Steam radiator volume
gerry gill
Member Posts: 3,083
.025 cubic foot per square foot edr for column radiators..perhaps Dan or Steamhead can address this more as to the charts origins.
<A HREF="http://www.heatinghelp.com/getListed.cfm?id=360&Step=30">To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"</A>
gwgillplumbingandheating.com
Steam radiator volume; cubic feet
I'm trying to figure out the cubic feet of all my radiators. I know the EDR = 640 sq ft. Are there charts that the dead men knew about ? All my rads are 3 column 45" tall.0 -
I have the same chart
Dan was the one who dug it up, not sure where though....
Don't see many 45-inch rads around here.... maybe they were too tall for the average Baltimore installer to handle... ;-)All Steamed Up, Inc.
Consulting0 -
heres another method,
Here is another way to find the cubic footage of a radiators air that I like. This method requires some math, but its not hard. In the Peerless Boiler Companies training manual entitled color of water they list the GALLON content of various heat emitters . a cast iron column radiator holds , according to Peerless Boiler, .114 gallons of water per square foot edr. Thats (point114). Okay, so say you have a 50 square foot edr radiator. Then 50 times .114 equals 5.7 gallons. Now there is 231 cubic inches to a gallon. So 5.7 times 231 equals 1316.7 cubic inches in the radiator..okay now there is 1728 cubic inches in a cubic foot, so 1316.7 divided by 1728 equals .76 cubic feet of air..
To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"gwgillplumbingandheating.com
I'm just making it harder ! But .........
Dan's chart = .025 Cu Ft / 1 EDR
Peerless = .114 gallons / 1 EDR == .01524 Cu Ft
My cad drawing = .0225 Cu Ft / 1 EDR @ 1/8" thick walls
If we use Dan's # then .025 * 6 = 0.15 Cu Ft for 1 - 3 column section 45" tall. That's in the ballpark.
Now we go through the back door !
If I multiply 6 * 240 == 1440 BTUs/Hr for 1 - 3 column section 45" tall.
If I'm getting 1440 BTU's/Hr into the room I've got to have that much or more going through the rad. Right ?
If the room stays at 70 F for a full hour.
It takes 970 BTU's to boil off 1 Lb of water and that gives you 28 Cu Ft of steam so 1440 BTU's should boil off 1.485 Lbs @ 39 Cu Ft. 39/.15 = 260 so in 3600 seconds 3600/260 = 14 seconds. Every 14 seconds the rad will condense the steam inside back to water. Of course it's a continous cycle it doesn't really happen in blocks of time.
Is that about right ?
Now after the boiler gets the water up to 212 + some, do the 1440 BTU's get added over an hours time ? Which would be .4 BTUs / second.
holy smokes Bill,
I thought I had time on my hands, hehe, all that math already has my brain hurting..hehe
- 167 Indoor-Air Quality