kevin coppinger_4
Member Posts: 2,124
have said... not a fan of piping it this way...I would only pipe as 2 seperate fills and combine the vents...you can do the crossover the same at the bottom...it will put a lot less strain on the tanks when filling...the other (traditional) way is not wrong...just not as good.kpc
<A HREF="http://www.heatinghelp.com/getListed.cfm?id=323&Step=30">To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"</A>
<A HREF="http://www.heatinghelp.com/getListed.cfm?id=323&Step=30">To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"</A>
0
Comments
-
Oil Tanks
Hello everyone.
Can you direct me to a reference source for the correct way to pipe and vent two tandem oil tanks?
Thank you and best regards, Arlene
Arlene Puentes
www.octoberhome.com
To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"0 -
Ok
So,
When tank #1 is full the oil starts to fill tank #2 from the connection at the top of the two tanks. So that a fill guage in tank #2 that indicates 3/4 full means that tank #1 is full and tank #2 is 3/4 full. Is this right?
Thank you very much for your help.
Arlene
www.octoberhome.com
To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"0 -
They should both be at 3/4 full.
After filling the tanks, the level in the two tanks will equalize through the oil line/crossover on the bottom of the tanks. So if the guage reads 3/4, then that should be the level in both tanks.0 -
As
long as both supply valves are open and not clogged,which is common in older tanks
To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"0 -
Roth...
Take a look at Roth-USA Oil Tanks...
www.roth-usa.com
These tanks are in my option the very best in quality, price and saftey...
Seriously look before you buy...
0 -
I pipe oil tanks with a 114 BK line in , a 2 inch cross over , and a 114 vent. That is a acceptable method per NFPA 31. Also using 114 for the fill and vent allow me to bring less fittings and tools......
A number of people don't like that method and pipe like what is mentioned , but be careful doing it that way.
Per NFPA 31 , If you use two fill lines the vents can not be tied together until they are above the fill points.
Dave in NH
0 -
Thank you
very much for your replies.
Time to look at NFPA 31 again!
best regards, Arlene
To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"0
This discussion has been closed.
Categories
- All Categories
- 87.4K THE MAIN WALL
- 3.2K A-C, Heat Pumps & Refrigeration
- 61 Biomass
- 429 Carbon Monoxide Awareness
- 120 Chimneys & Flues
- 2.1K Domestic Hot Water
- 5.8K Gas Heating
- 115 Geothermal
- 167 Indoor-Air Quality
- 3.7K Oil Heating
- 77 Pipe Deterioration
- 1K Plumbing
- 6.5K Radiant Heating
- 395 Solar
- 15.7K Strictly Steam
- 3.4K Thermostats and Controls
- 56 Water Quality
- 51 Industry Classes
- 50 Job Opportunities
- 18 Recall Announcements