Can I replace an old steam radiator with a baseboard radiator
RJ_2
RJ_2 Member Posts: 1
I just recently brought a unit in an older building, I want to change the steam radiator to a baseboard radiator. Wanted to know if this is possible to do? The boiler for the building is located in the basement, and the temparature is not control by the individual units.
    Steamhead Member Posts: 18,211
    You'd almost certainly need
    to run a return line from the baseboard, if this is not a two-pipe system. This probably wouldn't be practical in your situation. Do your radiators have two pipes connected to them, or just one?
    Why not try to find a radiator that has the same capacity but is shaped differently, maybe lower, longer and skinnier?
    You can control your radiators with thermostatic radiator valves. The proper type to use depends on the type of system in your building.
    Consulting
  • Ken_8
    Ken_8 Member Posts: 1,640
    Regardless of whether the radiator is
    one or two-pipe form, it can be replaced by fin-tube style baseboard heat.
    Pitch, overall length and venting are hyper critical, but it is possible and although much easier with a two pipe radiator change out, is also possible with a one pipe steam rad.
    The larger the rad removed, the more "challenging" the switch. The issue is amount and speed of the entering steam vs. the amount and speed of the returning condensate. By increasing the pipe diameter of the baseboard finned pipe, venting slowly with a smaller vent - and gentle pitch of the element, surprisingly large BTU output can be achieved without banging or spitting.