Fireplace heatloss calc
We have a wood burning fireplace in our SE facing living room. The 2-story chimney is located on an exterior east-facing wall on the first floor. There are heated rooms both above and below the LR and it has a total of 38 feet of exterior walls. The house is stucco and has what looks like 1/2" or so rolled burlap/wool/??? tacked between the studs.
The firebox is 39"w x 31"h x 21"d. We do have an old-style damper currently, but will be replacing with a chimney-top mounted stainless damper which actually seals when closed.
We live in Minnesota and use the fireplace 2 or 3 times per week during the heating months.
How can I go about calculating the heatloss of this room including the fireplace? In other words, what sort of impact does the fireplace have on the overall heatloss of the room?
There are 2 radiators in the LR right now. They are EACH 5-column, 33 sections and 20" tall. There is heated space both above and below.
Room dimensions are 25ft x 13ft. There are 47.85sf of old-style double hungs with wooden/original storms. There is also a set of french doors (also with wooden storms) that total of 27sf.
Without chaning the radiators, how do I determine the designed mix water temp for the zone supplying these radiators?
Thanks again and sorry for the long-winded post.
  • A.J.
    A.J. Member Posts: 257
    Fireplace will definaltly
    > between the studs._br__br_
    > The firebox is 39"w
    > actually seals when closed._br__br_
    > We live in
    > week during the heating months._br__br_
    > How
    > room?_br__br_
    > and below._br__br_
    > that total of 27sf._br__br_
    > Without chaning
    > radiators?_br__br_
  • A.J.
    Fireplace will definitly increase your infiltration
    but if your going to put a new damper in I wouldn't loose any sleep over your room being cold.
    I don't understand why you want to mix your water going to the radiator. If you have a two pipe system with radiators heating your house I would be more concerned with boiler condesation.
    Kupetz's Plb & Htg
  • Constantin
    Constantin Member Posts: 3,796
    There cannot be an exact answer...
    ... without a blower-door test. The biggest culprit with chimney's is the heat loss via the flue. For my climate, the ACCA Manual-J results vary by a factor of 6, depending on the "quality" of the fireplace. BTW, I put Lymance dampers on the tops of my chimney caps and the blower-door guy that came to our house was impressed how tightly insulated it was.
    Making some assumptions (like 9' ceilings), I slapped the data you gave into HVAC-Calc to come up with the following heat loss calculation for a design day in Duluth, MN (-10°F) - see below. They come with no guarantees, as I'm a mere homeowner, not a heating technician.
    Note the very low chimney losses. This is due to the fact that the floor area is very small (only one room). Were I to input the sq ft. floor area of your entire home, the results would scale by some factor set by Manual-J.
    Extrapolating, it is not inconceivable that your heat loss on a design day may be around 14kBTU/hr for that room alone. The only way to know is to run a Manual-J compliant heat loss calculation for the whole house.
    I would look up the capacity of the radiators to determine the supply temperature needed to keep you happy on a design day. That information should be available from the manufacturer or you may be able to find it in the Library (see toolbar at left).
  • hr
    hr Member Posts: 6,106
    Some of those
    insert type wood burners had combustion air ducted to, or near, them. This would be a big source of heat loss. certianly would not want to cap them off if wood will be burned in the unit, however.
    hot rod
  • jeff_51
    jeff_51 Member Posts: 545
    that is an uninsulated exterior masonry wall
    the slant fin heat loss calc you can get here for free has a design criterium (can't spell) in it that will help. Call us at651-426-6404 and ask for Randy. Tell him Jeff told you to call and I think he can give you a pretty good answer. We are in the twin cities. Measure up the square footage of exposed brick face. I usually figure a door area and figure it with no insulation. That may be a bit too much, but should get you close in this area
  • Jimmy Gillies
    Jimmy Gillies Member Posts: 250
    Heatloss with a open fire
    Chris,
    I was always told that if you have a fire in any room it would increase the number of air changes to say 21/2-3 each hour.
    I have used this method while doing heatloss calcs for a number of years.
    I hope that helps?
    Kind regards.
    Jimmy Gillies (Scotland)