Welcome! Here are the website rules, as well as some tips for using this forum.
Need to contact us? Visit https://heatinghelp.com/contact-us/.
Click here to Find a Contractor in your area.
If our community has helped you, please consider making a contribution to support this website. Thanks!
Sizing Indirect
Options
JimmyJam
Member Posts: 78
How would I properly size an indirect h20 htr for the following:
1 - double head shower (standard heads)
1 - 5' standard tub
1 - standard shower head
1 - clothes washer
5 - wash basins
I would be using a GB142-60 for the heating system.
Thanks!
1 - double head shower (standard heads)
1 - 5' standard tub
1 - standard shower head
1 - clothes washer
5 - wash basins
I would be using a GB142-60 for the heating system.
Thanks!
0
Comments
-
Indirect
The twin shower head looks like your largest load. 5gpm water draw . The boiler is a beast ,did you do a heat loss calulation ?Any way if you take a 10 min shower at 5gpm you need a 50 gallon storage which would also fill the tub. The 60 would recharge the tank in 15min or less.0
This discussion has been closed.
Categories
- All Categories
- 87.6K THE MAIN WALL
- 3.3K A-C, Heat Pumps & Refrigeration
- 59 Biomass
- 430 Carbon Monoxide Awareness
- 124 Chimneys & Flues
- 2.2K Domestic Hot Water
- 5.9K Gas Heating
- 120 Geothermal
- 169 Indoor-Air Quality
- 3.8K Oil Heating
- 78 Pipe Deterioration
- 1K Plumbing
- 6.6K Radiant Heating
- 396 Solar
- 16K Strictly Steam
- 3.5K Thermostats and Controls
- 56 Water Quality
- 51 Industry Classes
- 51 Job Opportunities
- 18 Recall Announcements