Sizing boiler for oversized system piping w/ iron radiators
I'm drawing a blank on where to look up the percentage to add for various situations on hot water retrofit boilers with oversized mains.
I'd like to be able to confirm some things....
Noel
  • I'm looking for charts or guides published
    Noel
  • bob young
    bob young Member Posts: 2,177
    ask Dan
    years ago i had a similar problem & the gents at wallace ennis helped me out.
  • If you find, please share. Have looked deeply myself.
    My best guess is to add nothing unless the basement or crawlspace has exceptionally high infiltration or exposure.
    Heat loss calcs usually have the basement/crawlspace at a lower temp than actual. The heat liberated down there only reduces loss in the space above. No air pressurization problems with hydronics, so the situation tends to cancel itself out.
  • Here you go, Mike
    http://www.heatinghelp.com/pdfs/143.pdf
    Right here in the library.
    Thanks, Dan.
    Noel
  • Mike T., Swampeast MO
    Mike T., Swampeast MO Member Posts: 6,928
    Noel
    Link doesn't seem to work. What's the section and title.
    I need to revisit "The Library" MUCH has been added...
  • older hot water heating systems
    the third one down is an old I C S course from 1907.
    Boiler sizing and derating for lower temperatures are in there. I'm still reading up on it.
    Noel
  • Perfect timing
    This agrees with what I've been discovering this week.
    Thanks, Dan. I really can use this info on a real situation this week.
    http://www.pmengineer.com/CDA/ArticleInformation/features/BNP__Features__Item/0,2732,161636,00.html
    Noel