Rodney Summers
Member Posts: 748
In a residential setting, what are the typical Delta T's used in the circulator-sizing formulas for the following types of loops:
1) System loop of CI Radaitors
2) System loop of copper-fin tube baseboard
3) Indirect fired DHW tank
Thanks!
1) System loop of CI Radaitors
2) System loop of copper-fin tube baseboard
3) Indirect fired DHW tank
Thanks!
0
Comments
-
Number
1 and 2 is typically 20° dT. Probably NOT for the reasons you suspect either...
# 3 has no design dT "standard." There are so many variables, e.g., if the well water is 38° and the indirect just filled and the boiler cold, we could see a 100° dT and that would be fine.
If sombody's in the shower and the boiler is large, the dT could be 5°. That too would be fine.0 -
HUH?? You answered your own question?
GPM = Btuh / (deltaT x 500)0
This discussion has been closed.
Categories
- All Categories
- 87.4K THE MAIN WALL
- 3.2K A-C, Heat Pumps & Refrigeration
- 61 Biomass
- 429 Carbon Monoxide Awareness
- 120 Chimneys & Flues
- 2.1K Domestic Hot Water
- 5.8K Gas Heating
- 115 Geothermal
- 167 Indoor-Air Quality
- 3.7K Oil Heating
- 77 Pipe Deterioration
- 1K Plumbing
- 6.5K Radiant Heating
- 395 Solar
- 15.7K Strictly Steam
- 3.4K Thermostats and Controls
- 56 Water Quality
- 51 Industry Classes
- 50 Job Opportunities
- 18 Recall Announcements