Sizing of TXV.
Empire_2
Member Posts: 2,340
Is it straight 10 ton or staged? 5/5 7.5 /3.0? Usually a larger air handler will have 2 circuits with 2 5 ton condensers or something along thoes lines.
Mike T.
Mike T.
Sizing of TXV
Hay Guy's.Just curious,on a 10 ton{120,000}Air Cond.system,should you use a 7.5 ton TXV or a 10 ton TXV0 -
TXV sizing
Hi Mike T.This is one compressor,with unloaders,and one TXV.0 -
OK,....10 ton valve is correct Because.....
When running at full load the compressor is pumping out its 10 ton capability. Depending on which unloader you have (either hot gas bypass or suction cut off) As the load in the building drops the unloaders (Unload) the compressors total capacity by a certain percentage. Let's say it's 25% of the total capacity. You now are running at only 75% of total capacity. The 10 ton valve will still be fed and will act more like a large dehumidifier to bring down the remaining load in the building.
Mike T.0 -
Techman
What type of compressor are you working on? Does it have the brass unloaders on the cylinder head? If you need adjustment manuals, I have them and would gladly forward them so you have them in your library.
Mike T.0 -
TXV sizing
Mike T. The compressor is a Carrier #06D,with unloaders on the heads[2] .Thanks, I would like to recieve the literature that you have.But, how?Regular or e-mail?0 -
Techman
I will post it here, but give me your E-Mail and I will send it that way to. I am not a pro when it comes to this stuff but I will try. M2112@adelphia.net Drop me a line and I will return the compressed folder on the capacity control.
Mike T.0 -
Mike T.
Just finished downloading unloader info,THANKS,Hope to return the favor someday.I kneeded help to download the stuff, I'm just learning this computer.0 -
Yea,...Computers are not my strong side.
Sometimes I think that I am the only one that has a hard time with this thing. I learn new things every day so I hope you could read it ;-) That info is nice to have. I find myself pulling it out just to adjust the unloaders from time to time. I save everything for situations like this. Good Luck Techman. Any Q: drop a line and if I can help I will.
Mike T.0 -
TXV Sizing-R-22 A.C.
Back to the original question!The Sizing of the TXV is based on the pressure drop across the valve.All r-22 TXV's are sized and labled based on 100psi press drop across the valve so a 10 ton TXV is 10.2 tons at the rating of 100 psi pressure drop across the valve.At 200psi pressure drop across the valve, the valve is now rated for 14.4 tons. The 7.5ton TXV at 100psi pressure drop is rated for7.4tons, but at 200psi press drop the 7.5ton TXV is rated for 10.5 tons. On a 72-75* day, the suction press will be 60-65psig and the hi side will be 175-185psig,that is a 120 press drop across the valve.On a 90-95* day,the suction press will be65-75psig and the hi side will be250-300psig .that is a180-215 press drop across the valve.The principle is just like an oil nozzle,raise the pump press from 100psi to 150psi and the oil output goes up.0 -
TXV
The expansion valve has only 1 Job, to control super heat. I think in your question, you have a great point. I think it would be based on average ambient temp for different areas of the country. To large of a valve would cause "hunting" and to small would "starve" the Evap. I think Eugene would like to take a stab at this .
Mike T.0 -
TXV Sizing
Mike T. Alco, Sporlan and the other makers of TXV's have "extended capicity charts" giving the different tonnages for different pressure drops across the valve.0 -
TXV
Mike T, all manufacturers of txv's have "extended capicity charts" these are based on the press drop across the valve,so like you said ;different ambient's around the country give different hi side pressurers thus different pressure drops.0
- 87K THE MAIN WALL
- 115 Chimneys & Flues
- 107 Geothermal
- 983 Plumbing
- 389 Solar