Heat source approval
Jim_65
Jim_65 Member Posts: 184
Does any one know of a high efficiency boiler that is approved to use in a non-barrier tubing system?
I have been told that the Triangle Tube Prestige does but I am having trouble finding that printed in the manual.
Thank you in advance!
  • Uni R_2
    Uni R_2 Member Posts: 589
    All of them!
    Provided that you have a heat exchanger in between the non barrier part of the system and the boiler. I would think that this would be the only sane way to connect them.
  • Jim_65
    Thank
    you for your response.
    I completely understand what you are implying but that is not my goal.
    If I used a heat exchanger to separate the systems would require a rather large heat exchanger based on the load and higher temperatures that would take the boiler out of condensing mode.
    This system is multi temperature and I am trying to utilize non-ferrous components for the system as a whole.
    BTW - I may not be sane in my approach. :)
  • Jim
    Most of the stainless steel boilers would most likely be OK but I don't know of any one that says so.
    Your bigger problem is the rest of the system - think Extrol, etc.
  • Jim_65
    Exactly
    These folks have an annual visit to replace the expansion tank and can not figure out why.
    But I believe we can eliminate this with a potable expansion tank. (Therm-X-trol)
    Thank you for your input.
  • ALH_4
    ALH_4 Member Posts: 1,790
    no hx
    I don't think you'll find any manufacturer that will warranty an installation without a heat exchanger. Would the heat exchanger be quite large? A thousand bucks or less seems like a decent price to not have to worry about it.
    -Andrew
  • Jim_65
    HX
    The cost of the heat exchanger is not an issue. Although I do agree with you about not having to worry about it would be priceless.
    This project is going to be tricky enough to adequately fit everything in the space we have been provided. With the additional scoop, circs, exp tanks, etc. that we need for the HX system could potentially eliminate access for future service of the system as a whole.
    Thank you Andrew.
  • Rely_2
    Rely_2 Member Posts: 61
    pool heat
    take a look at a W/M pool heater as the exchanger model #wmph 200 or 400 the delta T is 45 degrees and is small and compact good luck