in a non modulating form and without need from P/S. The Prestige also allows this piping arrangement since the built in pump has a fair amount of extra capcity since the head drop across the boiler is ratherlow.

    Boilerpro
  • Mike T., Swampeast MO
    Mike T., Swampeast MO Member Posts: 6,928


    The Utica UB95M is the one I was thinking of.

    The control and operations manual at the website still seems to have a Fahrenheit/Celsius problem where it explains outdoor reset. Wording states that the reset curve goes "flat" at outdoor temps below 32°F—e.g. boiler always fires to the max (parameter 4) setting. Graph shows this happening at 0°F. BIG difference!
  • Mike T., Swampeast MO
    Mike T., Swampeast MO Member Posts: 6,928


    Thanks Boilerpro. Am still looking for on-line manuals for the Prestige.