Old expansion tank
Steamhead
Steamhead Member Posts: 18,627
it didn't take long for the water to stop flowing out of that tank. You have to have a way of letting air back in. If there is a tank drainer fitting where the hose connection is, it should have a 1/8" plug on the side. Remove this plug to let air into the tank as the water drains.
If there's no other way, hook an air compressor to the tank drain and slowly pump air into it. Make sure you don't exceed 30 pounds on the boiler gauge or the relief will blow again.
<A HREF="http://www.heatinghelp.com/getListed.cfm?id=157&Step=30">To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"</A>
Consulting
  • Saggs
    Saggs Member Posts: 174
    Old expansion tank
    I have a customer with an old (in the ceiling) expansion tank on his peerless boiler. All components are original with system. Keeps weeping off relief valve. I opened up the drain valve till water stopped flowing then turned the water feeder back on. The relief valve was just changed, I'm not familiar with this type of tank. I know there's a dip tube which should allow some water to stay in it. Anyone have a correct procedure for getting these un-waterlogged? Thanks
  • tommyoil
    tommyoil Member Posts: 612
    Ceiling tank
    Is the boiler piped to the tank via a B&G ATF (airtrol Tank Fitting)mounted on the tank?
  • Mike T., Swampeast MO
    Mike T., Swampeast MO Member Posts: 6,928
    In normal operation the tank should be about half filled with water.
    This fitting, properly installed, will eliminate the problem at its source:
    "B&G Airtrol"
    Follow installation and filling instructions carefully. The simple air separators built in to some boilers work reasonably. If not present, you'll need a separate air separator. If an old gravity conversion system with high volume, the part of the instructions that say to disable circulator and heat to 220° (think that's the temp) don't [seem] to do much good at removing the initial air. Instead, have found it works well to run the circulator continually for a few days, then bleed the radiators. Then after a month or so of normal heating operation bleed again. After that (given no leaks in the system) air problems disappear.
  • Mark Eatherton1
    Mark Eatherton1 Member Posts: 2,542
    The EASY way to relieve vacuum...
    Provided that there is an isolation valve between the tank and the boiler, AND a seperate drain valve for the tank. Close the valve, put hose on drain valve. Open drain valve. When tank hits the GLUG stage, take a 1/4" ice maker tap saddle valve and tap into the line between the isolation valve and the tank. Open the valve and VIOLA, air in, water out. In less than thirty minutes, you're a HERO as opposed to the ZERO that stood there for three hours at $100+ dollars per hour watching the thing GLUG its way to empty.
    ME
  • And the
    > empty. :-)
    > ME
    > _A
    > 88&Step=30"_To Learn More About This
    > "Find A Professional"_/A_
  • And the REAL EASY way
    Install a diaphragm expansion tank right where the compression tank drain is . I run across this " setup " every once in a while .
  • Joe Mattiello
    Joe Mattiello Member Posts: 751
    No air vent required
    Hopefully no one installed air vents in the system. Plain steel conventional expansion tanks are used in an air control type system, as opposed to a diaphragm type tank used in an air separation type system. A common problem is when someone experiences air problems in the system they install air vent which are problematic with air control systems. For your reference I have attached some good reading material.
    Taco, Inc.
    Joe Mattiello
    Technical Service Technician
    joemat@taco-hvac.com
    401-942-8000 X 484
    www.taco-hvac.com
    Joe Mattiello
    Taco Comfort Solutions
  • Saggs
    Excellent suggestions from each of you. Many thanks for the reply to my problem. Yes the tank does have an air separator B$G I think mounted to the bottom of the tank itself. I think I'm going to try the ice maker tap idea or look for a bleed screw. Would replacing the drain valve with a diaphram tank work other than looking a little funky?
  • ken_27
    ken_27 Member Posts: 2
    expansion tank
    I Would recommend Putting On A Spirovent And A #30 Bladder Tank
  • oil-2-4-6-gas
    oil-2-4-6-gas Member Posts: 641
    put a hose on the drain with a vacuum breaker fitting -cost all of $2.00
  • Alan_11
    Alan_11 Member Posts: 64
    hanging diapragm tank
    Saggs,I would not reccomend hanging the new tank from the drain tapping on the old tank.Never seen it done either in 20 plus years.When the old tank gets waterlogged aftera while you have added 30 or 40 gallons of useless water to the system. Have replaced many ruptured or leakig tanks (air + water + steel=rust) You are better off leaving the old tank empty and dead in the ceiling and finding a way to hang a diapragm tank. an isolation valve to a new tank is a great help also.