gravity system
Steamhead (in transit)
Member Posts: 6,688
I've seen many of these in Baltimore. When dual (combined feeder and safety) valves came out someone got the dim-bulb idea they could handle the pressure by alternately feeding and then releasing water using the dual valve. This saved the cost of a tank. Trouble is, this wears the valves out, and if one of them gets stuck it could cause a leak or even an explosion.
Whenever I see one of these I sell the owner on a diaphragm expansion tank and a new dual valve and backflow preventer.
gravity system
is it possible to have a gravity system without an exspansion tank a closed system0 -
sure .
pipe goes up the chimney does a u'ie and drops back to the basement floor any expansion runs down the drain.:)0 -
Saw one in the St. Louis area. No circulator, no expansion tank. Was told they relied on the small amount of air trapped in the top of each radiator.0 -
I guess the gypo contractor is not a new phenomenon after all.
I always thought that all the Dead Guys were good guys. Did you really have to disabuse me of that idea?0 -
Yes and no. Some early gravity systems used an OPEN expansion tank in the attic, so it was an "open" system with an expansion tank.0 -
yes but
a closed system utilizing the little air pockets in the radiator tops? give me a break. The expansion tank in the attic is legitimate. Air pockets are not.0
- 120 Geothermal
